Default Shunt trip breaker

Can someone explain these a little better to me? I have a general idea on there purpose, but I was wondering about the inspection part of it. I have no idea what its protecting, should I just disclaim and say its present? Or how do you report on them if found?

BTW, Very small commercial building.

Thanks in advance.
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #2  
Old 7/22/09, 10:29 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Shunt trip breaker

From http://www.maintenanceresources.com/...ircbreak5.html


SHUNT TRIP

Some times it is advantageous to turn a breaker off from a remote location. To facilitate this task, an accessory called a shunt trip feature is installed by the manufacture inside of the breaker. This device consists of an electro-magnetic trip coil that is connected in series with an external field wired switch. When the switch contacts are closed, power is passed to the shunt trip coil causing the breaker’s mechanical latch to move to the open position. Re-closing the breaker is done by physically going to the breaker and manually moving the operating handle to the on–closed position.
When opened by use of the shunt trip coil, the breaker’s operating handle moves to the off (maximum handle travel) and not the tripped (short of full handle travel) position. Knowing this can help when trying to determine if the breaker tripped off due to an overcurrent condition or was remotely turned off.


HTH
Reply With Quote
  #3  
Old 7/22/09, 10:34 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 767
Send a message via AIM to jfrederick
Default Re: Shunt trip breaker

Yeah, I read this one already, but I thank you anyway. I was wondering exactly what they're usually installed for and why.
Reply With Quote
  #4  
Old 7/22/09, 10:38 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Shunt trip breaker

Often used to shut down supply air to the structure in the event of a fire.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #5  
Old 7/22/09, 9:32 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Shunt trip breaker

In industrial/commercial power systems almost all large circuit breakers use shunt trip circuitry. This allows multiple relays to monitor conditions in a circuit (overcurrent, ground fault, open phase, bus differential, etc.) and trip the applicable breaker(s) when required. There is very little true need for shunt trip breakers in the typical residence, but some will be found from time-to-time, employed mostly for convenience sake.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 7/22/09, 10:40 PM
Harry F. Johnson, II's Avatar
Harry F. Johnson, II Harry F. Johnson, II is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Henderson, CO
Posts: 17
Default Re: Shunt trip breaker

Quote:
Originally Posted by mlarson View Post
Often used to shut down supply air to the structure in the event of a fire.
elevators are another example



Harry "Bud "Johnson
Allay Home Inspection Services
WWW.ALLAYINSPECT.COM
ID# NACHI07081905
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
What's it take to trip a breaker? jfunderburk Electrical Inspections 14 10/20/08 12:44 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 4:25 PM
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 4:57 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 3:05 PM


All times are GMT -4. The time now is 9:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts