Default Service Neutral Shorted to Mast

If the service neutral is bonded to ground at the service panel, does a short to ground at the electrical mast result in any safety issue? What would have to go wrong for this manifest in an injury?

I found this at today's inspection and informed the cient and home owner, who was present. The owner called the utility, who arrived an hour later. The utility employee imformed the owner that it was not a problem and did not need to be fixed, though he did fix it after the owner asked him to.

Comments please.
Attached Thumbnails
service-neutral-shorted-mast-p1200451.jpg   service-neutral-shorted-mast-p1200467.jpg  
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/6/10, 8:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Neutral Shorted to Mast

Since the mast is bonded to the service neutral in the meter enclosure, electrically I don't really see a problem. But since the fix was simple one it doesn't hurt to keep it isolated.
Reply With Quote
  #3  
Old 3/6/10, 10:51 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Service Neutral Shorted to Mast

I am not sure I see a problem either, but I suspect there probably is one even if I don't understand it. The code would not require the service neutral to be isolated from the service mast without a good reason. anyone know the reason?

I suppose if the service neutral is grounded at the main panel and also shorted to the mast, then a significant amount of current will pass from the neutral bus bar in the main panel, into the panel enclosure, up the service mast conduit, and then back into the service neutral conductor through the short at the insulator on the mast. The conduit should not carry current. Also, a poor connection at the short circuit could result in arcing. Did I just answer by own question?

Last edited by pdickerson; 3/6/10 at 11:12 PM..
Reply With Quote
  #4  
Old 3/7/10, 7:03 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Neutral Shorted to Mast

I've given this some more thought. Since the neutral is now connected to the mast it will allow the conduit to carry some of the neutral current since the conduit is a parallel path with the neutral. This should be avoided if possible. Metallic service raceways will always have this problem. For example a metal nipple between the meter enclosure and the service panel will always carry some of the neutral current since the meter enclosure and the panel have the neutral bonded directly to each metal enclosure.

In the photo since the neutral will have a much lower impedance than the rusted connection of the service drop it's likely that the conduit will carry very little current. It still should be avoided and Paul was correct to point out that it needed to be corrected.
Reply With Quote
  #5  
Old 3/7/10, 11:13 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Service Neutral Shorted to Mast

If it was OK for the neutral conductor to be in contact with the mast, then why would they use an insulator in the first place. Every system shouls have only one grounding connection.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 3/8/10, 9:55 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Neutral Shorted to Mast

Quote:
Originally Posted by fnewman View Post
If it was OK for the neutral conductor to be in contact with the mast, then why would they use an insulator in the first place. Every system shouls have only one grounding connection.
It's funny we all agree that this should have been fixed but the NEC doesn't really seem to care about it. In fact in the NEC the grounded service entrance conductor is permitted to be bare when within the service raceway.

Quote:
230.41 Insulation of Service-Entrance Conductors.
Service-entrance conductors entering or on the exterior of buildings or other structures shall be insulated.
Exception: A grounded conductor shall be permitted to be uninsulated as follows:
(1) Bare copper used in a raceway or part of a service cable assembly.
Reply With Quote
  #7  
Old 3/8/10, 2:27 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Service Neutral Shorted to Mast

Just goes to show the power of the utility industry lobby ! They don't have to abide by the NEC anyway.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 3/8/10, 7:38 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Service Neutral Shorted to Mast

Robert,

Thank you for the code section post. That is news to me. I don't believe I have every seen a bare service neutral wire, and I am surprised the code allows this given the obviouse parallel path of neutral current through the service mast. Can one of our resident experts confirm that we are applying the code section correctly here?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Service box ground mnicholet Electrical Inspections 6 5/5/08 9:04 AM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 6:39 PM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM


All times are GMT -4. The time now is 8:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts