Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Siemens Panel

I had a new Siemens panel with four Square D breakers installed. The panel did not list any Square D breakers for use in the panel. I wrote it up as a defect. Just wanted to know if any of the Electrical gurus think it is ok to mix these two brands. They were not loose and of course they were passed by the city inspector. No anti-oxidant paste on the AL wires.

Anatol
Reply With Quote
  #2  
Old 3/12/07, 7:54 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

I don't remember but I think HOM breakers are classified for use in BR panels. I have to check that one.

Noalox is not code required. It's just a good idea.
Reply With Quote
  #3  
Old 11/15/07, 9:30 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 373
Default Re: Siemens Panel

Quote:
Originally Posted by Speedy Petey
I don't remember but I think HOM breakers are classified for use in BR panels. I have to check that one.

Noalox is not code required. It's just a good idea.
I beg to differ.
reviewed an older code check and under 1999 NEC (110-14 ) and 2002 NEC ( 110.14 ) BOTH REQUIRE anti-oxidant on AL conductors
Peter
Reply With Quote
  #4  
Old 11/15/07, 11:59 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Can you cite that?
My copy says

Quote:
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
There may be something in the installation instructions for that lug, making it a 110.3(B) issue but it has to say you shall or you must, not just that it is recomended. That is how the code works.
Reply With Quote
  #5  
Old 11/16/07, 12:10 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Siemens Panel

Quote:
Originally Posted by pbennett1
reviewed an older code check and. . .
That would be your problem right there. Code Check is a great reference tool, but they often contain errors or "misleading" information. You should always confirm any Code Check reference by looking at the actual code to which it refers.

Greg's reference is a great example of a misleading reference by Code Check Electrical, page 10.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 11/16/07 at 12:14 AM..
Reply With Quote
  #6  
Old 11/16/07, 12:15 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

These same words goes back as far as the 1968 cycle.
Reply With Quote
  #7  
Old 11/16/07, 12:22 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Interesting side bar if I understood the answer.
Reply With Quote
  #8  
Old 11/16/07, 12:31 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Short answer is yes.
http://forums.mikeholt.com/showthread.php?t=58733
Reply With Quote
  #9  
Old 11/16/07, 7:40 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Quote:
Originally Posted by relliott
About the breakers, thanks Robert.

And thanks guys for the back up on the Noalox thing. That's exactly what I meant.
I was out last night.
Reply With Quote
  #10  
Old 11/16/07, 11:11 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Siemens Panel

Lets understand this a little more....

"Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment. "

Not that they are required...but " where employed" they shall be suitable for their use.......lets also remember with many brands we do find compounds for use with AL conductors and believe it or not they make one for CU conductors as well.......you dont want to use a CU compound in AL conductors....defects the purpose........

I have asked Eaton directly on this to clear up the questions a long time ago, they do not test their panelboards with NoAlox compound.....the ratings are not based on the use of it at all........BUT it is important to note that on their disconnects you will see in the verbiage that NoAlox or similar compounds are required...if it is on the label saying to use it...then you have to use it and if it does not say it on the panel label you dont.......

BUT...as a side note.....when I do a service with AL conductors...I use it.......why?....because I buy into the hype...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 11/16/07, 11:17 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Siemens Panel

OH....BTW...........I do see where ALOT of inspectors turn down a job because of not having NoAlox......and when I consult them I always say why would you turn it down for that......the reponse is this " its the way we have always done it "

Then I reply........fine....I would suggest you be more concerned with electricians not using the proper " torque " settings on lugs and screws before I would concern myself over NoAlox.....if you are going to concern yourself with one......then factor in the other which if you believe NoAlox works ( and it does..when installed right )....then factor in the issue of over torquing and under torquing......"

How many electricians today carry a Torque Wrench to the jobsite.....I do seminars for Eaton all over the country...in fact I was just in Philadelphia and Chantilly last week.....guess how many carry a torque wrench in the truck.....about 50%.....guess how many said they have used it.....5 %



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 11/16/07, 5:13 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Quote:
Originally Posted by pabernathy
BUT...as a side note.....when I do a service with AL conductors...I use it.......why?....because I buy into the hype...
You are in good company my friend.
Reply With Quote
  #13  
Old 11/16/07, 5:18 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Quote:
Originally Posted by pabernathy
......the reponse is this " its the way we have always done it "
I always love that response.





Quote:
Originally Posted by pabernathy
How many electricians today carry a Torque Wrench to the jobsite.....I do seminars for Eaton all over the country...in fact I was just in Philadelphia and Chantilly last week.....guess how many carry a torque wrench in the truck.....about 50%.....guess how many said they have used it.....5 %
I do. I have a 3/8" orque wrench right in one of my tool boxes. I do use it, but alas, not all the time.
I have done comparison tests and I have to say, my "feel" is very close to correct torque.
Reply With Quote
  #14  
Old 11/16/07, 9:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Siemens Panel

Speedy........you are renown for being the "Torque Master"....Which is rare among electricians these days...I see installs where the electrician torqued lugs so tight it causes more issues than being loose......theo"torque"ly speaking that is.......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 11/16/07, 10:50 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Siemens Panel

Obviously my wrench is broken. The "T" fell off.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 4:45 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts