  #1  
Old 4/4/08, 10:00 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 663
Default Service point on roof

This service point rests directly on the roof. I can't find any reg against this, but it doesn't seem right. Any thoughts?
Attached Thumbnails
service-point-roof-points.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 4/4/08, 10:24 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Service point on roof

That's just wrong!



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good

Last edited by badair; 6/2/09 at 1:56 AM..
Reply With Quote
  #3  
Old 4/4/08, 10:44 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 663
Default Re: Service point on roof

Barry - Thanks for your reply. The drop clearances here on Long Island are atypical in regards to what might be found in other areas. I was more concerned with the service point resting direcly on the roof.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 4/4/08, 10:45 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

Quote:
Originally Posted by bsmith
This service point rests directly on the roof. I can't find any reg against this, but it doesn't seem right. Any thoughts?
Clearance required

Last edited by jtedesco1; 6/12/08 at 5:38 PM..
Reply With Quote
  #5  
Old 4/4/08, 11:09 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 663
Default Re: Service point on roof

Excellent - Thanks Joe



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #6  
Old 4/4/08, 11:46 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

Barry's graphic only show span clearance. That does NOT apply to drip loops.

Joe's graphic shows the drip loop clearance but the graphic is misleading, the 18" number is an exception to the 36" clearance also for spans.

I cannot find anything prohibiting a drip loop from being lower than 18". A drip loop will ALWAYS be lower than the span itself, so if the span can be 18" then the loop can obviously be lower.

TRUE, this is a poor installation ans should be called out as such, but IMO I can't find anything that makes it "illegal".
Reply With Quote
  #7  
Old 4/4/08, 12:26 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Service point on roof

May be wrong but I was taught, thought I had known, and said,
"No lower than 36" above any roof surfaces."

Reroofing has to be taken into account and any less is just unsafe, imo.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #8  
Old 4/4/08, 12:32 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

It is code legal to have the drop 18" off the roof in some instances.

Like I said though, all these clearance codes refer to the "span", not simply "conductors".

Just for reference here is the applicable section of the NEC:

225.19 Clearances from Buildings for Conductors of Not Over 600 Volts, Nominal

(A) Above Roofs
Overhead spans of open conductors and open multiconductor cables shall have a vertical clearance of not less than 2.5 m (8 ft) above the roof surface. The vertical clearance above the roof level shall be maintained for a distance not less than 900 mm (3 ft) in all directions from the edge of the roof.

Exception No. 1: The area above a roof surface subject to pedestrian or vehicular traffic shall have a vertical clearance from the roof surface in accordance with the clearance requirements of 225.18.

Exception No. 2: Where the voltage between conductors does not exceed 300, and the roof has a slope of 100 mm in 300 mm (4 in. in 12 in.) or greater, a reduction in clearance to 900 mm (3 ft) shall be permitted.

Exception No. 3: Where the voltage between conductors does not exceed 300, a reduction in clearance above only the overhanging portion of the roof to not less than 450 mm (18 in.) shall be permitted if (1) not more than 1.8 m (6 ft) of the conductors, 1.2 m (4 ft) horizontally, pass above the roof overhang and (2) they are terminated at a through-the-roof raceway or approved support.

Exception No. 4: The requirement for maintaining the vertical clearance 900 mm (3 ft) from the edge of the roof shall not apply to the final conductor span where the conductors are attached to the side of a building.
Reply With Quote
  #9  
Old 4/4/08, 1:12 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Service point on roof

I'll stick with 36" and let a sparky or code official discredit me.

No dishonor in being wrong for the sake of safer practices.

I know and lived through a nightmare with an inspector that was named in a $25M lawsuit for wrongful death of an electrocuted plumber under a house.

Many notations in his report about feeders on soil, open j-boxes, NO GFCI protection... ...even left a note on the doors for anyone entering the premises...

Beyond code is not a criminal offense...yet...and the subject photo appears to be a tragedy waiting to happen to some poor schmuck trying to earn a living.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #10  
Old 4/4/08, 1:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

I would enforce that as the bottom of the drip loop part of the "span" had to be 18" above the roof. If it was touching the roof (or close) you could also call "physical damage". Swinging in the wind, it wouldn't take long for those shingles to damage tthe insulation.
Reply With Quote
  #11  
Old 4/4/08, 1:31 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

Quote:
Originally Posted by Greg Fretwell
I would enforce that as the bottom of the drip loop part of the "span" had to be 18" above the roof. If it was touching the roof (or close) you could also call "physical damage". Swinging in the wind, it wouldn't take long for those shingles to damage tthe insulation.
I agree! So much confusion by other code scholars!
Reply With Quote
  #12  
Old 4/4/08, 1:35 PM
Andrew MacDonald's Avatar
Andrew MacDonald Andrew MacDonald is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Elgin, IL
Posts: 166
Default Re: Service point on roof

I'm with Barry on this one... Just plain WRONG.



Andrew MacDonald
MacDonaldPropertyInspections.com
InsightThermalDiagnostics.com

ITC/FLIR Certified Building Science Thermographer
ITC/FLIR Certified Level 1 Thermographer


Reply With Quote
  #13  
Old 4/4/08, 2:31 PM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 511
Default Re: Service point on roof

based on the size appearance it probably needs to be upgraded anyway.
where does the service entrance go where it is out of the picture on the right?

CJ
Reply With Quote
  #14  
Old 4/4/08, 3:38 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

Just to note, I DID state:
Quote:
Originally Posted by Speedy Petey
TRUE, this is a poor installation ans should be called out as such,....
Reply With Quote
  #15  
Old 4/4/08, 8:45 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

Quote:
Originally Posted by jtedesco1
I agree! So much confusion by other code scholars!
Not really. The word "span" has a well defined definition in the electrical trade. The drip loop is not part of the span.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Unfamiliar newer floor structure -- span too long for engineered joists? fbartlo Structural 8 2/10/08 12:11 PM
Ice Gaurd membrane dmacy Exterior 36 6/14/07 1:21 AM
Help Determining Reportable Service Size cbarrows Electrical 8 7/19/06 8:12 PM
Moss growing on roof ecox1 Exterior 43 1/19/06 10:57 PM


All times are GMT -4. The time now is 5:09 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts