It is my understanding that any time two 110V circuits share a common neutral, the circuits should be treated as a 220V circuit (double pole breaker). Example: a 12-3 romex was pulled, one leg feeds wall outlets, one leg feeds lighting. Should these circuits be controlled by two single pole breakers or one double?
If double pole is required, does some one have a code reference? |
|
#2
|
|||
|
|||
|
Many electricians don't think they are a good idea but I believe they are allowed if done correctly.
http://www.nachi.org/forum/f19/shared-neutrals-22893/ InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Actually most electricians think they are a good idea and use them whenever possible. I know I do.
Handle ties were not a code requirement until the new 2008 NEC. That is if your area has adopted it and the work was done after 1/1/08. This new handle twi code is IMO a sad event, and I am afraid that we and the NEC are taking a dangerous path towards "over coding" ourselves. There is NOTHING unsafe about MWBCs if handled properly. This new code is NOT a safety code, it is a code designed to protect unqualified people when working with electrical systems. That friends is NOT the intent of the NEC, ie: to protect the unqualified and untrained person from themselves. |
|
#4
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
240.20(B)(1) through (3): Revised to require identified handle ties where they are used with individual single-pole circuit breakers.
See the definition for this term, no longer will they be OK when Approved, see that definition too. |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
So then what is an identified handle tie?
|
|
#6
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
![]() The 2002 Code permits use of a circuit breaker as a disconnect. For a multiwire branch circuit, unless limited by 210.4(B), individual single-pole circuit breakers, with or without “approved” handle ties, are permitted as the protection for each ungrounded conductor of multiwire branch circuits that serve only single-phase, line-to-neutral loads. A proposal for the 2005 NEC [ROP 10-39] was accepted to delete the word “approved” and replace it with the word “identified” because Art. 100 defines “approved” as acceptable to the authority having jurisdiction. Some electrical inspectors have accepted nails, screws, or wires as an approved handle tie. Art. 100 defines “identified” as “recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular code requirement.” Accessories, such as handle ties, are readily available from product manufacturers. |
|
#7
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here's one:
|
|
#8
|
||||
|
||||
|
Quote:
Yep sure looks like a bent nail to me . Been working fine for many years ,must be OK my Brother-in-law the electrician put it in. ...Cookie If I can answer any questions please send me email Roycooke@hotmail.com On an inspection and need immediate help call my cell 613-827-2011 |
|
#9
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Joe This section was moved to 240.15 in the 2008 code cycle and the reference to 210.4(B) was removed. This is what Pete was referring to. In the 2008 cycle a multiwire branch circuit will be required to open simultaneously all ungrounded conductors (210.4(B)) With the wording that is found in the 2008 code handle ties no matter if they are approved, identified or just a plain old nail will not comply. |
|
#10
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
• Section 240.20, covering requirements for overcurrent protection in series with ungrounded conductors and requirements for operational characteristics of circuit breakers, is relocated to Part I of Article 240 in a new Section 240.15.
• These provisions are more appropriate in Part I, which covers general requirement for overcurrent devices. • No technical changes were made in this section, just relocated text. • |
|
#11
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes you are right it was moved and the only text change was in (A)(3) where they added "point" so it now reads grounded neutral point.
The big change was to 210.4(B) and now reads that a multiwire circuit must simultaneously open all ungrounded (hot) conductors. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Shared neutrals | Ian Gills | Electrical Inspections | 17 | 1/8/08 1:22 AM |
| Metal Rigid or PVC Rigid what is code | bpotts | Electrical Inspections | 5 | 12/4/06 3:40 PM |
| Proposed Definition of Neutral Conductor and Point | jtedesco1 | Electrical Inspections | 1 | 4/22/06 11:19 AM |