Please tell me what you think about the service size for this house. It is 120/240 service drop. It is a smaller meter, but has listed 200cl on it. The SE conductors appear to be #2 AWG AL. The main panel (Cutler Hammer) is rated for 125 amps. There are 5 main disconnects that total 190 amps. 1969 house.

Also, what do you think about the black wire lugged with the ground at the bottom right of the main panel? And, also about the ground lugged with the neutrals on the neutral bus in the sub panel? Thanks in advance.
Attached Thumbnails
service-size-and-panels-elect-meter.jpg   service-size-and-panels-main-panel.jpg   service-size-and-panels-main-panel-2.jpg   service-size-and-panels-sub-panel-wires.jpg   service-size-and-panels-sub-panel-2.jpg  

Reply With Quote
  #2  
Old 4/15/07, 1:20 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service size and panels

First off, we all need to get off this whole "200CL" meter fixation. This has absolutely NO bearing on service size. This is simply the classicification of the meter that the POCO uses. 200CL means nothing to anyone but the POCO.

Second, the sum of the breakers is another absolutely useless number. This also has NO bearing on service size, capacity or draw.

The small black on the neutral bar is the neutral from the chime transformer. They sometimes used to come with two blacks for some reason. This is not an issue.

I'll let others comment on the rest.
Reply With Quote
  #3  
Old 4/15/07, 1:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Service size and panels

Quote:
Originally Posted by ndueker
There are 5 main disconnects that total 190 amps. 1969 house.
To add to Peter's post - there are 5 throws for service disconnect. There are not "5 main disconnects." This is a split-bus. Service disconnect is accomplished by "switching off" the top bus.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/15/07, 1:48 PM
cbrands's Avatar
cbrands cbrands is offline
New User
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 96
Please Note: cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service size and panels

#2 awg is rated for 100 amp
panel is rated 125 amp

take the weakest link in the chain.

i'd report this as 100 amp service
Reply With Quote
  #5  
Old 4/15/07, 3:13 PM
ndueker ndueker is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Ames, IA
Posts: 2
Default Re: Service size and panels

My vote is 100 amp service. The owner had an inspection done when they bought the house a couple of years ago though, and the inspector said it was 60 amp service then. They have not changed anything either.


Also, it appears to me that the sub panel is not proper due to the neutral (grounded conductor) and the ground (grounding conductor) joined under the same lug on the neutral bus. The insulation on that neutral wire looked like it was scorched toward the bottom of the panel too. Any thoughts?
Reply With Quote
  #6  
Old 4/15/07, 6:23 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: Service size and panels

By the way, the '200CL' on a modern meter indicates the meter is rated @ 200A.



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #7  
Old 4/16/07, 1:16 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Service size and panels

I see a bunch of double tapped neutrals. The photos are a bit too small to see anything else.
Reply With Quote
  #8  
Old 4/16/07, 10:41 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service size and panels

The only comment I will add is.......watch my " Sizing a Service " video....as Peter stated.....the use of the "Meter Enclosure" can "ASSIST" in putting you into the ballpark but it is NOT something to be a major consideration.....

It may AID in putting together the puzzles.....BUT you need to focus on SE Size, OCPD and Panel Rating.......and when looking to the size of the SE..sometimes looking at the mast connection can help as well...

However....it is REALLY ( when using the meters as an AID )...the size of the meter enclosure...NOT the CL100, CL200 or CL320 or anything actually written on the meter insert itself....

http://www.theelectricalguru.com/video.html



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Size of service?? cbuell Electrical Inspections 4 4/14/07 4:50 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 2:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts