Default Service entrance and a raised garden

This doesn't look kosher to me...

Service entrance buried in a raised bed, about 18" of soil.

Picture isn't great, but what you're seeing is the (already open) portion of the service entrance below the meter.

Companion picture is of a "normal" meter and entrance on the same building.

Any suggestions for recommendations? I'm thinking the raised bed could cause water to get into the panel (but no water or rust was found inside)

Comments?
Attached Thumbnails
service-entrance-and-raised-garden-typical-electric.jpg   service-entrance-and-raised-garden-sec.jpg  
Reply With Quote
  #2  
Old 9/6/07, 4:00 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Service entrance and a raised garden

Hi Thomas,

That would have to be wrong on several counts
  • Common sense
  • Lack of service space
  • Panel not rated for direct burial!!
Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 9/6/07, 4:28 PM
Thomas Jansson's Avatar
Thomas Jansson Thomas Jansson is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Chicago, IL
Posts: 194
Default Re: Service entrance and a raised garden

Thanks much, Gerry.
Reply With Quote
  #4  
Old 9/6/07, 6:20 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

If this is part of the meter socker assembly the utility company should fix it.
Reply With Quote
  #5  
Old 9/6/07, 9:09 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Jim Port
If this is part of the meter socker assembly the utility company should fix it.
Absolutely NOT. I'd say probably over 90% of the country the customer is responsible for everything (except the meter itself) from the taps down or the lateral up. This includes the meter pan.
Reply With Quote
  #6  
Old 9/6/07, 9:11 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by gbeaumont
  • Panel not rated for direct burial!!
How do you know this for certain?
That looks to me like a meter pedestal rated for burial. I am pretty sure it can be buried right up the that latch visible in the photos.
Reply With Quote
  #7  
Old 9/6/07, 9:12 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Speedy Petey
Absolutely NOT. I'd say probably over 90% of the country the customer is responsible for everything (except the meter itself) from the taps down or the lateral up. This includes the meter pan.
\

No. The sparky who originally installed it is wrong

Customers do not install meter boxes.

Darn Electricians!



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 9/6/07, 9:13 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by wdecker
Customers do not install meter boxes.
No, they install flower beds.
Reply With Quote
  #9  
Old 9/6/07, 9:44 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Speedy Petey
How do you know this for certain?
That looks to me like a meter pedestal rated for burial. I am pretty sure it can be buried right up the that latch visible in the photos.
Funny Pete,

I thought the ones rated for direct burial had to be in a wooden lead lined box and at a depth of 6 feet

I learn something new every day

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #10  
Old 9/6/07, 10:05 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Speedy Petey
No, they install flower beds.
Do you have proof that the homeowner did this? Huh?

By Occum's Razor, blame the sparky.

I'l bet the the person who laid the pavers in the first picture was a moon lighting electrician.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 9/6/07, 10:09 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

Pete,

Around here the socket is set by the POCO. Contractor just runs SE tail out. POCO terminates to socket.
Reply With Quote
  #12  
Old 9/6/07, 10:16 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Jim Port
Pete,

Around here the socket is set by the POCO. Contractor just runs SE tail out. POCO terminates to socket.
Is it just me, of does this sound, somehow, kinky?

We GOTTA get some better terminology, don't you think?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #13  
Old 9/6/07, 10:21 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by wdecker
Do you have proof that the homeowner did this? Huh?

It was done by the "magic trowel" from a spot on the grassy knoll

By Occum's Razor, blame the sparky.

Or the cat, dead in the box, which reminds me, what is the sound of one hand clapping??

Whoosh..................whoosh...............whoos h

I'l bet the the person who laid the pavers in the first picture was a moon lighting electrician.

I'll have to disagree on that one as I see no signs of splicing
Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #14  
Old 9/6/07, 10:23 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by gbeaumont
Regards

Gerry
I stand corrected, Gerry.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 9/6/07, 11:08 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by gbeaumont
I'l bet the the person who laid the pavers in the first picture was a moon lighting electrician.
I once knew a guy who named his new company "Moon Light Electric". No joke.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Entrance jcampbell Electrical Inspections 9 10/30/06 12:14 AM
Another Service Entrance Amps Question pdickerson Electrical Inspections 2 8/7/06 3:39 PM
Service Entrance Amps? dtaylor Electrical Inspections 12 8/5/06 3:38 PM
Service Entrance Extension – Is It Kosher? DSuelflow Electrical Inspections 5 7/27/06 10:09 PM
Service Entrance Amperage? jfunderburk Electrical Inspections 18 6/16/06 10:16 PM


All times are GMT -4. The time now is 1:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts