4/0 copper feed from meter to panel, 8 total breakers in this panel including a 150 amp disconnect for the panel directly to the right, (not pictured), fed with 2/0 copper, the neutral is visible as it is double tapped at the neutral lug for pictured panel. Is there any way to know what size the service amperage is?
Attached Thumbnails
service-size-hpim1832.jpg   service-size-hpim1830.jpg   service-size-hpim1831.jpg  
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/28/10, 6:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Service size is?

Where is the service disconnect? This appears to be wired as service equipment, so a disconnect would be required. That would likely give you a better indication of the capacity.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 9/28/10, 6:57 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Service size is?

So he is telling you to look at the main breaker on the meter panel and see how many amps it is rated for .(simple explanation)
Reply With Quote
  #4  
Old 9/28/10, 7:10 PM
Sidney Alstad Sidney Alstad is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Blue Ridge Mountains, NC
Posts: 124
Default Re: Service size is?

There is no main disconnect. No disconnect at the exterior meter panel (picture 1). Only disconnect is a 150 amp breaker with 2/0 copper (bottom of picture 2) that feeds distribution panel to the right of this panel (picture 3).

That is why I am having difficulty finding the service amperage. Note that the two 2/0 neutrals are double tapped at the main panel in the OP. This is the first time I've ever seen 4/0 copper in a panel. It was not marked 4/0 copper, but was noticeably larger than the 2/0 copper.
Attached Thumbnails
service-size-hpim1833.jpg   service-size-hpim1831.jpg   service-size-hpim1824.jpg  
Reply With Quote
  #5  
Old 9/28/10, 7:34 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Service size is?

Great ,they can just switch out breakers live or pull the meter head.
"Electrician time".
Reply With Quote
  #6  
Old 9/28/10, 9:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Service size is?

4/0 CU is rated for 225 amps, but it's unlikely that panel is rated that high. The panel rating would be the limiting factor, but absent a service-disconnect, the point is moot. The installation needs to be corrected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 9/28/10, 10:11 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Service size is?

sure that is not a sub panel, and the panel to the right is the main?

Something odd looking about the way the main conductors are routed.

Last edited by bkelly2; 9/28/10 at 11:38 PM.. Reason: syntax
Reply With Quote
  #8  
Old 9/28/10, 10:14 PM
Sidney Alstad Sidney Alstad is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Blue Ridge Mountains, NC
Posts: 124
Default Re: Service size is?

Quote:
Originally Posted by jpope View Post
4/0 CU is rated for 225 amps, but it's unlikely that panel is rated that high. The panel rating would be the limiting factor, but absent a service-disconnect, the point is moot. The installation needs to be corrected.
Yes, that was one of my concerns. Both panels were rated for 200 amps.
Reply With Quote
  #9  
Old 9/29/10, 9:56 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service size is?

My guess would be it is a 200 amp, if that is what both the boxes are set up for. Looks like the service panel has a 150 amp breaker for the interior distribution panel.
Those other breaker probably feed the AC, Pool, or other outside items.
Reply With Quote
  #10  
Old 9/29/10, 11:31 PM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: Service size is?

was that meter box square? what is the meter rated at?



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #11  
Old 10/3/10, 1:46 PM
dhuxted's Avatar
dhuxted dhuxted is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Orangeville, On.
Posts: 66
Default Re: Service size is?

It would be rated the same as the breaker in the main panel serving the sub, may be using over sized wire which is fine( service to the sub looks to me like it originates from the breaker in the main) Therefore the sub can not be more than the breaker that serves it.
Reply With Quote
  #12  
Old 10/3/10, 2:22 PM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: Service size is?

Yes Yes, but dont forget the main rule is that the service size is equal to the weakest link up to and including the panel



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Question about Determining Electric Service Size sbelda General Inspection Discussion 2 8/18/07 2:48 PM
How Do I Determine Electrical Svs Size (posted by Judy Thompson) AskNACHI.org AskNACHI.org Inspection Questions Forum 3 8/10/07 4:03 PM
Size of service?? cbuell Electrical Inspections 4 4/14/07 4:50 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM