Default Sizing a Service- Weakest Link Method

Hey Guys,

I found this file and updated it for you all. Enjoy !

http://www.youtube.com/watch?v=b499RKjLroA



Paul W. Abernathy
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/12/10, 3:10 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Sizing a Service- Weakest Link Method

Paul, What is your opinion on reporting subpanel amperage? I see many inspectors just list the rating of the enclosure in the report as opposed to listing the amperage of the feeder circuit. I think the correct way is to list the available amps on these that you can actually use without modifications. Listing the rating of the enclosure is fine too but the real number should be disclosed in the report.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 6/12/10, 4:03 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing a Service- Weakest Link Method

When sizing a Remote Distribution Panel , you still have the same basic components. Feeder size, Feeder Breaker Size, Enclosure Rating. Just remember that the enclosure rating is not something we can rely on much because a 100A rated feeder protected by a 100A OCPD supplying a remote distribution panel with a rating of 150A would still be only 100A.



Paul W. Abernathy
Reply With Quote
  #4  
Old 6/12/10, 4:26 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing a Service- Weakest Link Method

I agree with you Bruce. A panel rated for 100 amps but fed with a 2 pole 40 would be a 40 amp subpanel to me.
Reply With Quote
  #5  
Old 6/12/10, 4:48 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing a Service- Weakest Link Method

Hmmm.......ahhh.....is that not what I typed using my example?



Paul W. Abernathy
Reply With Quote
  #6  
Old 6/13/10, 7:26 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sizing a Service- Weakest Link Method

Nice video, I like the weakest link concept. One thing that I didn't hear mentioned in your example is that your 200 amp main CB is protecting a panelboard only rated for 150 amps which could become a problem if the load ever exceeds 150 amps.
Reply With Quote
  #7  
Old 6/13/10, 9:06 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing a Service- Weakest Link Method

Remember now...we are only giving examples of the components of sizing using an extreme example as mentioned in the oopening statement. Once it is defered to the contractor amoung other issues it will be evaluated. The effort was simply to give an example of sizing for a home inspection report.

I agree in that example it should be reported that the enclosure is only 150A rated....and you are correct in that over 150A load could effect this....just remember when I do these short videos, I can't cover everything in order to keep viewers focused on the intent of the video itself.



Paul W. Abernathy
Reply With Quote
  #8  
Old 6/13/10, 9:10 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sizing a Service- Weakest Link Method

But......I must add.......That is a GREAT point inspectors should remember when reporting the issues......other than just trying to size it.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM