Default Service drop question

service-drop-question-dscn4213-small-.jpg.JPG
Views:	154
Size:	58.5 KB
ID:	17468
The mast seems to have the required 18 inches but anyone know off hand how much clearence from the roof the conductors should have.
It is only about two inches.
Reply With Quote
  #2  
Old 1/13/08, 11:41 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Service drop question

Off topic question, was the seal broken on the meter base?

tom
Reply With Quote
  #3  
Old 1/13/08, 11:56 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Service drop question

No but why do you ask?
Reply With Quote
  #4  
Old 1/14/08, 1:26 AM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Service drop question

Quote:
Originally Posted by relliott
Attachment 17468
The mast seems to have the required 18 inches but anyone know off hand how much clearence from the roof the conductors should have.
It is only about two inches.
That should be called out... The Service provider will fix it at no charge.


Ooops, 18 inches to 24 inches. I always look at it as a safety thing regardless of the clearence, and in this case it looks to me as something the Utillity would fix.
Reply With Quote
  #5  
Old 1/14/08, 1:30 AM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Service drop question

The Tie is supported under the drip or Gutter, this always makes me wright it up as a hazard.
Reply With Quote
  #6  
Old 1/14/08, 1:35 AM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Service drop question

I have been reading some of MY posts and I can tell you all that I DID NOT POST 90 % of them in the last 6 months or so. However, that is besides the case. I know who did post some of that and strangly enough it was not much different than I would have posted myself. Strange folks strange land..

I wish you all well.
Reply With Quote
  #7  
Old 1/14/08, 7:27 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop question

Quote:
Originally Posted by tallen
I have been reading some of MY posts and I can tell you all that I DID NOT POST 90 % of them in the last 6 months or so. However, that is besides the case. I know who did post some of that and strangly enough it was not much different than I would have posted myself. Strange folks strange land..

I wish you all well.
Strange, I got a PM this morning stating that I had violated someones private account here. I wouldn't know how to do this but it does seem that that person intends to see me in person.
Reply With Quote
  #8  
Old 1/14/08, 7:52 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Angry Re: Service drop question

Quote:
Originally Posted by Mike Whitt
Strange, I got a PM this morning stating that I had violated someones private account here. I wouldn't know how to do this but it does seem that that person intends to see me in person.
Mike:

See this message and then look near the bottom where you call someone a drunkard

http://www.nachi.org/forum/showpost....3&postcount=67

When that link is accessed it takes the member to their control panel, did you do this, if you did better ask Danny to give you some KY Jelly, I am bull s h i t and the showdown will come soon for you and probably the other stooge!
Reply With Quote
  #9  
Old 1/14/08, 8:17 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop question

Quote:
Originally Posted by jtedesco1
Mike:

See this message and then look near the bottom where you call someone a drunkard

http://www.nachi.org/forum/showpost....3&postcount=67

When that link is accessed it takes the member to their control panel, did you do this, if you did better ask Danny to give you some KY Jelly, I am bull s h i t and the showdown will come soon for you and probably the other stooge!
Okay I see what you are saying now. I was trying to open up to my Latest Reputation Received so that every one could see the vuglar language that someone had posted there directed toward me. No harm no foul.
Reply With Quote
  #10  
Old 1/14/08, 9:33 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Service drop question

Thanks for all the great answers.
Reply With Quote
  #11  
Old 1/14/08, 9:39 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Service drop question

Not sure about your masthead clearance question but I hope you pointed out that fence to your buyers.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #12  
Old 1/14/08, 9:41 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Service drop question

Not concerned about the masthead, but rather clearance of the lines from the gutter.
What is the rule from the NEC?
Wish Paul was feeling better.
Reply With Quote
  #13  
Old 1/14/08, 11:36 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop question

For that type of service drop the best infomation will be from the POCO they have pretty spefic detals on the service drop connection and where to mounted to the sturcture or on mast.

As far i am looking at the photo if this place is above the second story or second floor hightwise it should be ok but i wish there is other photo seeing at diffrent angle but the hevey angle iron bracket if lagged bolted or thru bolted to the actual stucture it is ok but on the sheeting [ plywood or OSB etc ] not a really pratical idea becasue few POCO did stated a warning especally with semilong run the line tenstion can be pretty hard on the bracket [ keep in your mind this true with snow/ ice belt area ]

and let me add the last comment here if it is above the window and away from window there is no issue with that.

but again please check with your POCO for most recent regulations for your area.

Merci, Marc
Reply With Quote
  #14  
Old 1/14/08, 12:43 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Service drop question

Just to restate ,I am mainly concerned with the two hot s touching the gutter if they sag.
service-drop-question-dscn4222-small-.jpg.JPG
Views:	61
Size:	60.1 KB
ID:	17485
Reply With Quote
  #15  
Old 1/14/08, 1:14 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service drop question

Here you go! Looks like that connection was temporary, or iy may have been a job with no permit?

Last edited by jtedesco1; 1/22/08 at 7:12 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Service disconnect question wsiegel Electrical Inspections 3 8/28/07 9:59 AM
Service Drop Was Finally Removed! jtedesco1 Electrical Inspections 1 12/1/06 2:40 AM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 10:41 PM


All times are GMT -4. The time now is 4:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts