Howdy, Electrical Experts!
As we get ready to roll the presses on the second printing of our residential electrical inspection book (thanks to Paul Abernathy and the late, great Gerry Beaumont, may he RIP), it's come to our attention that we have a discrepancy regarding the minimum height clearance for swimming pools. Can someone advise, please (without relying on the online residential electrical course, since we will likely need to make a correction there, too)? I believe our source should be the NEC, but Nick asked me to throw the question out to you guys. Thanks to member Ron [StillTryingtoFindOutHisLastName] for catching this! |
| Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is from a previous thread. I had to paste it together since the Table could not be copied as it appears in the NEC. For more complete information check out Table 680.8:
Quote:
|
|
#3
|
||||
|
||||
|
Not quite what you're looking for, but this is what our utility company says about pool clearance.
AMEREN ELECTRIC SERVICEMANUAL 800−2 06/25/09 Clearances of Services over Swimming Areas
Although it is possible to have services over swimming areas, this practice is discouraged. It is necessary that the maximum conductor sag under various operating and environmental conditions be determined. Contact your local Ameren representative for assistance. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#4
|
||||
|
||||
|
That's what we have in a chart in the course (22'6"). The discrepancy is in a graphic that was created by one of our former graphics folks, but the measurement is either old or just wrong.
Thanks for taking the time to post! If we have any more thumbs-ups or thumbs-downs on this, please keep posting! (And I couldn't agree more with CCurrins -- the idea of being in an outdoor pool situated beneath a service drop would have me shaking...!) |
|
#5
|
||||
|
||||
|
This is what we follow in florida.
424.1.4.2.4 Overhead wiring. Overhead service wiring shall not pass within an area extending a distance of 10 feet (3048 mm) horizontally away from the inside edge of the pool walls, diving structures, observation stands, towers or platforms. Allowances for overhead conductor clearances to pools that meet the safety standards in the National Electrical Code may be used instead. Greg Bell Titusville, Fl 02111507 Serving Central Florida
Last edited by gbell; 5/14/10 at 4:18 PM.. |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
||||
|
||||
|
Please see attached. (Nick told me not to do this initially.)
The "10 feet away" is not in dispute; it's the height between the service drop and the pool. |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
According to the NEC it should be 22.5' above the water level. |
|
#9
|
||||
|
||||
|
OK, Guys --
Thanks for weighing in. I'm going to correct the measurement in the graphic, and Nick will upload the replacement to the Image Library as soon as he gets it from me. Be sure to download it for yourselves if you have our CD of images. Have a great weekend! |
|
#10
|
|||
|
|||
|
Lol...so much for being an author of anything....lol.....typical
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Electricians Check List | pabernathy | Electrical Inspections | 74 | 12/5/07 6:39 PM |
| Service Drop Clearances | jhagarty | Electrical Inspections | 12 | 8/15/07 8:31 PM |
| Inadequate Drop Clearance | jpope | Electrical Inspections | 4 | 6/27/06 3:03 PM |
| Service Drop Run Over Balcony? | jtedesco1 | Electrical Inspections | 0 | 5/31/06 5:23 AM |
| Service Drop and SEC | jpope | Electrical Inspections | 11 | 1/14/06 11:15 PM |