Default service panel question

Seems like I should know this but........What thoughts does anyone have on a 150amp panel including a 100amp breaker to power a pole barn....usually see this as a subpanel but this breaker was installed as any other breaker would be. Properly installed cable/conduit out to the pole barn from the house. There is a 100amp panel in the barn that has about 8 breakers installed to run the barn.

It seemed odd to see it set up like this.......any issue with the general service for the house being 150a and having this 100a addition wired through the panel?

Thanks, Frank



Frank Buttermore
HTI Inspection Services, LLC
Howell, MI
www.htiinspectionservices.com
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/16/10, 4:07 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service panel question

There is no problem if the conductors/OCPD's and panel stabs are all the proper size. The service could be 150 amps and the pole barn could also be fed by a 150 amp feeder from the service. The real deciding factor is the connected load on the 150 amp service.
Reply With Quote
  #3  
Old 9/16/10, 4:12 PM
Frank J. Buttermore Frank J. Buttermore is offline
InterNACHI Member
 
Join Date: May 2005
Location: Howell, MI
Posts: 16
Default Re: service panel question

Typical 1400 foot ranch. Panel only about 50% used...100a would be plenty for the house itself and yes, everything appears to be correctly sized.



Frank Buttermore
HTI Inspection Services, LLC
Howell, MI
www.htiinspectionservices.com
Reply With Quote
  #4  
Old 9/16/10, 5:40 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service panel question

Like Robert said, no issue.
Reply With Quote
  #5  
Old 9/16/10, 11:11 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: service panel question

hmmm....so was this "barn" remote distribution panel in compliance with NEC 225.31, 225.32, 225.33 and 225.36?



Paul W. Abernathy
Reply With Quote
  #6  
Old 9/28/10, 6:01 PM
Frank J. Buttermore Frank J. Buttermore is offline
InterNACHI Member
 
Join Date: May 2005
Location: Howell, MI
Posts: 16
Default Re: service panel question

Thank you, Paul, for requiring me to do more homework. To your question, I would have to say yes, it does meet those requirements. I am accustomed to seeing a sub-panel directly next to the house panel, then the run starting from there. It still seems "wierd", but I guess it will work. BTW, there were a couple of issues that called for an electrician to correct and I asked that they have him take a look at this set-up and ensure it meets all requirements.

I don't post a lot, mostly just read them, but I sure get a lot of good advice from your posts and replies.

Thanks!



Frank Buttermore
HTI Inspection Services, LLC
Howell, MI
www.htiinspectionservices.com
Reply With Quote
  #7  
Old 10/3/10, 1:50 PM
dhuxted's Avatar
dhuxted dhuxted is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Orangeville, On.
Posts: 66
Default Re: service panel question

Just did a similar set up and is ok and approved by ESA here in Ontario
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Question Regarding Panel jevans Electrical Inspections 11 8/12/09 7:31 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM


All times are GMT -4. The time now is 8:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts