Default Service Drop Question

Whenever I do a 4 point, insurance inspection, I note the service drop as a deficiency in need of repair if it is significantly less than 10' high. Usually, I'll only note it if it is about 9'.
My question is, "Is anyone else doing this?"
While I don't want to hurt the homeowner, If someone hit the drop with a ladder and it was found to be 9', instead of 10', I could be held liable.
Any thoughts?



Reece D. WelchBSA,CMI,CGC,CCC,HI,MRSA
Certified Master Inspector®
State Licensed General Contractor
State Licensed Roofing Contractor
State Licensed Home Inspector
State Licensed Mold Assessor

Offices: 121 S. DeSoto Ave Phone: 863-494-1560
Arcadia, FL 34266 Fax: 863-494-6233
www.HISofSWFL.com
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/31/11, 8:14 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Service Drop Question

The installation provisions for a utility service drop are typically the responsibility of the utility company, who have their own requirements. You can use model codes as a quide, but you may want to find out what the local utility company requirements are. After that it's a judgement call for an existing installation.

And I hope your not using a metal tape to measure the height, because the bare messenger (neutral) wire typically carries current ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #3  
Old 8/31/11, 12:38 PM
Thomas R. Hession's Avatar
Thomas R. Hession Thomas R. Hession is online now
InterNACHI Member
 
Join Date: Jan 2010
Location: Pinellas Park, Fl.
Posts: 716
Default Re: Service Drop Question

It's been my experience that service drops to residential dwellings start just below the transformer than slope down to the service mast. If it is less than ten feet than the homeowner is responsible for raising his service mast to the required height.

Please correct me if I am wrong...

Reece...ever have to go back to verify that the deficiency has been repaired?



Tom Hession
HHH Home Inspection Services LLC
Pinellas Park, Fl.
312-371-5076
http://www.inspectorpages.com/thession
http://www.pinellasinspector.com/
http://www.facebook.com/pinellashomeinspection

Home, Health, Happiness
Reply With Quote
  #4  
Old 8/31/11, 6:19 PM
Reece D. Welch's Avatar
Reece D. Welch Reece D. Welch is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Arcadia, FL
Posts: 256
Default Re: Service Drop Question

Quote:
Originally Posted by thession View Post
It's been my experience that service drops to residential dwellings start just below the transformer than slope down to the service mast. If it is less than ten feet than the homeowner is responsible for raising his service mast to the required height.

Please correct me if I am wrong...

Reece...ever have to go back to verify that the deficiency has been repaired?
Actually, I'm going back tomorrow to check the repair of a service drop that was about 4" above the peak of an outbuilding. The homeowner had the weatherhead raised.
I don't like going back for free.



Reece D. WelchBSA,CMI,CGC,CCC,HI,MRSA
Certified Master Inspector®
State Licensed General Contractor
State Licensed Roofing Contractor
State Licensed Home Inspector
State Licensed Mold Assessor

Offices: 121 S. DeSoto Ave Phone: 863-494-1560
Arcadia, FL 34266 Fax: 863-494-6233
www.HISofSWFL.com
Reply With Quote
  #5  
Old 8/31/11, 6:20 PM
Reece D. Welch's Avatar
Reece D. Welch Reece D. Welch is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Arcadia, FL
Posts: 256
Default Re: Service Drop Question

Quote:
Originally Posted by roconnor View Post
The installation provisions for a utility service drop are typically the responsibility of the utility company, who have their own requirements. You can use model codes as a quide, but you may want to find out what the local utility company requirements are. After that it's a judgement call for an existing installation.

And I hope your not using a metal tape to measure the height, because the bare messenger (neutral) wire typically carries current ...
Yes. Yes, I am using a metal tape measure. I have been VERY cautious. Do you have a better method?



Reece D. WelchBSA,CMI,CGC,CCC,HI,MRSA
Certified Master Inspector®
State Licensed General Contractor
State Licensed Roofing Contractor
State Licensed Home Inspector
State Licensed Mold Assessor

Offices: 121 S. DeSoto Ave Phone: 863-494-1560
Arcadia, FL 34266 Fax: 863-494-6233
www.HISofSWFL.com
Reply With Quote
  #6  
Old 8/31/11, 8:41 PM
jtedesco3 jtedesco3 is offline
New User
 
Join Date: Jul 2011
Location: Boston, MA
Posts: 38
Please Note: jtedesco3 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Question

Use a nonmetallic measuring stick instead:

Reply With Quote
  #7  
Old 8/31/11, 8:50 PM
jtedesco3 jtedesco3 is offline
New User
 
Join Date: Jul 2011
Location: Boston, MA
Posts: 38
Please Note: jtedesco3 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Question

Quote:
Originally Posted by rwelch View Post
Whenever I do a 4 point, insurance inspection, I note the service drop as a deficiency in need of repair if it is significantly less than 10' high. Usually, I'll only note it if it is about 9'.
My question is, "Is anyone else doing this?"
While I don't want to hurt the homeowner, If someone hit the drop with a ladder and it was found to be 9', instead of 10', I could be held liable.
Any thoughts?
You should review NEC "Section 230.24 Clearances. Overhead service conductors shall not be readily accessible and shall comply with 230.24(A) through (E) for services not over 600 volts, nominal." This rule was revised long ago to comply with the NESC so that heights above various locations would be the same.
Reply With Quote
  #8  
Old 8/31/11, 8:55 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Service Drop Question

Quote:
Originally Posted by thession View Post
If it is less than ten feet than the homeowner is responsible for raising his service mast to the required height.
It is the same around here.
Attached Thumbnails
service-drop-question-elec-service-20drop-20clearance-20diagram-640x480-.jpg  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 8/31/11, 9:03 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop Question

Code wise it's somewhat contradictory because on one hand service drops are covered by the utility company regulations and are outside of the purview of the NEC, but the NEC still lists minimum heights in 230.24. I'm guessing that if the drop is solely covered by the utility then 230.24 does not apply.

Quote:
90.2 Scope.
(A) Covered. This Code covers the installation of electrical conductors, equipment, and raceways; signaling and communications conductors, equipment, and raceways; and optical fiber cables and raceways for the following:
(1) Public and private premises, including buildings, structures, mobile homes, recreational vehicles, and floating buildings
(2) Yards, lots, parking lots, carnivals, and industrial substations

(3) Installations of conductors and equipment that connect to the supply of electricity
(4) Installations used by the electric utility, such as office buildings, warehouses, garages, machine shops, and recreational buildings, that are not an integral part of a generating plant, substation, or control center.
(B) Not Covered. This Code does not cover the following:
(1) Installations in ships, watercraft other than floating buildings, railway rolling stock, aircraft, or automotive vehicles other than mobile homes and recreational vehicles
FPN: Although the scope of this Code indicates that the Code does not cover installations in ships, portions of this Code are incorporated by reference into Title 46, Code of Federal Regulations, Parts 110–113.
(2) Installations underground in mines and self-propelled mobile surface mining machinery and its attendant electrical trailing cable
(3) Installations of railways for generation, transformation, transmission, or distribution of power used exclusively for operation of rolling stock or installations used exclusively for signaling and communications purposes
(4) Installations of communications equipment under the exclusive control of communications utilities located outdoors or in building spaces used exclusively for such installations
(5) Installations under the exclusive control of an electric utility where such installations
a. Consist of service drops or service laterals, and associated metering, or
Reply With Quote
  #10  
Old 8/31/11, 10:05 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Service Drop Question

Quote:
Originally Posted by jtedesco3 View Post
Use a nonmetallic measuring stick instead:
The one pictured is a specialized tool, and a little costly at around $700 just for getting a service drop height. He could just use a 16' fiberglass surveyors rod at around $60 ...



Quote:
Originally Posted by Robert Meier View Post
Code wise it's somewhat contradictory because on one hand service drops are covered by the utility company regulations and are outside of the purview of the NEC, but the NEC still lists minimum heights in 230.24. I'm guessing that if the drop is solely covered by the utility then 230.24 does not apply.
Thats my read too. And in some more rural areas the service drops to a pole with a meter near the property line, and then continues overhead to the building which is covered by the NEC.

Have heard of at least a few cases where inspectors flagged somewhat low drops, and clients were later told by the utility there wasn't a problem. Some utilities require greater clearances (e.g. see attached from local utility company). If you dont like egg face sandwiches the best thing to do if you are checking drop clearances is contact the local utility company to get their requirements.

And put away that metal tape for gods sake ... is your life worth $60 ...
.
Attached Files
File Type: pdf LIPA Service Drop Clearances - 2009 Redbook.pdf (45.4 KB, 52 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 9/1/11 at 9:44 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM
Service entry question acassady Electrical Inspections 1 7/31/09 7:33 AM
Service Drop Q alarsen1 Electrical Inspections 11 2/25/07 9:45 AM
Service Drop Clearance Over Roof mlong Electrical Inspections 6 12/19/06 7:39 AM


All times are GMT -4. The time now is 8:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts