Question for the electricians.
I inspected a home where the upstairs bathroom had a fully enclosed shower stall (door had no gap along the top when closed). The stall had a light/fan combo that was on the garage GFCI. I called it as incorrect stating there should be no other outlets on the bath circuit. However, the electrician on site stated that since the shower stall was "fully enclosed", it was considered a separate "wet" location and had to be GFCI protected. He was not specific with any code reference but said it had something to do with the shower stall being considered as a steam room. Any thoughts?? |
|
#2
|
|||
|
|||
|
Perhaps the NEC would shed more light on the subject Louis.
From the 03 IRC E3903.8 the fixture should be labeled SUITABLE FOR WET LOCATION. Now if you go to E4103 section (Spas & Hot tubs) you could interpet the code to install a GFCI protection. "Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#3
|
||||
|
||||
|
Quote:
Ok....so I will say BOTH are a bit incorrect here.......now I have to run.... FYI.....yep..."the fixture should be labeled SUITABLE FOR WET LOCATION." Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The electrician is full of it IMO. There is no such thing as a "separate wet location" in a bathroom just because of the type of shower doors. Tell him he does get points for creativity though. There is NO GFI requirement for "wet locations". This is a myth long perpetuated. There is NO requirement for enclosed recessed shower lights to be GFI protected either. The fan however probably does state in the instructions that if it is within a shower or bath location it must be GFI protected. But the NEC does not tell us it must be GFI'd. The NEC tells us we MUST follow mfg instructions and install GFI protection. Summary: Yes, it most likely does require GFI protection. Yes, it can be on another circuit such as the garage. No, it is NOT a "separate wet location". |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Shower stall vent | mmasney | Interior | 14 | 1/15/08 4:58 PM |
| Installing GFCI in garage with no ground | cyezza | Electrical | 53 | 11/30/07 6:05 PM |
| GFCI Safety Notice | rcooke | Electrical | 1 | 10/30/07 1:29 PM |
| Garage GFCI | rdale | Electrical | 29 | 8/8/07 5:06 PM |
| exhaust fan over shower stall | dbook | Electrical | 5 | 4/24/07 5:40 PM |