If the service neutral is bonded to ground at the service panel, does a short to ground at the electrical mast result in any safety issue? What would have to go wrong for this manifest in an injury?
I found this at today's inspection and informed the cient and home owner, who was present. The owner called the utility, who arrived an hour later. The utility employee imformed the owner that it was not a problem and did not need to be fixed, though he did fix it after the owner asked him to. Comments please. |
| Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since the mast is bonded to the service neutral in the meter enclosure, electrically I don't really see a problem. But since the fix was simple one it doesn't hurt to keep it isolated.
|
|
#3
|
|||
|
|||
|
I am not sure I see a problem either, but I suspect there probably is one even if I don't understand it. The code would not require the service neutral to be isolated from the service mast without a good reason. anyone know the reason?
I suppose if the service neutral is grounded at the main panel and also shorted to the mast, then a significant amount of current will pass from the neutral bus bar in the main panel, into the panel enclosure, up the service mast conduit, and then back into the service neutral conductor through the short at the insulator on the mast. The conduit should not carry current. Also, a poor connection at the short circuit could result in arcing. Did I just answer by own question? Last edited by pdickerson; 3/6/10 at 11:12 PM.. |
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I've given this some more thought. Since the neutral is now connected to the mast it will allow the conduit to carry some of the neutral current since the conduit is a parallel path with the neutral. This should be avoided if possible. Metallic service raceways will always have this problem. For example a metal nipple between the meter enclosure and the service panel will always carry some of the neutral current since the meter enclosure and the panel have the neutral bonded directly to each metal enclosure.
In the photo since the neutral will have a much lower impedance than the rusted connection of the service drop it's likely that the conduit will carry very little current. It still should be avoided and Paul was correct to point out that it needed to be corrected. |
|
#5
|
|||
|
|||
|
If it was OK for the neutral conductor to be in contact with the mast, then why would they use an insulator in the first place. Every system shouls have only one grounding connection.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#7
|
|||
|
|||
|
Just goes to show the power of the utility industry lobby ! They don't have to abide by the NEC anyway.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#8
|
|||
|
|||
|
Robert,
Thank you for the code section post. That is news to me. I don't believe I have every seen a bare service neutral wire, and I am surprised the code allows this given the obviouse parallel path of neutral current through the service mast. Can one of our resident experts confirm that we are applying the code section correctly here? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Service box ground | mnicholet | Electrical Inspections | 6 | 5/5/08 9:04 AM |
| Difficult Chimneys | thance | Inspecting HVAC Systems | 2 | 1/29/08 8:16 PM |
| Electricians Check List | pabernathy | Electrical Inspections | 74 | 12/5/07 6:39 PM |
| Proposed Definition of Neutral Conductor and Point | jtedesco1 | Electrical Inspections | 1 | 4/22/06 10:19 AM |