I recently inspected a property where the basement had been remodeled. The service and sub panels created an obstacle as far as an eye sore for finishing the basement. The homeowner's solution was to enclose the panels in a closet door and frame.
![]() When closed, there is absolutely no clearance (OK maybe an inch or two) between the door face and the deadfront. This remodel took place within the last few years. An electrician stated in his estimate that clearance was acceptable at time of installation. I totally disagree. Thoughts? Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
A door is NOT a permanent barrier and does NOT impede on clearances. If, when the door is open, you retain proper clearances it is absoluetly fine. |
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is exactly the way my electric closet is. With the door open I have working space with an inch or so to spare. The door swing tends to enforce the depth of the working space as long as you don't block the door
|
|
#4
|
||||
|
||||
|
A stack of storage containers in front of a service panel isn't permenant either. Is this allowed?
Let me add to my first post that due to poor installation, the door required a great deal of effort and strength to open. After toying with it for a while, I discovered that by lifting up on the knob, the door would open easily. Does this change the barrier requirements? Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You are a home inspector, you can write up the door that is hard to open, just like you would if the bathroom door was sticking.
|
|
#6
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
William, I'm not sure what you are looking for. It seems like you simply want someone to agree with you.
|
|
#7
|
||||
|
||||
|
No. I just want clarification or explanation of why this is an acceptable installation.
I did write up the sticking door, but I also wrote it up as a clearance issue. Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
How about explaining why it is not acceptable.
Unless the door is 24" wide you made a mistake in writing it up. Sorry. |
|
#9
|
||||
|
||||
|
Quote:
Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#10
|
||||
|
||||
|
Quote:
I just want further explanation and I think I have it. Interpreting yours and Greg's explanation... as long as the door fully opens, required working space will be adequate. I suppose I should have commented on ease of access rather than clearance. Now I know. Thanks. Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#11
|
||||
|
||||
|
A hinged door does not inhibit the requirements for panels to be "readily accessible." A locked door, or a pile of items that would need to be moved, does inhibit the required access.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Quote:
This was part of my thoughts, except that I erroneously flagged it under the "working clearance" side of things. Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#13
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#14
|
||||
|
||||
|
Ditto what Jeff Pope said in his two posts.
NACHI 2005 U.S. Member of the Year
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Service Panel Quiz? | hmcclard | Electrical Inspections | 5 | 10/24/07 11:53 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Zinsco Service Disconnect Panel | pdickerson | Electrical Inspections | 7 | 9/16/06 11:59 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |