Default Service Entrance Conductors Concealed

Service drop is at left rear corner. Meter is at right rear corner. Conductors are hidden as they run from one corner of house to the other by a room additon and vinyl siding that was added. Is this acceptable? I think not, and searched the board but was overwhelmed with the query return. Thanks for your help. A C0*e reference would also be appreciated (can't find it in E3505).

service-entrance-conductors-concealed-083106-030-small-.jpg.jpg
Views:	204
Size:	21.0 KB
ID:	5357



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 8/31/06, 11:43 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Service Entrance Conductors Concealed

If the exposed portion looks ok I would not be concerned but you might note that the cable is not all visible for inspection.
Reply With Quote
  #3  
Old 9/1/06, 11:35 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Entrance Conductors Concealed

Quote:
Originally Posted by jfunderburk
Service drop is at left rear corner. Meter is at right rear corner. Conductors are hidden as they run from one corner of house to the other by a room additon and vinyl siding that was added. Is this acceptable? I think not, and searched the board but was overwhelmed with the query return. Thanks for your help. A C0*e reference would also be appreciated (can't find it in E3505).

Attachment 5357
This is not acceptable according to NEC 230.6.

Search for: "Conductors Considered Outside the Building."

PS: I would take a look in the spaces above the concealed run, if they are accessible in an "attic, or crawl" space, and look for "illegal tapping", just to put my mind at ease.
Reply With Quote
  #4  
Old 9/1/06, 11:43 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Entrance Conductors Concealed

Quote:
Originally Posted by jtedesco1
This is not acceptable according to NEC 230.6.
Joe - 230.6 is a defining reference. Can you explain how this is unacceptable or prohibited by the section you provided?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 9/2/06, 9:32 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Entrance Conductors Concealed

Jeff:

This concealed Type SE cable assembly is now a defect, because it is not visible, and would be the subject of the investigation if there was a fire. See the Definition of Concealed.

If we could see the entire length, as it was before it was covered up (concealed) and the service point of connection at the drip loop, it may be possible that it was changed (buried splice) from one type to another type of cable.

230.6 is the rule that considers: "Unprotected SEC's" and is why it gives us some different methods that will show where the SEC's are outside of the building. I am sure that some firefighters have experiences that will support the hazard.

I posted a message here:

ELECTRICAL FIRES AND THEIR CAUSES

I will monitor this site too, and also suggest that we read Chapter 18 of NFPA 921 available for reveiw here:

NFPA 921: Guide for Fire and Explosion Investigations, 2004 Edition

Preview this document.

Last edited by jtedesco1; 9/2/06 at 10:16 AM..
Reply With Quote
  #6  
Old 9/2/06, 1:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Entrance Conductors Concealed

Are you citing the length of the concealment, or the concealment itself? Most SEC's are concealed to some extent.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 9/2/06, 1:23 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Service Entrance Conductors Concealed

I was concerned as the cable was not visible or apparent. Construction had covered it when they added a covered back porch. Think what would happen if someone drives a nail into the upper wall of the back porch and hits that cable!

Here's what I said in my report: "The service entrance conductors are concealed and inaccessible. We recommend that the electric utility
evaluate the installation of the service entrance conductors and repair as deemed necessary."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 9/2/06, 2:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Entrance Conductors Concealed

Concealed (as defined by the NEC).


Rendered inaccessible by the structure or finish of the building. Wires in concealed raceways are considered concealed, even though they may become accessible by withdrawing them.

As I said, most, if not all, service entrance conductors are concealed to some extent. In fact, NEC 300.37 requires concealment of the SEC's.


I don't beleive that "concealment" is an issue here. I don't have the NFPA to reference, so I hope that Joe will provide the applicable section here.

Even the "length" of the SEC's is subjectively "allowed" by the NEC, as there are no specific requirements set forth that I am aware of (other than "as close as possible").

Can you be more specific Joe T.? I see this often and would like a solid reference.





IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 9/2/06 at 2:41 PM..
Reply With Quote
  #9  
Old 9/2/06, 2:54 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Entrance Conductors Concealed

Quote:
Originally Posted by jfunderburk
I was concerned as the cable was not visible or apparent. Construction had covered it when they added a covered back porch. Think what would happen if someone drives a nail into the upper wall of the back porch and hits that cable!

Here's what I said in my report: "The service entrance conductors are concealed and inaccessible. We recommend that the electric utility
evaluate the installation of the service entrance conductors and repair as deemed necessary."
The service entrance cables between the meter and the weatherhead are the responsibility of the homeowner. As such the homeowner or buyer, as the case may be, is responsible to correct such defects.
You pointed out what could be a large expense to the buyer. A new service in this area usually runs $1000-1500.
Reply With Quote
  #10  
Old 9/2/06, 6:35 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Entrance Conductors Concealed

Quote:
Originally Posted by jfunderburk
I was concerned as the cable was not visible or apparent. Construction had covered it when they added a covered back porch. Think what would happen if someone drives a nail into the upper wall of the back porch and hits that cable!

Here's what I said in my report: "The service entrance conductors are concealed and inaccessible. We recommend that the electric utility
evaluate the installation of the service entrance conductors and repair as deemed necessary."
Joe:

Good choice of words and identification of a problem.

Jeff:

I agree, but each installation must be considered individually such as new construction, existing, and remodels that always make the problems worse when the cable is covered up.

Joe's image shows some really old cable.
Reply With Quote
  #11  
Old 9/2/06, 9:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Entrance Conductors Concealed

Joe F. - is that a cable assembly or conduit?

If that is a cable assembly, I take back everything I said

My statements were made under the assumption that this was conduit we were looking at.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 9/2/06, 10:42 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Service Entrance Conductors Concealed

Cable assembly. Not conduit. Sorry I didn't make that clear.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 9/3/06, 12:46 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Entrance Conductors Concealed

I should have know from the size, but at a quick glance, I thought it was conduit



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 9/3/06, 12:48 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Service Entrance Conductors Concealed

Quote:
Originally Posted by jpope
I should have know from the size, but at a quick glance, I thought it was conduit
At a quick glance of the photo, I also assumed conduit was pictured.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #15  
Old 9/3/06, 1:33 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,954
Default Re: Service Entrance Conductors Concealed

Quote:
Originally Posted by jfunderburk
Service drop is at left rear corner. Meter is at right rear corner. Conductors are hidden as they run from one corner of house to the other by a room additon and vinyl siding that was added. Is this acceptable? I think not, and searched the board but was overwhelmed with the query return. Thanks for your help. A C0*e reference would also be appreciated (can't find it in E3505).

Attachment 5357
Concealed Feed in Canada must be incased in Cement or not allowed .
I do believe the main reason is it is to easy to steal power in a concealed area.
Open the conduit or strip the insulation .
Join a couple of Cables and free power.
Thats the main reason why Grow houses want under ground feed to the house .
Cut through the basement wall to the supply and wallah free power .
Roy Cooke ... Royshomeinspection.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service entrance and a raised garden tjansson Electrical Inspections 18 9/7/07 9:47 AM
Service Entrance jcampbell Electrical Inspections 9 10/30/06 1:14 AM
Another Service Entrance Amps Question pdickerson Electrical Inspections 2 8/7/06 4:39 PM
Service Entrance Amps? dtaylor Electrical Inspections 12 8/5/06 4:38 PM
Sizes for Service Entrance Conductors jtedesco1 Electrical Inspections 0 2/5/06 12:22 PM


All times are GMT -4. The time now is 3:48 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts