Ok, this is the 3rd time this week that I've seen a setup like this. The neutral feed is turned into a ground feed and pushed through the mass head. In the panel, of course, there is no neutral feed to be found and all the neutral circuit wires are connected at the same lug where the neutral feed should be. Is anyone else familiar with this sort of setup and help me understand why its not a good idea (assuming it's not)?
Thanks ahead of time! Last edited by ehyde; 6/7/07 at 4:27 PM.. |
|
#2
|
||||
|
||||
|
The service neutral is the "ground."
All equipment grounding conductors, neutrals (grounded conductors) and the grounding electrode are bonded to the service neutral at the service equipment. Past the point of the service equipment, the neutrals and grounds are separated. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#4
|
||||
|
||||
|
I'm not sure what constitutes a "conversion" in your mind, but the conductor is the same, regardless of what you're calling it.
It is the service-neutral from the transformer to the service equipment. The service-neutral acts as the grounded conductor and grounding conductor for the service equipment. Maybe I'm not stating it well (cuz I ain't no sparkie IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yeah, I'm not really seeing a problem here. What, in particular, concerns you?
"The neutral feed is turned into a ground feed", makes no sense, so you might need to explain that a bit. |
|
#6
|
|||
|
|||
|
Please Note:
ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Thanks for the post. |
|
#7
|
||||
|
||||
|
Quote:
A conductor is a conductor is a conductor. Solid does not mean "ground" and multi-strand does not mean "neutral." They are simply different types of conductors. The conductor (in this case) is the service neutral, which runs from the transformer to the service panel, regardless of whether it's solid or multi-strand or a combination of both. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
What about 310.3?
|
|
#9
|
||||
|
||||
|
Well that's something else altogether. I've never even considered that, but now it's etched in my mind and I will be on the look-out. . .
310.3 Stranded Conductors. Where installed in raceways, conductors of size 8 AWG and larger shall be stranded. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Electrical Safety Foundation International Links | jtedesco1 | Electrical | 5 | 12/8/07 4:10 PM |
| Cloth service entrance... | wwarner | Electrical | 5 | 4/19/07 12:55 AM |
| Service panel Question | cpetty | Electrical | 4 | 1/24/07 10:36 PM |
| Service Entrance Amperage? | jfunderburk | Electrical | 18 | 6/16/06 11:16 PM |
| Service entrance conductor | jjackson | Electrical | 30 | 1/7/06 6:05 AM |