Default Should bonding strap be removed?

This is a sub panel 3 wire feed, and the ground going to the water line. The grounds and neutrals are seperated, but the bonding strap is attached. These grounds appear to be bonded to the box also. So the bonding strap should be removed correct?

Thanks, Steve
Attached Thumbnails
should-bonding-strap-removed-1-small-.jpg.jpg
Views:	483
Size:	44.8 KB
ID:	9776   should-bonding-strap-removed-2-small-.jpg.jpg
Views:	342
Size:	43.1 KB
ID:	9777   should-bonding-strap-removed-3-small-.jpg.jpg
Views:	322
Size:	83.3 KB
ID:	9778   should-bonding-strap-removed-4-small-.jpg.jpg
Views:	382
Size:	83.4 KB
ID:	9779  
Reply With Quote
  #2  
Old 3/7/07, 9:08 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Should bonding strap be removed?

Ok.....From what i see that feeder that is actually supplying this panel is VERY small......looks like a freakin 10 AWG supplying this thing...so i got issues with that right off the bat.

I also have to tell you a 3 wire setup is WRONG.....but I will tell you a few things about bonding.....if they ran 3 wire to this and they did NOT leave that bonding strap in their would be a hard pressed way to clear a fault on the enclosure.....so while it is wrong I begin to worry about (2) wrongs not EVER making any right.....

They need to redo this panel with a (4) conductor setup and isolate the "grounded" conductor bar.....now if they TAKE that advice they need to have an electrician look at the load of this enclosure as well.

Now.....I will go on a limb because Bonding and Grounding is kinda my gig.....if they decided to do nothing...atleast bonding them together gives the chance of clearing a fault....but not a perfect situation so honestly I would simply defer and let the electrician look this over and defer your liability.

Now I also don't think the GE breaker should be in this enclosure because it to me looks like it will not fit properly in the cover opening footprint but thats really just me shooting in the wind on that one.

I also see some BLACK conductors being re-identified as "grounded" conductors and so on....Defer...Defer...Defer and let the Electrician sort it out.

I am sure others will find additional things.....I am back to watching my Movie....Later

P.S. I also QUESTION that screw holding the bonding strap on...looks like a sheetmetal screw to me .....and a stripped one to boot which tells me it is not from a tapped hole...but again just my observation and YES....if this panel was done RIGHT it would need that bonding strap removed......again you could remove it now but then you could have trouble if the enclosure is energized...again it SHOULD just be redone with (4) Conductors and done right....

Oh...also the GEC to the water pipe should go back to the main panel that feeds this "remote" panel.....



Paul W. Abernathy

Last edited by pabernathy; 3/7/07 at 9:12 PM..
Reply With Quote
  #3  
Old 3/7/07, 9:53 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Should bonding strap be removed?

It's real obvious someone installed a new panel here on some ancient wiring. The original wiring has no grounding conductors, now they brought in new romex circuits to a panel not equipped with a way to properly ground it. The panel should never have been changed without bringing in the proper feeders.

Also it it defintely not legal to use the interior water piping as a grounding path. Plus, with the bonding strip in place, any compromise in the neutral feeder will place voltage on the house plumbing.
Reply With Quote
  #4  
Old 3/7/07, 10:08 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Should bonding strap be removed?

Thank you both.
Steve
Reply With Quote
  #5  
Old 3/7/07, 10:11 PM
rstuart rstuart is offline
New User
 
Join Date: Feb 2004
Posts: 3
Please Note: rstuart is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Should bonding strap be removed?

Excellent analysis, very good. Thank you.
Ross
Reply With Quote
  #6  
Old 3/8/07, 7:43 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Should bonding strap be removed?

Most certainly........at some point this will be a SHOCKING experience for the owner of this electrical mess....



Paul W. Abernathy
Reply With Quote
  #7  
Old 3/8/07, 8:26 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: Should bonding strap be removed?

Paul, by 4 conductor, what do you mean? It can't be 2 hots a neutral and a ground. The ground does not count as a conductor.
Reply With Quote
  #8  
Old 3/8/07, 8:39 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Should bonding strap be removed?

it is when you RUN it.....you are trying to count it in some kinda calculation or if it is current carrying...I am saying in THIS case it needs .

Ah.......the bare is called " Equipment Grounding Conductor" so last I checked it is most certainly a conductor and in the 4 wire setup it is most certainly a conductor.........

You must maintain a low impedence path for fault current and the 4th conductor ( be is bare, insulated or conduit ) can serve that purpose depending on the installation.



Paul W. Abernathy
Reply With Quote
  #9  
Old 3/8/07, 10:08 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: Should bonding strap be removed?

So why is it that you don't count it the same when figuring out area, or when you have bx (3 wire = 2 hots and a neutral, 3 wire with ground = self explaining).
Reply With Quote
  #10  
Old 3/8/07, 10:13 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: Should bonding strap be removed?

So why is it that when calculating the area of a box the ground is done differently? Why is itthat BX is 3 conductor or 3 conductor with a ground?
I know that it is called a grounding conductor but it only conducts a fault.
Reply With Quote
  #11  
Old 3/8/07, 10:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Should bonding strap be removed?

lol....mysteries of the world huh...lol

In reference to BX itself....if we are talking about TRUE BX then it's case is not a grounding conductor...period but we have been down that road.

In the counting..it is counted as a conductor.....all combined as being considered (1) conductor.....so it is counted just in a different way.

However, that would be in TRYING to explain the CODE and I wont do that hear because I can just see the NEGATIVE boxes flying now....

In the use of it to a "remote" panel it is most certainly a conductor which DOES carry away fault current...or any CURRENT likely to be emposed on it in an effort to help clear the OCPD while providing a low impedence path to the enclosure and thus back to the source....( not ground as many still think )

lol......you will have to write the NEC to ask why they only count the EGC as (1) conductor in box sizing.....I did not write that code...

Also...lets not confuse older style BX with AC cable seen today.....all depends on the intent of the cable being used.



Paul W. Abernathy
Reply With Quote
  #12  
Old 3/8/07, 5:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Should bonding strap be removed?

I can't believe that so far, nobody's pointed out the most obvious problem.

The panel has what appears to be many knob and tube circuits coming in one big romex connector.


300.15 Boxes, Conduit Bodies, or Fittings —Where Required.
A box shall be installed at each outlet and switch
point for concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific
wiring methods for which they are designed and listed.
Where the wiring method is conduit, tubing, Type AC
cable, Type MC cable, Type MI cable, nonmetallicsheathed
cable, or other cables, a box or conduit body shall
be installed at each conductor splice point, outlet point,
switch point, junction point, termination point, or pull
point, unless otherwise permitted in 300.15(A) through
(M).


312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures.
Conductors entering enclosures within the scope of
this article shall be protected from abrasion and shall comply
with 312.5(A) through (C).
(B) Metal Cabinets, Cutout Boxes, and Meter Socket
Enclosures. Where metal enclosures within the scope of
this article are installed with messenger supported wiring,
open wiring on insulators or concealed knob-and-tube wiring,
conductors shall enter through insulating bushings or,
in dry locations, through flexible tubing extending from the
last insulating support and firmly secured to the enclosure.
Reply With Quote
  #13  
Old 3/8/07, 5:17 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Should bonding strap be removed?

Because thats what the forum is for........to have everyone provide issues and insight...not for one person to do it.

However I don't believe these picture were posted to elaborate on all the items in the pictures.....but more so to answer the specific question of the original poster and that was this :

Quote:
This is a sub panel 3 wire feed, and the ground going to the water line. The grounds and neutrals are seperated, but the bonding strap is attached. These grounds appear to be bonded to the box also. So the bonding strap should be removed correct?
I am more than sure he came up with plenty of other defects but was more concerned on the topic he posted.



Paul W. Abernathy
Reply With Quote
  #14  
Old 3/8/07, 5:38 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Should bonding strap be removed?

Yes, I was posting about the specific defect.
Thanks for all replies.
Steve
Reply With Quote
  #15  
Old 3/8/07, 5:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Should bonding strap be removed?

Quote:
Originally Posted by pabernathy
However I don't believe these picture were posted to elaborate on all the items in the pictures......
It's okay. I take every liberty available to me.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM
Nat Gas water heater electr. bonding lfreeze Electrical Inspections 14 1/15/07 10:16 PM
What Is Bonding...... pabernathy Electrical Inspections 46 1/1/07 1:17 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 2:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts