Question Service Panel question for board sparkies

Take a look at the SE cable bends inside the service panel. Are these bends too "tight"?

Is liquidtight FMC direct to service panel acceptable?

Can you bond (Service panel bonding) two seperate service panels (one bonded panel via screw) then take a conductor from that grounded /neutral buss to second unbonded service panel and connect to (grounded / neutral bus ) and consider that second service panel also panel bonded?? (hope that question is clear)

I know this was asked before but what is acceptable length of SE cable coming into the house? I have over 15 feet (guessing here).

Here is a pic of the service panel. Enjoy..
Attached Images
File Type: jpg 100_3585.JPG (33.7 KB, 104 views)

Last edited by pbolliger; 5/12/06 at 3:28 PM.
Reply With Quote
  #2  
Old 5/12/06, 5:32 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 1,586
Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information
Default Re: Service Panel question for board sparkies

I don't have a problem with the bending there...

I doubt that second panel is a service panel therefore the neutral and grounds must be seperate. Is it fed via that liquid tight conduit? If it is another service panel it should have its own neutral and ground to the meter base.

The length of the SE cable is location specific, here it is 10 feet of cable length max before an outside disconnect is required.
Reply With Quote
  #3  
Old 5/12/06, 7:17 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 567
Patrick Bolliger .
Send a message via Skype™ to pbolliger
Default Re: Service Panel question for board sparkies

Hey Bruce,

There are two separate service panels. Each panel gets it's own SEC. Its a two unit building so they have separate meters and service panels.

No "sub" panel here.

I read somewhere liquid tight FMC must have a grounding conductor within the conduit when greater then 6 feet in length and going to a motorized appliance like a compressor..hmmm


The SE cable might just fall within that distance..

Thanks for your input.
Reply With Quote
  #4  
Old 5/13/06, 1:49 AM
crane542 crane542 is offline
New User
 
Join Date: May 2006
Posts: 11
crane542 hasn't had much positive or negative feedback
Please Note: crane542 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Panel question for board sparkies

NEC says service must have grounding conductor attached to metalic water pipe, grounding electrode, or footer rebar. In your picture I don't see an appropriatly sized grounding conductor leaving the panel. The bending is ok and often times you will see these bent into a donut to get them into the lugs. The home panels don't give you much room to work in, they should all be sized like the commercial stuff. LFM requires a bonding wire if over 6' but in the picture it appears he attempted to satisfy this with the white wire ( highly unlikely that it's a neutral) but it should be striped or marked green to properly identify it.
Reply With Quote
  #5  
Old 5/13/06, 12:32 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Service Panel question for board sparkies

Quote:
Originally Posted by pbolliger
Take a look at the SE cable bends inside the service panel. Are these bends too "tight"?

Is liquidtight FMC direct to service panel acceptable?

Can you bond (Service panel bonding) two seperate service panels (one bonded panel via screw) then take a conductor from that grounded /neutral buss to second unbonded service panel and connect to (grounded / neutral bus ) and consider that second service panel also panel bonded?? (hope that question is clear)

I know this was asked before but what is acceptable length of SE cable coming into the house? I have over 15 feet (guessing here).

Here is a pic of the service panel. Enjoy..
A.) I don't also have too much of a problem with the bends on the SE, the best way to check this is the look at the insulation at the inner part of the ends...if it starts to kringle up and show compression it is too tight...versus having to actual measure the bend radius and what not.

B.) FMC....in general is fine.....except in regards to Service Equipment if over 6' and so on.....and requires a bonding wire......not sure in the image if the FMC actually goes to a service panel per say.....

C.) Bonding (2) service panels....if you are speaking of the method we use for a 400A service that has (2) 200 services fed from one outside meter cab....Sure....YOU bond them both as normal with the green ground screw..but you run a jumper between them to make them a continuous bond among themselves.......If you are speaking of a remote panel like a "SUB" or " Remote Distribution Panel"..No....should not be done.

D.) Question is on length of SE as it enters the dwelling from the meter cab...If I am gathering your question right....It must terminate in the SE panel at the closest point of entry...NOW...the NEC leaves that open a bit so the local AHJ will have to rull on that.....around here it fluxes from 3-5' in length before it would need a service disconnect ....

Hope that answered your questions.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #6  
Old 5/13/06, 12:57 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 567
Patrick Bolliger .
Send a message via Skype™ to pbolliger
Question Re: Service Panel question for board sparkies

Thanks Paul I was waiting for your input... I was hoping you were going to help me here.

I have two seperate meters for this setup. Two meters , two seperate service panels, one GEC to the "Chicago water pipe" method..
The first service panel is bonded with screw in bus to panel.
The second panel has the bonding screw removed and what looks like a "jumper" from 1st panel (grounded ) neutral bus to second panel neutral bus plus a fitting between panels . I am guessing here that was to complete bonding but is that acceptable? . Looks like 10AWG for GEC to water pipe for 100 amp service. ??? Does that fly??

The panels are new along with meters and "some parts" of wiring system but it looks as if the rest of the house wiring is possible original.. See J box pics and do you think there are pushing overfill wiring in these puppies??






Paul if you saw this place you would have to add it to your list of "what are they thinking "
Attached Images
File Type: jpg 100_3567.JPG (40.3 KB, 20 views)
File Type: jpg 100_3577.JPG (29.0 KB, 18 views)
Reply With Quote
  #7  
Old 5/14/06, 12:34 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 5,577
William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information
Default Re: Service Panel question for board sparkies

Pat; Gotta love the BX.

Chicago. No work done without permit and union electricians and letter from your alderman and a payoff to the precinct captain and a 'donation;' to the local "Firemans's protective league".

Then they allow BX.

Go figure.



Will Decker
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 5/14/06, 10:14 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 567
Patrick Bolliger .
Send a message via Skype™ to pbolliger
Default Re: Service Panel question for board sparkies

Yous got da right Will.

You should have seen this place... Will 111 years old...been through some bad times...

Take a look at my posting and pic here..

www.nachi.org/forum/showthread.php?t=4257&page=2
Reply With Quote
  #9  
Old 5/14/06, 10:24 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 5,577
William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information
Default Re: Service Panel question for board sparkies

Too good, Pat.



Will Decker
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Service panel Question cpetty Electrical 4 1/24/07 10:36 PM
Service wire size to breaker panel sfalvey Electrical 12 10/31/06 5:28 PM
Main service disonnect question jmichalski Electrical 5 1/29/06 5:32 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 6:28 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics