Question Service Weather Heads

This is a 3-4 month old service that was inspected by the AHJ. Are weather heads not required on SEU cable services anymore? Were they ever required? I have been calling this condition out without complaint, but this is the second one I have run into like it.
Attached Thumbnails
service-weather-heads-dsc07719.jpg  
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/25/11, 9:45 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

NEC 230.54 still requires a weatherhead or a gooseneck. That goes not look like a gooseneck to me.
Reply With Quote
  #3  
Old 7/25/11, 9:54 AM
Greg W. Mathias, CCHI Greg W. Mathias, CCHI is offline
InterNACHI Member
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 658
Wink Re: Service Weather Heads

I found this one on a ten year old home. I called the agent and sent her this picture and all she said was " not much wrong there, just needs to be stood up nailed back to the house" I don't think she got it.
Attached Thumbnails
service-weather-heads-keyprime-june-14th-2011-004.jpg  



Greg Mathias, CCHI
Journeyman Carpenter
Global Property Inspections
Lloydminster, AB. Canada
(780)205-9912
Reply With Quote
  #4  
Old 7/25/11, 9:59 AM
Greg W. Mathias, CCHI Greg W. Mathias, CCHI is offline
InterNACHI Member
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 658
Default Re: Service Weather Heads

Quote:
Originally Posted by jlevy1 View Post
This is a 3-4 month old service that was inspected by the AHJ. Are weather heads not required on SEU cable services anymore? Were they ever required? I have been calling this condition out without complaint, but this is the second one I have run into like it.
They allow these in our area as long as the dead head is through bolted into solid framing. Not sure from the picture if that is the case. I think it is a disaster waiting to happen.



Greg Mathias, CCHI
Journeyman Carpenter
Global Property Inspections
Lloydminster, AB. Canada
(780)205-9912
Reply With Quote
  #5  
Old 7/25/11, 10:02 AM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Service Weather Heads

Quote:
Originally Posted by gmathias1 View Post
They allow these in our area as long as the dead head is through bolted into solid framing. Not sure from the picture if that is the case. I think it is a disaster waiting to happen.
This is nothing more than vinyl tape wrapped around the SEU. How can it be bolted without a weather head?
Reply With Quote
  #6  
Old 7/25/11, 10:03 AM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Service Weather Heads

Quote:
Originally Posted by Jim Port View Post
NEC 230.54 still requires a weatherhead or a gooseneck. That goes not look like a gooseneck to me.
Thank you Jim. I was second guessing myself.
Reply With Quote
  #7  
Old 7/25/11, 10:11 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

I think the dead head mentioned would be the triplex anchor.
Reply With Quote
  #8  
Old 7/25/11, 10:12 AM
Greg W. Mathias, CCHI Greg W. Mathias, CCHI is offline
InterNACHI Member
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 658
Default Re: Service Weather Heads

Quote:
Originally Posted by Jim Port View Post
I think the dead head mentioned would be the triplex anchor.
Yes you are correct. Just another name for them.



Greg Mathias, CCHI
Journeyman Carpenter
Global Property Inspections
Lloydminster, AB. Canada
(780)205-9912
Reply With Quote
  #9  
Old 7/25/11, 11:34 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Service Weather Heads

It's hard to tell from that photo angle, but the SE cable might turn down after the clamp which could be considered a gooseneck, which can be used instead of a weatherhead.

The thing I dont like is how they landed and tapped the bare grounded messenger wire. Looks like just two strands of the wire go to the anchor ... ... instead of the full wire going to the anchor with a tap off that for the SE cable neutral ... see the attached diagram.
.
Attached Thumbnails
service-weather-heads-se-cable-gooseneck.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 7/25/11, 5:11 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

Goosenecks, which are formed with just a bunch of identified tape and are permitted by the NEC. They should look like the one in Bob's diagram. Here's the NEC requirement for the tape:

Quote:
230.54(B) Service Cable Equipped with Service Head or Gooseneck. Service cables shall be equipped with a service head. The service head shall comply with the requirement for fittings in 314.15.
Exception: Type SE cable shall be permitted to be formed in a gooseneck and taped with a self-sealing weather-resistant thermoplastic
Quote:
Originally Posted by roconnor View Post
The thing I dont like is how they landed and tapped the bare grounded messenger wire. Looks like just two strands of the wire go to the anchor ... ... instead of the full wire going to the anchor with a tap off that for the SE cable neutral.
.
Those attachments products are referred to as galvanized steel dead end grips and are added by the POCO to secure the drop to the point of attachment. It is not strands from the grounded conductor.


Last edited by Robert Meier; 7/25/11 at 5:50 PM.. Reason: Added Photo
Reply With Quote
  #11  
Old 7/25/11, 6:51 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

Quote:
Originally Posted by jlevy1 View Post
This is a 3-4 month old service that was inspected by the AHJ. Are weather heads not required on SEU cable services anymore? Were they ever required? I have been calling this condition out without complaint, but this is the second one I have run into like it.

After looking at the image again I can see why they opted for the rather ugly gooseneck over the weatherhead. Weather heads are not designed to be mounted on an angle as would be required by way the SE cable is installed. The top of the weather head would need to be mounted with it's attachment screw on top. That would not have been an easy task given the way that the cable was run.

Reply With Quote
  #12  
Old 7/25/11, 7:11 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

Quote:
Originally Posted by Jim Port View Post
I think the dead head mentioned would be the triplex anchor.
Haven't heard that term here before. That's what I have been calling the SE cables from the POCO since 1975.
Reply With Quote
  #13  
Old 7/25/11, 7:31 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

Brian, around here if someone says triplex they would typically be referring to the power company overhead cable.

Someone else mentioned only one or two strands around the anchor. That cable has a steel strand that is used to carry the weight and provide the strength.
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/25/11, 8:14 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

Quote:
Originally Posted by Jim Port View Post
Brian, around here if someone says triplex they would typically be referring to the power company overhead cable.

Someone else mentioned only one or two strands around the anchor. That cable has a steel strand that is used to carry the weight and provide the strength.
That's what I was referring to......just called it "SE cables from the POCO".
Reply With Quote
  #15  
Old 7/25/11, 8:23 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Weather Heads

Quote:
Originally Posted by Robert Meier View Post
After looking at the image again I can see why they opted for the rather ugly gooseneck over the weatherhead. Weather heads are not designed to be mounted on an angle as would be required by way the SE cable is installed. The top of the weather head would need to be mounted with it's attachment screw on top. That would not have been an easy task given the way that the cable was run.

Don't like that "gooseneck" method......have never seen one here in 39 years of working around houses and farms. In this picture, with high winds and rain, I see that as an easy entry point for water.

In your areas, are any there special requirements to prevent water that got into into the service conduit from entering the panel? I see a fair amount of corrosion here on the SE terminals/wires from water entry.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical service rating jskrypka Canadian Inspectors 7 1/4/09 6:37 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 9:24 AM
Service entrance conductor jjackson Electrical Inspections 30 1/7/06 5:05 AM