Default Service entrance conductor

Can anybody tell me what the term kcmil means in terms of cable?
Reply With Quote
  #2  
Old 1/4/06, 9:48 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

KCMIL is a quantity of measure units; KCMIL is 1000 CMILS. All wire sizes larger than 4 ought AWG are given as KCMIL sizes. KCMIL wire size is the equivalent cross sectional area in thousands of circular mils. A circular MIL (CMIL) is the area of a circle with a diameter of one thousandth (0.001) of an inch, often termed CMA. Be aware that the wire sizes in the KCMIL system increase as the numbers get larger, which is exactly opposite from the AWG system.
Reply With Quote
  #3  
Old 1/4/06, 10:55 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,184
Default Re: Service entrance conductor

An excellent explantation, Bob.

When would I need this information.
Reply With Quote
  #4  
Old 1/4/06, 11:00 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

lol...If you do Residential Inspections....probably NEVER...lol

Online Definition...lol

Thousand Circular Mil; wire size for multiple stranded conductors over 4/0 AWG in diameter. Formerly MCM.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 1/4/06, 2:00 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

Quote:
Originally Posted by ecrofutt
An excellent explantation, Bob.

When would I need this information.
Thanks but I just grabbed it off the www.

You probably will not need that info.

4/0 takes us well into 200 amp services, above 200 amp services you might see conductors in kcmil
Reply With Quote
  #6  
Old 1/4/06, 6:25 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Service entrance conductor

How much max current is acceptable for 500 kcmil underground service that runs 350 feet from the transformer to the meter ?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 1/4/06, 6:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service entrance conductor

That would depend on the type (TW, UF, RHW, etc.) and material (AL or CU), but assuming there are not more than three current carrying conductors, the capacity can be from 260 amps to 430 amps (if I read the chart right).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 1/4/06, 10:38 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

Quote:
Originally Posted by bking
How much max current is acceptable for 500 kcmil underground service that runs 350 feet from the transformer to the meter ?
As much as the POCO says. Utilities do not follow NEC standards.
Reply With Quote
  #9  
Old 1/4/06, 11:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

Great point brian.... In that question the answer lies in that the local UTL company chooses unless you are rural where they do not run the lines from the pad or pole to the house then the electrician would have to calculate it.

Funny how I have seen service drops that are HALF the size of the SE conductors from the meter to the panel and the UTL company never questions it so to be honest I never question it as it is not my business to question them.....I only get concerned on MY end of the equation.

Actually.....for math sake the amps on the 500KCMIL at 75 degrees is 380-400Amps in copper.

Jeff I think you used 60 degree factors in their, it is over 100A it needs to be at 75 degrees and can actually be used at the 90 degree if correction factors are going to be applied.

Anyway...assuming WE have to run the 500 KCMIL to a 400A service and they are using Copper....which happens alot.....

Ok.....at 400A going 350' and 500KCMil....the voltage drop would only by 3% and if using Alum you would have to adjust for it as well and increase wire size to account for it....Now this is RAW since nothing else has been figured in like correction factors for Temps.

I can say most of the runs for a properly placed PAD or POLE will not be 350'...but with all things said it is possible and in rural areas you have to consider it being a real possibility.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 1/4/06 at 11:25 PM..
Reply With Quote
  #10  
Old 1/4/06, 11:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service entrance conductor

Quote:
Originally Posted by pabernathy
Jeff I think you used 60 degree factors in their, it is over 100A it needs to be at 75 degrees and can actually be used at the 90 degree if correction factors are going to be applied.
Are you kidding Paul? Do you really think I did the math ?

I posted info directly from 310.16



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 1/5/06, 12:36 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

lol....I got ya brother.....Just use the 75 Degree and 90 Degree columns for the most part..unless you are having issues with terminal ratings that call for the 60 degree column to be used.

Most cases we use 75 degree unless a correction is needed then the 90 degree column can be used.

Your subtle point is also GREAT.....HI's generally dont need to worry about that....lol..You would HOPE the local AHJ checked that but heck in west virginia you never know...OH WAIT...I dont want to affend any West Virginians...Sorry Joe Ferry...tehehehhehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 1/5/06, 12:41 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Service entrance conductor

I was referring to AL in my prev. post

The temp. rating is unknown but with it underground I am not concerned with any heat rise for a residential application.

I'm not sure of the voltage at the transformer but its 120V at the panels with around 80 amps load.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 1/5/06, 12:46 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

Quote:
Originally Posted by bking
How much max current is acceptable for 500 kcmil underground service that runs 350 feet from the transformer to the meter ?
Dude.....are you SURE its 120V at the panel and 80A load....and they used 500 kcmil....?????

Now......those figures do not make any sense to me ( 500KcMil for those figures )..sorry I must be missing something here.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 1/5/06, 12:48 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

Quote:
I'm not sure of the voltage at the transformer but its 120V at the panels with around 80 amps load.
This is the part that is confusing.....your post for 500KCMil is certainly not going to be used in the above situation...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 1/5/06, 1:09 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Service entrance conductor

120V approx per leg and 80 amps per 120v leg under operation, max rating 400A via two 200A panels.

why was this hard to understand?
think residential homes...... were HI's



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Service entrance and a raised garden tjansson Electrical Inspections 18 9/7/07 9:47 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 3:40 PM
Service Entrance Amps? dtaylor Electrical Inspections 12 8/5/06 4:38 PM
Service Entrance Amperage? jfunderburk Electrical Inspections 18 6/16/06 11:16 PM


All times are GMT -4. The time now is 12:27 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts