  #16  
Old 12/16/07, 7:44 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel bonding to ground

... and if the MBJ is a screw it is required to be a green screw.
Reply With Quote
  #17  
Old 12/16/07, 7:57 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

See....thats what makes NACHI great for HI's.....look at all you are learning from a single post....SEE......we do change the world...lol



Paul W. Abernathy
Reply With Quote
  #18  
Old 12/17/07, 11:18 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Service panel bonding to ground

Quote:
Originally Posted by dvalley
Paul is referring to this solid #6 AWG.

"Click To Enlarge"
Attachment 16734

Did you check at the water main?
The ground wires are doubled up at the bus bar when there are extra screws available.

Also should the ground and neutral be on the same bus?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #19  
Old 12/18/07, 12:31 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Service panel bonding to ground

Doubling up the equipment grounds is legal as long as they are the same size wire. The grounds and neutrals can be on the same bus in service equipment.
Reply With Quote
  #20  
Old 12/18/07, 5:41 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Service panel bonding to ground

Quote:
Originally Posted by rwashington
The ground wires are doubled up at the bus bar when there are extra screws available.

Also should the ground and neutral be on the same bus?
You're looking for separation of the grounds and neutrals only at LSE (sub panels).
Reply With Quote
  #21  
Old 12/18/07, 8:27 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

Quote:
Originally Posted by rwashington
The ground wires are doubled up at the bus bar when there are extra screws available.

Answer: Yes, if the panel legend allows this. However, pleases don't confuse "Grounded" and " Grounding"....just to be clear here...so if you mean ground as in the bare conductors....yes, it is allowed per the legend. No, if you are speaking in terms of the " Grounded " white conductors...they should never share a termination as per 408.21 - 2002 NEC ( 408.41 -2005 NEC ).

Also should the ground and neutral be on the same bus?

Answer: Yes, in the MAIN distribution panel.....NO, if you are dealing with a remote distribution panel down stream of the main panel. View my video on Grounding and Bonding at www.theelectricalguru.com on the video page.
Enjoy....Someone probably covered it but you know you like my version better....thehehehe



Paul W. Abernathy
Reply With Quote
  #22  
Old 12/18/07, 10:25 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Service panel bonding to ground

Thanks fellas. I shall be spending alot more time on this thread.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #23  
Old 12/18/07, 2:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service panel bonding to ground

Quote:
Originally Posted by rwashington
Thanks fellas. I shall be spending alot more time on this thread.
Nah...just know you got us watchin your back brother...we are always here for you.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Service panel full of paper tags gwilcox Electrical Inspections 5 8/17/07 6:55 AM
Looking for comments on this service ground wire connection cbuell Electrical Inspections 6 2/8/07 6:27 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts