I just finished going through the Electrical Studies (excellent piece of work BTW!!! Thank you for this!!!) and found a possible discrepancy that I wanted to try and clear up. It's not a big deal as our service drop clearances in Canada are a little different than in the States - they are slightly higher; are Canadians taller?

According to the quiz a service drop over a swimming pool must be 22 1/2' above and 10' away horizontally... and the minimum service drop clearance over a flat roof is 10'. However, according to this diagram in some Carson Dunlap material I have, the numbers are different... 18' over a pool and 8' (min) over a flat roof. Which is correct?

service-drop-q-service-drop-clearances-us-small-.jpg (Small).jpg
Views:	518
Size:	34.7 KB
ID:	9365
Reply With Quote
  #2  
Old 2/22/07, 9:51 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

Arne, you're going to feel dumb when I tell you this, but in your diagram, the words at the top say "Service Drop Clearances (UNITED STATES)". What is correct is whatever Canada says is correct. The clearances in the diagram represent the minimum required in the IRC, and which is recognized as the minimum in the states. Ergo, the heights you quoted for Canada are correct for your jurisdiction. Sometimes, we can't see the forest for the trees, eh?
Reply With Quote
  #3  
Old 2/22/07, 1:23 PM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

Quote:
Originally Posted by jbreazeale
Arne, you're going to feel dumb when I tell you this, but in your diagram, the words at the top say "Service Drop Clearances (UNITED STATES)". What is correct is whatever Canada says is correct. The clearances in the diagram represent the minimum required in the IRC, and which is recognized as the minimum in the states. Ergo, the heights you quoted for Canada are correct for your jurisdiction. Sometimes, we can't see the forest for the trees, eh?
Let's just leave ourselves out of this for a moment lol... My question is one of curiosity; I know what the Canadian numbers are - (the differences in our service drop criteria being that we don't have a 3' minimum over a roof, rather, service drops OVER roofs are generally not allowed except by special permission; our clearances are higher over roadways & driveways; and we don't specify any criteria for running over swimming pools, probably because they are always frozen over... hee, hee). So... having said that...

I am comparing apples & apples and realize that my diagram is for the States, as it is immediately to the left of the diagram labelled for Canada in the same text book I have. I probably just didn't articulate myself very well the first time, but my question is, "Why is a US diagram different from this US-based quiz (from the NACHI website), as it pertains to these two service drop questions"?

The diagram depicts a minimum of 8' (8-10) over a roof, and 18' above a pool - whereas the quiz reads 10' and 22.5' respectively. Either the diagram that Carson Dunlap is using is wrong, or the quiz is. I'm just curious.

I went back to the quiz and copied & pasted the questions I am referring to below...

The minimum service drop clearance over a flat roof used as a roof garden should be?

10ft (correct)
12 ft
8 ft
18 ft



Service drops around a swimming pool should be?

12 ft above and 15 ft horizontally away from
10 ft above and 22 ft horizontally away from
22 1/2 ft above and 10 ft horizontally away from (correct)
18 ft above and 10 ft horizontally away from
15 ft above and 8 ft horizontally away from
10 ft above and 20 ft horizontally away from
Reply With Quote
  #4  
Old 2/23/07, 2:21 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

IC, sed the blind man...I really wasn't trying to be a smart **s, Marc, and apologize if you felt insulted. And I see the problem you are having now. A bit of ambiguity there, eh? They got swimmin pules in the Great White North? I thought you guys called them backyard hockey courts!
Reply With Quote
  #5  
Old 2/23/07, 2:23 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

I mean, Arne...not Marc....dang, time to go to bed!
Reply With Quote
  #6  
Old 2/23/07, 3:30 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

Quote:
Originally Posted by jbreazeale
I mean, Arne...not Marc....dang, time to go to bed!
LOL! No worries, and never once felt insulted. Cheers!
Reply With Quote
  #7  
Old 2/23/07, 3:49 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

Quote:
Originally Posted by jbreazeale
They got swimmin pules in the Great White North? I thought you guys called them backyard hockey courts!
You mean like this?

service-drop-q-canadiangirl-small-.jpg.jpg
Views:	1375
Size:	39.0 KB
ID:	9427
Reply With Quote
  #8  
Old 2/23/07, 8:06 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: Service Drop Q

Was'nt that picture in the quiz over a deck or roof garden?
Reply With Quote
  #9  
Old 2/24/07, 10:01 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Service Drop Q

The question asks for minimum distance. So 8' should be the answer for the flat roof. But.... a garden adds a foot or two and it becomes a trick question. Dirt does have a height to it. So 10' would be the minimum distance.

Last edited by dvalley; 2/24/07 at 10:06 AM..
Reply With Quote
  #10  
Old 2/24/07, 10:10 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Service Drop Q

As for the pool, the answer should be 18 ft above and 10 ft horizontally.

"Click to Enlarge"
Attachment 9460

Note the diagram above also states that if the flat roof is a balcony (which a garden would be considered a balcony) the minimum distance must be 10 feet.

Last edited by dvalley; 10/7/07 at 4:40 PM..
Reply With Quote
  #11  
Old 2/24/07, 10:56 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Q

680.8 says 22.5 feet above the water for overhead conductors 0-750v, 25' up to 15kv and 27' if it is over 15kv OR 10 away
Reply With Quote
  #12  
Old 2/25/07, 9:45 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service Drop Q

Yeah....you have to remember Carson Dunlops stuff is OLD...and I mean OLD....the NEC and Canadian codes change over time but once an image is made it is kinda DONE...unless someone updates it.....

The 22.5 is CURRENT standards.......and what you will see mostly with regard to dwellings...0-750V is well within what your dwelling will deal with in these clearances.

At one time it was lower...I believe the revision came between the 1999NEC and the 2002 NEC.....maybe the POOL poles got longer...who knows.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Drop Dropped While at Inspection!! mlong Electrical Inspections 9 10/20/07 6:20 AM
Service Drop Clearances jhagarty Electrical Inspections 12 8/15/07 8:31 PM
Service Drop Clearance Over Roof mlong Electrical Inspections 6 12/19/06 7:39 AM
Service Drop Run Over Balcony? jtedesco1 Electrical Inspections 0 5/31/06 5:23 AM
Service Drop and SEC jpope Electrical Inspections 11 1/14/06 11:15 PM


All times are GMT -4. The time now is 4:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts