Default service upgrade

Sometimes on the recommendation of others some people will take matters in their own hands.

This old house needed a service upgrade and the heating system needed to be upgraded. The homeowner did the electrical upgrade himself but hired a heating contractor to change out the heating system. It was the HVAC contractor that bought a permit and got the inspection department involved thank you Mel for these great pictures.

Notice in the first picture the panel cover as it will tell you this is a flush mount panel.



In this second picture the depth of the mechanical room can be determined. Also notice the service riser, it was not changed.




Well at least the fellow was trying to bring the house up to today’s standards.
Reply With Quote
  #2  
Old 1/25/08, 1:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: service upgrade

Sweet!



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/25/08, 1:36 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service upgrade

He needs a bigger door

If the door is 32x80 he would be "hold your nose legal" if it opens all the way.
How about derating all that wire in the 2" raceway?
That and the SE being too small would be my biggest concerns.
Reply With Quote
  #4  
Old 1/25/08, 1:43 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service upgrade

Looking at a zoomed in picture, that 2" is pretty ugly where it comes in (not the right angle) so he would be a whole lotbetter off just pulling it out and running a few more smurfs down to the old panel. (I assume that is where it goes). Then he could get under 9 CCCs in each.. Then schedule the PoCo to come out and connect the new SE.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
200 Amp Service Upgrade jhagarty Electrical Inspections 8 12/20/07 11:26 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 7:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 10:41 PM


All times are GMT -4. The time now is 2:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts