4/0 copper feed from meter to panel, 8 total breakers in this panel including a 150 amp disconnect for the panel directly to the right, (not pictured), fed with 2/0 copper, the neutral is visible as it is double tapped at the neutral lug for pictured panel. Is there any way to know what size the service amperage is?
|
| Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Where is the service disconnect? This appears to be wired as service equipment, so a disconnect would be required. That would likely give you a better indication of the capacity.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
So he is telling you to look at the main breaker on the meter panel and see how many amps it is rated for .(simple explanation)
|
|
#4
|
|||
|
|||
|
There is no main disconnect. No disconnect at the exterior meter panel (picture 1). Only disconnect is a 150 amp breaker with 2/0 copper (bottom of picture 2) that feeds distribution panel to the right of this panel (picture 3).
That is why I am having difficulty finding the service amperage. Note that the two 2/0 neutrals are double tapped at the main panel in the OP. This is the first time I've ever seen 4/0 copper in a panel. It was not marked 4/0 copper, but was noticeably larger than the 2/0 copper. |
|
#5
|
||||
|
||||
|
Great ,they can just switch out breakers live or pull the meter head.
"Electrician time". |
|
#6
|
||||
|
||||
|
4/0 CU is rated for 225 amps, but it's unlikely that panel is rated that high. The panel rating would be the limiting factor, but absent a service-disconnect, the point is moot. The installation needs to be corrected.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
sure that is not a sub panel, and the panel to the right is the main?
Something odd looking about the way the main conductors are routed. Last edited by bkelly2; 9/28/10 at 11:38 PM.. Reason: syntax |
|
#8
|
|||
|
|||
|
Yes, that was one of my concerns. Both panels were rated for 200 amps.
|
|
#9
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
My guess would be it is a 200 amp, if that is what both the boxes are set up for. Looks like the service panel has a 150 amp breaker for the interior distribution panel.
Those other breaker probably feed the AC, Pool, or other outside items. |
|
#10
|
||||
|
||||
|
was that meter box square? what is the meter rated at?
|
|
#11
|
||||
|
||||
|
It would be rated the same as the breaker in the main panel serving the sub, may be using over sized wire which is fine( service to the sub looks to me like it originates from the breaker in the main) Therefore the sub can not be more than the breaker that serves it.
|
|
#12
|
||||
|
||||
|
Yes Yes, but dont forget the main rule is that the service size is equal to the weakest link up to and including the panel
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| New Washington Legislation Submitted | gdomagala | Legislation, Licensing & Legal Issues for Inspectors | 294 | 2/10/08 1:20 AM |
| Question about Determining Electric Service Size | sbelda | General Inspection Discussion | 2 | 8/18/07 2:48 PM |
| How Do I Determine Electrical Svs Size (posted by Judy Thompson) | AskNACHI.org | AskNACHI.org Inspection Questions Forum | 3 | 8/10/07 4:03 PM |
| Size of service?? | cbuell | Electrical Inspections | 4 | 4/14/07 4:50 PM |
| Adequate service size....oh, and a GFCI question | ksherstobetoff | Electrical Inspections | 13 | 2/8/07 1:18 PM |