Default Service Panel Used As Junction Box

Attachment 5027Inspected a home yesterday that had a new addition added to the back, the old service panel is being used as a junction box as a new service was installed in the addition. This is a new one on me and not sure if this can be done or not, what do you think?



Great Lakes Home & Property Inspections
Utica MI 48317
http://www.greatlakesinspections.com

Last edited by mbazzo; 5/9/08 at 12:41 PM..
Reply With Quote
  #2  
Old 8/11/06, 1:21 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Service Panel Used As Junction Box

I have seen it done in the past as well. Before I did home inspections. I saw it in a home over in Hazel Park, MI.

I don't know the rules about this but would like to know what others think.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #3  
Old 8/11/06, 1:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Panel Used As Junction Box

So long as it's covered, it's not a problem. Was there a hinged cover in addition to the dead front?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 8/11/06, 1:31 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Panel Used As Junction Box

It is done quite often by DIYers and often suggested to them for some reason.
I don't care for this practice AT ALL and do not know why it is done so often.
To me it reeks of DIY, but if covered properly and not overloaded there is nothing illegal or unsafe about it.
Reply With Quote
  #5  
Old 8/11/06, 1:31 PM
Michael Bazzo, CMI Michael Bazzo, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Utica, MI
Posts: 1,564
Default Re: Service Panel Used As Junction Box

Yes a hinged cover was attached to the dead front. Not sure how well the dead front even with a loosly latched cover would contain a fire with out breakers helping to seal the can.



Great Lakes Home & Property Inspections
Utica MI 48317
http://www.greatlakesinspections.com

Last edited by mbazzo; 8/11/06 at 1:38 PM..
Reply With Quote
  #6  
Old 8/11/06, 1:36 PM
Michael Bazzo, CMI Michael Bazzo, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Utica, MI
Posts: 1,564
Default Re: Service Panel Used As Junction Box

Quote:
Originally Posted by Speedy Petey
I don't care for this practice AT ALL and do not know why it is done so often.
To me it reeks of DIY, but if covered properly and not overloaded there is nothing illegal or unsafe about it.
I don't like the looks of it either and certainly a dyi er at work. All those wire nuts made me alittle nervous as well. thought crimped connections would have been a better option.



Great Lakes Home & Property Inspections
Utica MI 48317
http://www.greatlakesinspections.com
Reply With Quote
  #7  
Old 8/11/06, 1:55 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,490
Default Re: Service Panel Used As Junction Box

Is there not a general provision in the code that prohibits the use of equipment for anything other than its designed purpose?
Reply With Quote
  #8  
Old 8/11/06, 2:10 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Panel Used As Junction Box

Quote:
Originally Posted by mbazzo
All those wire nuts made me alittle nervous as well. thought crimped connections would have been a better option.
I would not say that at all. A correct wire nut plice is as sound as anything else.
Crimping is the stuff of larger service conductors and stranded low-voltage wiring.
Reply With Quote
  #9  
Old 8/11/06, 2:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Panel Used As Junction Box

Quote:
Originally Posted by jbushart
Is there not a general provision in the code that prohibits the use of equipment for anything other than its designed purpose?
Yes, there is, and there is some contention as to whether or not splices and wire nuts are allowed in a panel board. It really comes down to the interpretation by the AHJ.

Typically, the conductors for the new service equipment are spliced at the existing panel (which is gutted) to the circuits. This is done by licensed EC's quite commonly.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 8/11/06, 2:18 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Panel Used As Junction Box

It is alright here, and in Commercial applications I liked to install, and use terminal strips. They look so much better
Reply With Quote
  #11  
Old 8/11/06, 2:45 PM
Peter Foxe Smothers's Avatar
Peter Foxe Smothers Peter Foxe Smothers is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Shreveport, LA
Posts: 912
Default Re: Service Panel Used As Junction Box

It is done by electricians all the time here.



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #12  
Old 8/11/06, 3:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Panel Used As Junction Box

Jeff, the panelboard was removed so this is just an enclosure. I have heard of AHJs who want the hinged cover screwed shut tho.
Reply With Quote
  #13  
Old 8/11/06, 4:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Service Panel Used As Junction Box

Quote:
Originally Posted by Greg Fretwell
Jeff, the panelboard was removed so this is just an enclosure. I have heard of AHJs who want the hinged cover screwed shut tho.
I know Greg, I was referencing the post by James where he commented on "listing and labeling." This used to be a "panelboard" enclosure and has been modified into a "junction box," which (technically) goes against its "listing and labeling."

Every time I have seen this condition, the hinged cover has been screwed shut as well.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 8/11/06, 5:42 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Panel Used As Junction Box

It was and still is a "CABINET" and according to its Listing and purpose is not a "JUNCTION BOX" and violates 110.3(B).

If further clarification is needed, the UL site www.ul.com includes a telephone number that can be called to clarify my personal opinion.

The Panelboard was removed from a Cabinet and although a common practice, is legally considered to be a conflict.

2006 UL White Book (large file - 5MB)

See Cabinets
Reply With Quote
  #15  
Old 8/11/06, 6:03 PM
Vern Mitchinson, CMI's Avatar
Vern Mitchinson, CMI Vern Mitchinson, CMI is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 1,998
Default Re: Service Panel Used As Junction Box

It is quite common here when Old houses that had fuse boxes are up dated to current standards. How ever the old fuse box is removed and a 6 x 6 x 3 metal box with screwed on cover is installed. Licensed Electricians and Electrical Inspectors have approved this so I do not question it.
Usually there are two or more circuits from the new panel connected inside the new box.
I do however wonder about the rule that forbids more then one circuit inside the same junction box.



Vern Mitchinson_CET_CMI
Past President
International Association of Certified Home Inspectors. Alberta Canada
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Service Panel Quiz? hmcclard Electrical Inspections 5 10/25/07 12:53 AM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Zinsco Service Disconnect Panel pdickerson Electrical Inspections 7 9/16/06 12:59 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 9:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts