Default Re: Service entrance conductor

lol........hard to understand when you say 120V and 80A.......

Always use 120/240 and Total Amps..lol

Also much easier to say in the original post...about the 500kcMil that it feeds (2) 200A panels for 400Amps...lol.....

In this case the 500 KcMil is very normal and seen almost all the time and installed in most cases by the POCO....we use Utly down here but I like the sound of POCO better..lol



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #17  
Old 1/5/06, 9:44 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

o.k..... call me IGNINT, but what's POCO?
Reply With Quote
  #18  
Old 1/5/06, 9:48 PM
gmartin2 gmartin2 is offline
New User
 
Join Date: Nov 2005
Location: duluth, mn
Posts: 32
Please Note: gmartin2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

Power Company?
Reply With Quote
  #19  
Old 1/5/06, 10:00 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

Quote:
Originally Posted by gmartin2
Power Company?
oh......thanx.
Reply With Quote
  #20  
Old 1/5/06, 10:51 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: FL panhandle
Posts: 3,725
Default Re: Service entrance conductor

Not to be confused with "Pogo" sage of the swamp.
Reply With Quote
  #21  
Old 1/6/06, 6:50 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: Service entrance conductor

It has been mentioned but it bares repeating.

In my opinion HIs should not even concern themselves with service conductors under the control of the power company.

How do you know what conductors are under the NEC and what conductors are under the utility?

It has to do with the location of what is called the Service Point

Quote:
Service Point. The point of connection between the facilities of the serving utility and the premises wiring.
Now for overhead services 99% of the time this service point is the splice at the weather head.

For underground services 99% of the time the service point is the line side terminals of the electric meter.

That applies even in areas where the electrician has to install the conductors from that meter to the utility.

BUT...each power company and state utility commission can have there own rules, the only way you can be 100% certain of the service point is to check with the Utility commission.

It is not unusual at all for the power company to run a conductor that is 50% the size of the conductor that the electrician is required to run.

DO NOT BE CONCERNED WITH THIS.

The power company knows what they are doing and if this smaller conductor under their control was to fail they will be out to fix it at no cost to the homeowner.

I installed an 800 amp service in a 30 unit apartment building, it connected to what I would call 200 amp power company service conductors, that was 15 or 20 years ago and as far as I know it is still fine.

How?

Easy, the 800 amp service in this building required by the NEC service calculations is grossly over sized. The power company knows this, they use demand histories to determine what will be sufficient.

Last edited by Bob Badger; 1/6/06 at 6:57 AM..
Reply With Quote
  #22  
Old 1/6/06, 8:11 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,431
Default Re: Service entrance conductor

Quote:
Originally Posted by Bob Badger
In my opinion HIs should not even concern themselves with service conductors under the control of the power company.
When you're speaking of the size of the service conductors, I agree completely.

However, when we see deteriorated or damaged conductors, or conductors wrapped around tree branches (or other obvious safety concerns) we should certainly report the condition.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #23  
Old 1/6/06, 8:19 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: Service entrance conductor

Quote:
Originally Posted by jpope
When you're speaking of the size of the service conductors, I agree completely.

However, when we see deteriorated or damaged conductors, or conductors wrapped around tree branches (or other obvious safety concerns) we should certainly report the condition.
Yes I agree, all safety concerns should be reported.

I guess my point would be is that the size of the power company's conductors is not a safety issue.
Reply With Quote
  #24  
Old 1/6/06, 8:31 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,688
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

lol....BOB...I see you have a new haircut..thehehehe....



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #25  
Old 1/6/06, 8:58 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Cool Re: Service entrance conductor

Quote:
Originally Posted by pabernathy
lol....BOB...I see you have a new haircut..thehehehe....


Yeah, it fits my personality better.

He is also Tattooed on my shoulder.
Reply With Quote
  #26  
Old 1/6/06, 11:58 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,688
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service entrance conductor

lol......

The comment on the 800A service is correct in that we see this all the time. Now take a new electrician in the field and they see this smaller 4/0 service coming down to a Aux. Gutter and then hiting a bank of meters and so on....and then the electrician ( green one mind you ) and walks in and sees the size conductors needed on the so called "OUR SIDE" of the job....they freak out....

Just takes time to understand them and know that POCO ( Utly ) work on their own rules and regulations.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #27  
Old 1/6/06, 2:53 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: Service entrance conductor

Bob,

An illustation to your overhead se cable size point.

tg
Attached Thumbnails
service-entrance-conductor-sec-small-.jpg.JPG
Views:	20
Size:	47.0 KB
ID:	273  
Reply With Quote
  #28  
Old 1/6/06, 7:19 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,396
Default Re: Service entrance conductor

Some heat pumps cause some dimming of the lights when they first turn on.
This can be more noticeable at night for obvious reasons.

Some of the hvac makers have had complaints on this. It is many times due to long runs from the transformer to the house and even with 500 kcmil feeders.

Anyone have any good data on this surge current stuff?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207

"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #29  
Old 1/6/06, 7:58 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

You already have the jest of it.

The instant power is applied to a motor you have what is called locked rotor current. All that means is the powers on but the motor is stationary.

The current immediately jumps, typically to about 6 times the full load amps. So if you have a heat pump with an FLA of 20 the starting load will be in the neighborhood of 120 amps. Unless the transformer is reasonably close you will see the lights dim for a moment till the motor is up to speed, the start up current drops almost as quickly as it rises. However incandescent lights are very sensitive to voltage fluctuations and our eyes are very good at seeing it.

The best, pretty much only fix short of moving the transformer is the installation of a 'soft start' on the heat pump. Instead of a contactor applying full voltage all at once a soft start will apply the voltage slowly which limits the high start up current.

Once you get into bigger motors 'across the line starts' are pretty much imposable as the start up currents effect the rest of the electrical system to severely.

The company I work for had to do a hard start of a 500 HP motor that had a FLA of about 525 amps so the Locked rotor would be in the area of 3000 amps. Long story short the power company paid us a visit and was none to happy with us. We effected good size area of RI.

Last edited by Bob Badger; 1/6/06 at 8:05 PM..
Reply With Quote
  #30  
Old 1/6/06, 9:46 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service entrance conductor

That service point picture does a good job of demonstrating the NESC side vs the NEC side. That looks like #2 triplex on the drop and 4/0 on the SE.
The #2 triplex is pretty much all you ever see on a dwelling here. It doesn't matter if it is a single wide trailer with a 60a service or a 4000 square foot McMansion.
FPL did a sweep 20-25 years ago and swapped them all out from the 3 separate strands on insulators. Everyone got the same thing.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 7:57 AM
Service entrance and a raised garden tjansson Electrical 18 9/7/07 8:47 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical 5 12/4/06 2:40 PM
Service Entrance Amps? dtaylor Electrical 12 8/5/06 3:38 PM
Service Entrance Amperage? jfunderburk Electrical 18 6/16/06 10:16 PM


All times are GMT -4. The time now is 12:01 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts