Old 8/12/09, 3:30 PM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Siemens distribution panel bonding screw installation

This was a recently installed/updated electrical service, exterior service equipment, and a distribution panel (as seen here). My dilema is that there was a green bonding screw installed, however, the label inside the panel confused me a bit. The screw was not installed all the way, as you can see in the last pic. Everything else seemed to be professionally installed and correct, however, this bonding screw set up has me a bit perplexed. I know that the neutral is not supposed to be bonded, but is it? Any helpful insight would be greatly appreciated. Thanks in advance.
Attached Thumbnails
siemens-distribution-panel-bonding-screw-installation-314-minneapolis-defiance-076.jpg   siemens-distribution-panel-bonding-screw-installation-314-minneapolis-defiance-074.jpg   siemens-distribution-panel-bonding-screw-installation-314-minneapolis-defiance-075.jpg  
Reply With Quote
Find an InterNACHI certified District Of Columbia Home Inspector (and anywhere else in North America)
  #2  
Old 8/12/09, 4:14 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Siemens distribution panel bonding screw installation

Newer panels have labels that say "bond when required".

You would have to know the length of that screw to know for sure if is not touching, it sure looks like someone tried to do it right but should have removed the screw so someone would not "fix it" by tightening it.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 8/12/09, 7:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Siemens distribution panel bonding screw installation

The screw should be removed completely. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 8/12/09, 7:59 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Siemens distribution panel bonding screw installation

Joshua,

That label is for "When" the neutral "Grounded" conductor is to be bonded to the enclosure. In your case based on what you have told us your assumption is correct and the bonding screw needs to be removed. However, you do need to verify the EGC is actually connected to the panel enclosure so you ensure they at least have a low impedance fault current path.



Paul W. Abernathy
Reply With Quote
  #5  
Old 8/16/09, 10:15 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Siemens distribution panel bonding screw installation

So when would you know that the green screw needed to be kept in place?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #6  
Old 8/16/09, 12:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Siemens distribution panel bonding screw installation

Quote:
Originally Posted by rwashington View Post
So when would you know that the green screw needed to be kept in place?
When it is a main panelboard or in a remote distribution panel that is using that specific buss only for grounding purposes and the "grounded" buss bar is isolated as it should be on a remote distribution panel.

Understand that the "GREEN" screw is but only one method. It can be used in a main distrubution panel for bonding the common grounded and grounding terminal bar to the enclosure which is a common practice or in a remote distribution panel ( some call Sub-panel) where you have a seperate "grounding" buss bar which is for the "EGC" Equipment Grounding Conductors" to terminate. You may see a panel with a tie bar that once removed seperates two different buss bars. If that were the case, the one side with the green bonding screw is for "EGC's" only and the other is for the "Grounded" conductors ( ie: in your case true neutrals when dealing with typical home inspections ).

Hope this is helpful......



Paul W. Abernathy
Reply With Quote
  #7  
Old 8/16/09, 1:15 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Siemens distribution panel bonding screw installation

Paul those conductors look like regular neutrals in this case.
Reply With Quote
  #8  
Old 8/16/09, 2:34 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Siemens distribution panel bonding screw installation

Quote:
Originally Posted by relliott View Post
Paul those conductors look like regular neutrals in this case.
I was refering to the question posed by Richard Only.



Paul W. Abernathy
Reply With Quote
  #9  
Old 8/16/09, 11:14 PM
Justin D. Schlueter Justin D. Schlueter is offline
New User
 
Join Date: Jul 2008
Location: Minnesota
Posts: 11
Please Note: Justin D. Schlueter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens distribution panel bonding screw installation

Quote:
Everything else seemed to be professionally installed and correct, however, this bonding screw set up has me a bit perplexed. I know that the neutral is not supposed to be bonded, but is it?
The Siemens boxes come from the factory that way. If you need to leave it unbonded, you simply leave it as is (the way it is in your photo), If it needs to be bonded, you screw it in. The screw itself is "upset" on the end similar to the terminal screws on switches and receptacles to help prevent it from being removed completely or falling out. It is a good idea, because many times the bonding screw gets lost, and people substitute any old screw, which is obviously wrong. I learned early on that the first thing you do when you take a panel out of the box to install it is to put in the bonding screw (if needed.)

In my opinion, Siemens came up with a good way to "stupid proof" a small portion of the install.
Reply With Quote
  #10  
Old 8/17/09, 12:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Siemens distribution panel bonding screw installation

Personally as a rule...If the bonding screw was not going to be used in a given install then it would be removed. Unless, the screw itself was going to be used to actually bond a terminal bar to the case then the best way to "stupid proof" the installation is to remove it. Now, like I said before;it may be something needed if the design of the panel can still use that specific terminal bar for the "grounding" purposes...otherwise the best course of action I teach young electricians is remove it if their is any possible chance of an improper case to neutral connection down the road.



Paul W. Abernathy
Reply With Quote
  #11  
Old 8/18/09, 9:42 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Siemens distribution panel bonding screw installation

That panel looks to me like it has more problems then the bonding screw.

Loose "hot" conductor, Door bell transformer at side of panel.. Is that ye old'e cloth wrapped wir'in. What say ye... about that gents?

Here are some modern lighting fixtures for your enjoyment...
Attached Thumbnails
siemens-distribution-panel-bonding-screw-installation-dsci3548.jpg   siemens-distribution-panel-bonding-screw-installation-dsci3573.jpg   siemens-distribution-panel-bonding-screw-installation-dsci3574.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Subpanel Bonding Screw away Electrical Inspections 24 1/9/08 2:46 PM
Steel post question sspradling Structural Inspections 42 3/2/07 8:59 PM
Panel screw hits a live wire rwand1 Electrical Inspections 23 4/3/06 5:50 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts