Found this today in service panel at 60 AMP breaker for a welder, what problems do we face with the wire being trimmed to fit under the lug.
Thanks! in advance for your input. |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
You face the possibility of the termination overheating, but your real problem is a wire gauge too big for the lug. That lug is probably rated for #4, Max. That looks like at least #2. There are ways to adapt, but cutting off strands is not one of the ways.
(Looks like the torque chart on the bottom of the breaker in your picture only shows up to #6) |
|
#3
|
||||
|
||||
|
Thanks! Marc
|
|
#4
|
||||
|
||||
|
is this a trick question!?
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Probably not. Do you feel tricked? Many people think the installation pictured is fine, which it certainly is not.
|
|
#6
|
||||
|
||||
|
Marc,
sorry I was kidding, and you did not get it. education of really important. |
|
#7
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am with Marc Shunk side with this situation and unforetally I did see it from time to time. { both USA and France side both way are nothing new to me } ANd that set up is not very good and there is alot of good way to do it properly. Merci,Marc |
|
#8
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
John Kogel www.allsafehome.ca |
|
#9
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Square D HOM Breaker & Max Wire Size | pbennett1 | Electrical Inspections | 20 | 3/3/08 9:22 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 4:28 PM |