Default Service panel clearance

I recently inspected a property where the basement had been remodeled. The service and sub panels created an obstacle as far as an eye sore for finishing the basement. The homeowner's solution was to enclose the panels in a closet door and frame.
service-panel-clearance-pict0752.jpg

When closed, there is absolutely no clearance (OK maybe an inch or two) between the door face and the deadfront.

This remodel took place within the last few years. An electrician stated in his estimate that clearance was acceptable at time of installation.

I totally disagree.


Thoughts?




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #2  
Old 8/11/06, 2:56 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel clearance

Quote:
Originally Posted by wwarner
Thoughts?
Yes.
A door is NOT a permanent barrier and does NOT impede on clearances. If, when the door is open, you retain proper clearances it is absoluetly fine.
Reply With Quote
  #3  
Old 8/11/06, 3:08 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel clearance

That is exactly the way my electric closet is. With the door open I have working space with an inch or so to spare. The door swing tends to enforce the depth of the working space as long as you don't block the door
Reply With Quote
  #4  
Old 8/11/06, 3:10 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Service panel clearance

A stack of storage containers in front of a service panel isn't permenant either. Is this allowed?

Let me add to my first post that due to poor installation, the door required a great deal of effort and strength to open. After toying with it for a while, I discovered that by lifting up on the knob, the door would open easily. Does this change the barrier requirements?




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #5  
Old 8/11/06, 3:37 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel clearance

You are a home inspector, you can write up the door that is hard to open, just like you would if the bathroom door was sticking.
Reply With Quote
  #6  
Old 8/11/06, 3:38 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel clearance

William, I'm not sure what you are looking for. It seems like you simply want someone to agree with you.
Reply With Quote
  #7  
Old 8/11/06, 3:40 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Service panel clearance

No. I just want clarification or explanation of why this is an acceptable installation.

I did write up the sticking door, but I also wrote it up as a clearance issue.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #8  
Old 8/11/06, 3:48 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service panel clearance

How about explaining why it is not acceptable.

Unless the door is 24" wide you made a mistake in writing it up.
Sorry.
Reply With Quote
  #9  
Old 8/11/06, 3:50 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Service panel clearance

Quote:
Originally Posted by Greg Fretwell
That is exactly the way my electric closet is. With the door open I have working space with an inch or so to spare. The door swing tends to enforce the depth of the working space as long as you don't block the door
I can see this emphasizing working space with the door open. I guess I was looking at a safety standpoint when closed as innaccessible and a potential fire hazard.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #10  
Old 8/11/06, 4:07 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Service panel clearance

Quote:
Originally Posted by Speedy Petey
How about explaining why it is not acceptable.

Unless the door is 24" wide you made a mistake in writing it up.
Sorry.
Why are you sorry?

I just want further explanation and I think I have it. Interpreting yours and Greg's explanation... as long as the door fully opens, required working space will be adequate.

I suppose I should have commented on ease of access rather than clearance.

Now I know. Thanks.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #11  
Old 8/11/06, 4:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service panel clearance

A hinged door does not inhibit the requirements for panels to be "readily accessible." A locked door, or a pile of items that would need to be moved, does inhibit the required access.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 8/11/06, 4:23 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Service panel clearance

Quote:
Originally Posted by jpope
A hinged door does not inhibit the requirements for panels to be "readily accessible." A locked door, or a pile of items that would need to be moved, does inhibit the required access.
Understood, but in this instance of the door being very difficult to open, would you not indicate an accessibility problem, until corrected?

This was part of my thoughts, except that I erroneously flagged it under the "working clearance" side of things.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #13  
Old 8/11/06, 4:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service panel clearance

Quote:
Originally Posted by wwarner
Understood, but in this instance of the door being very difficult to open, would you not indicate an accessibility problem, until corrected?
Yes, I would.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 8/12/06, 1:07 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Service panel clearance

Ditto what Jeff Pope said in his two posts.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Service Panel Quiz? hmcclard Electrical Inspections 5 10/25/07 12:53 AM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Zinsco Service Disconnect Panel pdickerson Electrical Inspections 7 9/16/06 12:59 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts