Two questions hopefully you all can tell from the picture whats going on.

1) Does that wiring size look correct for a 35 amp breaker?
2) Why the white wire (Neutral?)
Attached Thumbnails
sizing-and-neutral-question-cinn-003.jpg  



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #2  
Old 2/15/07, 8:30 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing & Neutral Question?

Hard to tell from the picture. It should be a #8 wire.

The white wire is improperly identified. Is should have black tape on it.
Reply With Quote
  #3  
Old 2/15/07, 8:49 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Sizing & Neutral Question?

The white wire did have black tap on about an inch down, I could not trace where the wire went due to crowding.



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #4  
Old 2/15/07, 9:02 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing & Neutral Question?

A) If this instalation predates 1999(?) then no identification was necessary. That's not to say it's not a good idea. Also, tape is not a legal identifier for such small wire. A permanent marker or paint is proper.
It is/was SOP to use "2-wire" for straight 240v circuits.


B) If this is feeding an air conditoner it is VERY likely that it is the correct size for that circuit.
You cannot simply say it is wrong without furhter investigation. You can call it out for evaluation, but IMO you should not automatically lable it as "wrong".

Also, bear in mind. A white wire is absolutely NOT always a neutral.
Reply With Quote
  #5  
Old 2/15/07, 9:12 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Sizing & Neutral Question?

Thanks guys--Much Appreciated..

Speedey, that is the AC breaker, max breaker recommended was a 35 amp breaker., I know a white wire isnt always a neutral, but why confuse us little people..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #6  
Old 2/15/07, 10:02 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing & Neutral Question?

Speedy,

Agreed that black tape is not legal, but it is better than nothing. I would rather see that than nothing (and that is what most electricans use that I have seen).

Tim,

If they didn't try to confuse us, our job wouldnt be any fun.
Reply With Quote
  #7  
Old 2/15/07, 11:43 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing & Neutral Question?

Quote:
Originally Posted by wsiegel
Agreed that black tape is not legal, but it is better than nothing.
I guess working with it has tainted me. I'd rather see nothing as opposed to tape. After a short while the tape dries up and leaves a black sticky mess.
I never assume anything but, seeing a two pole breaker with a black and white is nothing odd in my world. Especially in an older setting.
Reply With Quote
  #8  
Old 2/15/07, 11:53 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing & Neutral Question?

(C) Circuits of 50 Volts or More.
The use of insulation
that is white or gray or that has three continuous white
stripes for other than a grounded conductor for circuits
of 50 volts or more shall be permitted only as in (1)
through (3).
(1) If part of a cable assembly and where the insulation is
permanently reidenti
fied to indicate its use as an ungrounded
conductor, by painting or other effective
means at its termination, and at each location where the
conductor is visible and accessible.

I don't have a problem arguing in court that TAPE is a " other effective means" as I can scrap off paint as well...so anything is removable.

My argument would be to cite other areas within the code for similar issues:

(D) Identi
fication of Ungrounded Conductors.
Where
more than one nominal voltage system exists in a building,
each ungrounded conductor of a multiwire branch circuit,
where accessible, shall be identi
fied by phase and system.
This means of identi
fication shall be permitted to be by
separate color coding, marking tape, tagging, or other approved
means and shall be permanently posted at each
branch-circuit panelboard.

In this section they consider marking tape and consider it a permanently posted method....

lol...so I will fight the fight for Marking Tape....




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 2/15/07, 12:23 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing & Neutral Question?

I know we are getting off on a tangent, but I like this "conversation".

I'm going to counter you on this Paul.

In your first code quote, the words "permanently identified" are the key. With "permanent" being the kicker. I definitely consider paint as permanent as it is not easily removed. And a Sharpie marker is, well... a permanent marker.
I really doubt anyone can argue that tape is permanent.

Also, the second quote is IMO not applicable since it is expressly referring to "more than one nominal voltage system exists in a building" and conductors of multi-wire circuits.
Again, not really applicable to a residential setting, or even a commercial setting with only one voltage system (IE:120/208v), and is specific to multi-wire circuits.
Reply With Quote
  #10  
Old 2/15/07, 12:39 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing & Neutral Question?

I disagree...lol....but thats why we are chatting on it...

I would argue that with paint remover I could remove this from the conductor and in turn degrade the conductor...while tape would be considered -reidentifed in similar nature.

or other effective
means at its termination,
and at each location where the
conductor is visible and accessible

I call the "OR" other effective means.........
I also would agrue with my attorney ( being funny here ) in that no testing has been done to prove that painting a conductor would not damage or degrade the condition of the conductor based on the following statements.

110.11 Deteriorating Agents.
Unless identified for use in
the operating environment, no conductors or equipment
shall be located in damp or wet locations; where exposed to
gases, fumes, vapors, liquids, or other agents that have a
deteriorating effect on the conductors or equipment; or
where exposed to excessive temperatures.

FPN No. 1: See 300.6 for protection against corrosion.
FPN No. 2: Some cleaning and lubricating compounds can
cause severe deterioration of many plastic materials used
for insulating and structural applications in equipment.

lol...Ok ...lol....no funny comments about bringing that section up....building a case to say to the judge...see how the NEC makes statements that could allow my use of tape...lol

I will hold tight to this part...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 2/15/07, 12:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing & Neutral Question?

I would say....the allowance of the NEC to re-identify conductors in the field as well would be a good basis for "Marking Tape" as a method of re-identification would be acceptacle in my view.

Ok...here is an area that would apply to dwellings that refer to re-identification


(B) Sizes Larger Than 6 AWG.
An insulated grounded
conductor larger than 6 AWG shall be identified by one of
the following means:
(1) By a continuous white or gray outer finish.
(2) By three continuous white stripes along its entire length
on other than green insulation.
(3) At the time of installation, by a distinctive white or
gray marking at its terminations. This marking shall
encircle the conductor or insulation.
* Note- Should the amend to say "permanently"...?

There are alot of areas in the NEC that refers to permanently marking and it could be tags, signs and signage all of which can easliy be removed.

I hear ya brother.......just dont fine the use of TAPE...a statement worth of being called Illegal... Thats a STRONG word to use on a section of the NEC that seems to be broken up and in the end gives a possible opening for debate.





Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 2/15/07, 12:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing & Neutral Question?

Here is a issue that brings up the same debate about " Physical Damage " and " Permanently marked " which the NEC does not define and leaving it open to the AHJ to determine. Leaving it a far CRY from being considered "Illegal" in my eyes.....James Stallcups eyes, Mike Holt's eyes and countless others because their TEXTbooks see tape as a viable option.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 2/15/07, 2:35 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: Sizing & Neutral Question?

Gee I have been out of the trade for a few years but we frquently fed many in house services ( industry ) with single conductor core flex and aways identified the feeds with tape.
I have used plastic tape many times to change a white to back
I have pulled 200 or more red #14 for controls and always taped on number tags and they seem to last for ever .

Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #14  
Old 2/15/07, 4:51 PM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: Sizing & Neutral Question?

I'm smarter.......no I'm smarter.......no I'm smarter.
Home inspectors are not specialists. What is the point of all this code talk. It must take you guys days to write a report after looking at the NEC,, plumbing, HVAC, structural, and all the other code books and finally giving your client a report that is technically exhaustive.
Reply With Quote
  #15  
Old 2/15/07, 5:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing & Neutral Question?

dude it is not a smarter thing......we are simply debating ideas...why it someone always wants to make something more out of simple chatting and learning from each other......I value Peters opinion and I offer my opinion..

It is not a pi$$ing contest...........this is a HI board but if two electricians want to engage in a conversation and debate why is it not allowed...have we not atleast earned that much to be allowed to learn from each other outselves?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 3:40 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 10:44 AM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 2:38 AM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 11:19 AM


All times are GMT -4. The time now is 7:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts