Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Speedy Petey
How do you know this for certain?
That looks to me like a meter pedestal rated for burial. I am pretty sure it can be buried right up the that latch visible in the photos.
You must have a different kind of dirt up there if you can direct bury a paint over steel can. Around here that would rust off at the ground in a year or two. They rust up bad enough 5 feet off the ground.
Reply With Quote
  #17  
Old 9/7/07, 12:49 AM
Thomas Jansson's Avatar
Thomas Jansson Thomas Jansson is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Chicago, IL
Posts: 193
Default Re: Service entrance and a raised garden

And, indeed, you can already see the rust coming along quite nicely on the unburied portion.

Recommended removal of the small raised garden for numerous reasons. Wood-framed brick veneer structure, moisture being held against the house, chance of water entry, damage to interior, structure, contents and finishes, wooden sill below grade, blah, blah, blah. The buried electric just put the "slam" into the dunk.
Reply With Quote
  #18  
Old 9/7/07, 7:34 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance and a raised garden

Have a lookie below. Like I said, the one in the link is to be buried almost to the upper cover latch.

Milbank is one of the largest meter socket manufacturers in the world.

http://www.milbankmfg.com/products/c...40%2005-07.pdf



I am really not trying to be a P-I-A, but it's just you guys can't "slam" something simply because you think it is not right.

If I installed that service, and someone put that planter in after, then a H-I comes in and says I installed the service wrong, I'd be pissed! That makes me look bad for NO reason. Then I have to go out of my way to defend myself due to NO fault of my own. All because of an opinion not based on fact.
See where I am coming from.

Last edited by Speedy Petey; 9/7/07 at 7:38 AM..
Reply With Quote
  #19  
Old 9/7/07, 9:47 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Service entrance and a raised garden

Quote:
Originally Posted by Jim Port
Pete,

Around here the socket is set by the POCO. Contractor just runs SE tail out. POCO terminates to socket.
Perhaps - but around here the electrician picks up the meter base from the power company, mounts and wires it from the mast down through the meter terminals to the panels, or from the meter to the panel in the case of underground service. The POCO then installs the conductors from their transformer, usually at the same time the meter is plugged in after final inspection.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Entrance jcampbell Electrical Inspections 9 10/30/06 1:14 AM
Another Service Entrance Amps Question pdickerson Electrical Inspections 2 8/7/06 4:39 PM
Service Entrance Amps? dtaylor Electrical Inspections 12 8/5/06 4:38 PM
Service Entrance Extension – Is It Kosher? DSuelflow Electrical Inspections 5 7/27/06 11:09 PM
Service Entrance Amperage? jfunderburk Electrical Inspections 18 6/16/06 11:16 PM


All times are GMT -4. The time now is 10:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts