Service drop is at left rear corner. Meter is at right rear corner. Conductors are hidden as they run from one corner of house to the other by a room additon and vinyl siding that was added. Is this acceptable? I think not, and searched the board but was overwhelmed with the query return. Thanks for your help. A C0*e reference would also be appreciated (can't find it in E3505).
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#2
|
||||
|
||||
|
If the exposed portion looks ok I would not be concerned but you might note that the cable is not all visible for inspection.
|
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Search for: "Conductors Considered Outside the Building." PS: I would take a look in the spaces above the concealed run, if they are accessible in an "attic, or crawl" space, and look for "illegal tapping", just to put my mind at ease. |
|
#4
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff:
This concealed Type SE cable assembly is now a defect, because it is not visible, and would be the subject of the investigation if there was a fire. See the Definition of Concealed. If we could see the entire length, as it was before it was covered up (concealed) and the service point of connection at the drip loop, it may be possible that it was changed (buried splice) from one type to another type of cable. 230.6 is the rule that considers: "Unprotected SEC's" and is why it gives us some different methods that will show where the SEC's are outside of the building. I am sure that some firefighters have experiences that will support the hazard. I posted a message here: ELECTRICAL FIRES AND THEIR CAUSES I will monitor this site too, and also suggest that we read Chapter 18 of NFPA 921 available for reveiw here: NFPA 921: Guide for Fire and Explosion Investigations, 2004 Edition Preview this document. Last edited by jtedesco1; 9/2/06 at 10:16 AM.. |
|
#6
|
||||
|
||||
|
Are you citing the length of the concealment, or the concealment itself? Most SEC's are concealed to some extent.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
I was concerned as the cable was not visible or apparent. Construction had covered it when they added a covered back porch. Think what would happen if someone drives a nail into the upper wall of the back porch and hits that cable!
Here's what I said in my report: "The service entrance conductors are concealed and inaccessible. We recommend that the electric utility evaluate the installation of the service entrance conductors and repair as deemed necessary." “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#8
|
||||
|
||||
|
Concealed (as defined by the NEC). Rendered inaccessible by the structure or finish of the building. Wires in concealed raceways are considered concealed, even though they may become accessible by withdrawing them. As I said, most, if not all, service entrance conductors are concealed to some extent. In fact, NEC 300.37 requires concealment of the SEC's. I don't beleive that "concealment" is an issue here. I don't have the NFPA to reference, so I hope that Joe will provide the applicable section here. Even the "length" of the SEC's is subjectively "allowed" by the NEC, as there are no specific requirements set forth that I am aware of (other than "as close as possible"). Can you be more specific Joe T.? I see this often and would like a solid reference. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 9/2/06 at 2:41 PM.. |
|
#9
|
|||
|
|||
|
Please Note:
smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
You pointed out what could be a large expense to the buyer. A new service in this area usually runs $1000-1500. |
|
#10
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Good choice of words and identification of a problem. Jeff: I agree, but each installation must be considered individually such as new construction, existing, and remodels that always make the problems worse when the cable is covered up. Joe's image shows some really old cable. |
|
#11
|
||||
|
||||
|
Joe F. - is that a cable assembly or conduit?
If that is a cable assembly, I take back everything I said My statements were made under the assumption that this was conduit we were looking at. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Cable assembly. Not conduit. Sorry I didn't make that clear.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#13
|
||||
|
||||
|
I should have know from the size, but at a quick glance, I thought it was conduit
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#14
|
||||
|
||||
|
Quote:
Joseph P. Hagarty, CMI joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#15
|
||||
|
||||
|
Quote:
I do believe the main reason is it is to easy to steal power in a concealed area. Open the conduit or strip the insulation . Join a couple of Cables and free power. Thats the main reason why Grow houses want under ground feed to the house . Cut through the basement wall to the supply and wallah free power . Roy Cooke ... Royshomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Service entrance and a raised garden | tjansson | Electrical Inspections | 18 | 9/7/07 9:47 AM |
| Service Entrance | jcampbell | Electrical Inspections | 9 | 10/30/06 1:14 AM |
| Another Service Entrance Amps Question | pdickerson | Electrical Inspections | 2 | 8/7/06 4:39 PM |
| Service Entrance Amps? | dtaylor | Electrical Inspections | 12 | 8/5/06 4:38 PM |
| Sizes for Service Entrance Conductors | jtedesco1 | Electrical Inspections | 0 | 2/5/06 12:22 PM |