Is a Siemens panel rated to have Square D HOM breakers installed?? I seem to remember that the they can have some Square D lines but not sure about HOM.
Foxe Smothers ( Owner / Inspector ) Pelican State Inspection Your Best Choice for Home Inspection in the Shreveport & Bossier City Area! www.PelicanState.Net www.ShreveportHomeInspector.net www.BossierCityHomeInspector.net foxe@pelicanstate.net LSBHI #10399 |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Nope. Absolutely not. They physically fit, however.
|
|
#3
|
||||
|
||||
|
Thanks Marc, did not think so. How about the QO's?
Foxe Smothers ( Owner / Inspector ) Pelican State Inspection Your Best Choice for Home Inspection in the Shreveport & Bossier City Area! www.PelicanState.Net www.ShreveportHomeInspector.net www.BossierCityHomeInspector.net foxe@pelicanstate.net LSBHI #10399 |
|
#4
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Square D QO and Cutler-Hammer CH both have unique buss designs.
The Square D HOM and Cutler-Hammer BR along with others share a similar design and while they may not be listed for use in other brands of panels most times they will fit. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |