Can anyone show me where or how this service panel is bonded to ground?
Thanks.
Attached Thumbnails
service-panel-bonding-ground-img_9460-small-.jpg.jpg
Views:	1172
Size:	34.6 KB
ID:	16730   service-panel-bonding-ground-img_9461-small-.jpg.jpg
Views:	1179
Size:	51.9 KB
ID:	16731   service-panel-bonding-ground-img_9462-small-.jpg.jpg
Views:	1028
Size:	45.5 KB
ID:	16732   service-panel-bonding-ground-img_9463-small-.jpg.jpg
Views:	1026
Size:	48.4 KB
ID:	16733  
Reply With Quote
  #2  
Old 12/16/07, 7:17 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

Hey fella........it appears there is a 4 AWG or 6 AWG on the lower right side of the grounded/grounding buss. That could be your grounding to a Ufer if 4 AWG oe Rods if 6 AWG.... Now i am answering this on my motorola Q phone so i cant see it real well....

1) Did you check to make sure a bonding jumper was installed...either by screw or strap...i just cant see the image well.

2) always remember in your main service panel look for that enclosure bond....and check the bare conductors and their size.......look for connections for a Ufer or Rods at or near the meter outside.

FYI - it looks like the main bonding jumper is missing........grounding may be present but the isue may be the bonding of the enclosure .



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #3  
Old 12/16/07, 7:25 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Service panel bonding to ground

Paul is referring to this solid #6 AWG.

"Click To Enlarge"
service-panel-bonding-ground-img_9461-20-28small-29.jpg

Did you check at the water main?
Reply With Quote
  #4  
Old 12/16/07, 7:28 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

The bond screw is missing. It goes in that empty hole just to the right of the right hand service conductor.

There could be another bond wire connected to the panel somewhere, but I can't see it and it would not be a factory bond.
Reply With Quote
  #5  
Old 12/16/07, 7:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

Quote:
Originally Posted by dvalley
Paul is referring to this solid #6 AWG.

"Click To Enlarge"
Attachment 16734

Did you check at the water main?
I hope it is not 6 AWG going to the water main David....bein that this looks like a 200A panel...chances are 2/0 CU or 4/0 AL then the size would need to be 4 AWG......so if it is indeed 6 AWG......i would check for Rods....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 12/16/07, 7:40 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

That looks like #4 solid to me Paul. Problem is there is only one I can see.
There should be at least two in any case. Even if the water is just a bond and not used as an electrode.
Water/rod. Water/Ufer. Water/steel. Etc.
Reply With Quote
  #7  
Old 12/16/07, 7:42 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Service panel bonding to ground

Quote:
Originally Posted by pabernathy
I hope it is not 6 AWG going to the water main David....bein that this looks like a 200A panel...chances are 2/0 CU or 4/0 AL then the size would need to be 4 AWG......so if it is indeed 6 AWG......i would check for Rods....
I guess you have to be there to actually figure the size of the ground.
Reply With Quote
  #8  
Old 12/16/07, 7:46 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

The NEC Defines this as the: "Main Bonding Jumper" or as it appears in NEC Article 100:

"Bonding Jumper, Main. The connection between the grounded circuit conductor and the equipment grounding conductor at the service."
Reply With Quote
  #9  
Old 12/16/07, 7:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

Agreed fella.....i cant see much on this small 3 inch screen. If only one is present and it is 4 AWG then i would look for a Ufer....if that is present no other is needed unless it is indeed present like Peter said.....then they have to be tied together...

So we have to assume IF the water line coming in is metal.....if not increases the chances it is a Ufer......BUT any electrician who leaves out the bonding screw i begin to question many things....right know we know it is not bonded properly....since that is all we can see on that issue....we are grasping at straws....lol

Need more info from the OP



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 12/16/07, 7:57 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

Quote:
Originally Posted by pabernathy
......BUT any electrician who leaves out the bonding screw i begin to question many things....right know we know it is not bonded properly....since that is all we can see on that issue....we are grasping at straws....lol
Good point!


The only thing I could see is if the installer used #4 and went right from the water bond to a rod with the same #4. Unconventional but legal.
Reply With Quote
  #11  
Old 12/16/07, 8:05 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

very true Peter......there are many possible concepts....he/she could run 4 AWG to the water main piping....then go from it ( within 5 ' of entrance ) to a set of ground rods with 6 AWG we just dont see here....nothing says it has to come back to the panel shown...so we can thin of many ways........guess they are all assuming right now but YES it does concern me that no bonding jumper is present.........we think alike fella.....Thats a GOOD thing....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 12/16/07, 8:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

Keep in mind......if it is a Ufer as far as the grounding goes....you would only see one as supplimentals are not required for CEE .....

So it really depends on whats present.....if metal water piping in earth....yes needs a suppliment electrode...if not metal and only a CEE is used then only (1) 4 Awg would be needed.

This makes it soooo hard for electrical guys like Me, Peter, Joe, Greg and other electrical guys to guess without all the factors present.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 12/16/07, 8:33 PM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 93
Default Re: Service panel bonding to ground

That solid #6 AWG goes to a grounding rod.
In reference to the mentioned missing bond screw on the right:
1) this screw is supposed to go through to the panel box?
2) since there is a tie bar present, wouldn't the bond screw on the left suffice?
Reply With Quote
  #14  
Old 12/16/07, 8:38 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

You could also have the GEC coming out of the meter base, very popular here.
Reply With Quote
  #15  
Old 12/16/07, 8:40 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

1) this screw is supposed to go through to the panel box?
Yes.

2) since there is a tie bar present, wouldn't the bond screw on the left suffice?
That silver screw to the left is not a bond screw. It does not go through into the back box.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 293 2/10/08 2:20 AM
Service panel full of paper tags gwilcox Electrical Inspections 5 8/17/07 7:55 AM
Looking for comments on this service ground wire connection cbuell Electrical Inspections 6 2/8/07 7:27 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 9:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts