Default Re: Service point on roof

From the handbook

BTW note the word "span" is not used in the 18" exception

Quote:
Exception No. 3: Where the voltage between conductors does not exceed 300, a reduction in clearance above only the overhanging portion of the roof to not less than 450 mm (18 in.) shall be permitted if (1) not more than 1.8 m (6 ft) of service-drop conductors, 1.2 m (4 ft) horizontally, pass above the roof overhang, and (2) they are terminated at a through-the-roof raceway or approved support.
Attached Thumbnails
service-point-roof-image3.jpg  

Last edited by Greg Fretwell; 4/4/08 at 9:59 PM..
Reply With Quote
  #17  
Old 4/4/08, 10:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

Neither the NECH commentary or the accompanying illustrations modify the base code text. The exception is an exception to the base rule which does reference "span".
Reply With Quote
  #18  
Old 4/4/08, 10:33 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service point on roof

...and open multiconductor cables. I will simply fail the SE part past the service point.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Unfamiliar newer floor structure -- span too long for engineered joists? fbartlo Structural Inspections 8 2/10/08 11:11 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 7:12 PM
Moss growing on roof ecox1 Exterior Inspections 45 1/19/06 9:57 PM


All times are GMT -4. The time now is 8:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts