Default Service drop clearance for swimming pools?

Howdy, Electrical Experts!

As we get ready to roll the presses on the second printing of our residential electrical inspection book (thanks to Paul Abernathy and the late, great Gerry Beaumont, may he RIP), it's come to our attention that we have a discrepancy regarding the minimum height clearance for swimming pools.

Can someone advise, please (without relying on the online residential electrical course, since we will likely need to make a correction there, too)? I believe our source should be the NEC, but Nick asked me to throw the question out to you guys.

Thanks to member Ron [StillTryingtoFindOutHisLastName] for catching this!



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/14/10, 3:14 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,052
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop clearance for swimming pools?

This is from a previous thread. I had to paste it together since the Table could not be copied as it appears in the NEC. For more complete information check out Table 680.8:

Quote:
680.8 Overhead Conductor Clearances.
Overhead conductors shall meet the clearance requirements in this section. Where a minimum clearance from the water level is given, the measurement shall be taken from the maximum water level of the specified body of water.
(A) Power. With respect to service drop conductors and open overhead wiring, swimming pool and similar installations shall comply with the minimum clearances given in Table 680.8 and illustrated in Figure 680.8.
FPN: Open overhead wiring as used in this article typically refers to conductor(s) not in an enclosed raceway.

Table 680.8 Overhead Conductor Clearances

Insulated Cables, 0750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor:


Clearance Parameters:

A. Clearance in any direction to the water level, [6.9m or 22.5 feet]
edge of water surface, base of diving platform, or
permanently anchored raft
Reply With Quote
  #3  
Old 5/14/10, 3:14 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,226
Default Re: Service drop clearance for swimming pools?

Not quite what you're looking for, but this is what our utility company says about pool clearance.


AMEREN ELECTRIC SERVICEMANUAL 800−2 06/25/09


Clearances of Services over Swimming Areas
Although it is possible to have services over swimming areas, this practice is discouraged. It is necessary that the maximum conductor sag under various operating and environmental conditions be determined. Contact your local Ameren representative for assistance.






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #4  
Old 5/14/10, 3:34 PM
Kate Tarasenko's Avatar
Kate Tarasenko Kate Tarasenko is offline
InterNACHI Staff
 
Join Date: Jul 2009
Posts: 309
Default Re: Service drop clearance for swimming pools?

That's what we have in a chart in the course (22'6"). The discrepancy is in a graphic that was created by one of our former graphics folks, but the measurement is either old or just wrong.

Thanks for taking the time to post!

If we have any more thumbs-ups or thumbs-downs on this, please keep posting!

(And I couldn't agree more with CCurrins -- the idea of being in an outdoor pool situated beneath a service drop would have me shaking...!)



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
  #5  
Old 5/14/10, 4:13 PM
Greg Bell, Sr's Avatar
Greg Bell, Sr Greg Bell, Sr is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,553
Default Re: Service drop clearance for swimming pools?

This is what we follow in florida.

424.1.4.2.4 Overhead wiring. Overhead service wiring shall not pass within an area extending a distance of 10 feet (3048 mm) horizontally away from the inside edge of the pool walls, diving structures, observation stands, towers or platforms. Allowances for overhead conductor clearances to pools that meet the safety standards in the National Electrical Code may be used instead.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida

Last edited by gbell; 5/14/10 at 4:18 PM..
Reply With Quote
  #6  
Old 5/14/10, 4:17 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,052
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop clearance for swimming pools?

Quote:
Originally Posted by ktarasenko View Post
That's what we have in a chart in the course (22'6"). The discrepancy is in a graphic that was created by one of our former graphics folks, but the measurement is either old or just wrong.

Thanks for taking the time to post!

If we have any more thumbs-ups or thumbs-downs on this, please keep posting!

(And I couldn't agree more with CCurrins -- the idea of being in an outdoor pool situated beneath a service drop would have me shaking...!)
Can you post the graphic?
Reply With Quote
  #7  
Old 5/14/10, 4:37 PM
Kate Tarasenko's Avatar
Kate Tarasenko Kate Tarasenko is offline
InterNACHI Staff
 
Join Date: Jul 2009
Posts: 309
Default Re: Service drop clearance for swimming pools?

Quote:
Originally Posted by Robert Meier View Post
Can you post the graphic?
Please see attached. (Nick told me not to do this initially.)

The "10 feet away" is not in dispute; it's the height between the service drop and the pool.
Attached Thumbnails
service-drop-clearance-swimming-pools-service-drop-clearances.jpg  



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
  #8  
Old 5/14/10, 4:41 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,052
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop clearance for swimming pools?

Quote:
Originally Posted by ktarasenko View Post
Please see attached. (Nick told me not to do this initially.)

The "10 feet away" is not in dispute; it's the height between the service drop and the pool.

According to the NEC it should be 22.5' above the water level.
Reply With Quote
  #9  
Old 5/14/10, 4:59 PM
Kate Tarasenko's Avatar
Kate Tarasenko Kate Tarasenko is offline
InterNACHI Staff
 
Join Date: Jul 2009
Posts: 309
Default Re: Service drop clearance for swimming pools?

OK, Guys --

Thanks for weighing in. I'm going to correct the measurement in the graphic, and Nick will upload the replacement to the Image Library as soon as he gets it from me.

Be sure to download it for yourselves if you have our CD of images.

Have a great weekend!



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
  #10  
Old 5/15/10, 8:58 AM
Paul W. Abernathy, CMI's Avatar
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Melissa, TX
Posts: 8,571
Send a message via Skype™ to pabernathy
Default Re: Service drop clearance for swimming pools?

Lol...so much for being an author of anything....lol.....typical



Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation

Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, associations, organizations or affiliations.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electricians Check List pabernathy Electrical Inspections 75 1/6/14 7:19 AM
Service Drop Clearances jhagarty Electrical Inspections 12 8/15/07 8:31 PM
Inadequate Drop Clearance jpope Electrical Inspections 4 6/27/06 3:03 PM
Service Drop Run Over Balcony? jtedesco1 Electrical Inspections 0 5/31/06 5:23 AM
Service Drop and SEC jpope Electrical Inspections 11 1/14/06 11:15 PM