Question Small gray box with double-tapped wires: what is it?

Attached are photos from service panels that had small gray boxes -- one of which had a green LED -- attached to the service panel, and double-tapped to two breakers. What is this? Is it supposed to be double-tapped? One of the panels was a recent installation, approved by the city.
Attached Thumbnails
small-gray-box-double-tapped-wires-elec-panel-gray-box-8-24-2006.jpg   small-gray-box-double-tapped-wires-elec-panel-gray-box-8-22-2006.jpg  
Reply With Quote
  #2  
Old 8/26/06, 6:50 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by fbartlo
Attached are photos from service panels that had small gray boxes -- one of which had a green LED -- attached to the service panel, and double-tapped to two breakers. What is this? Is it supposed to be double-tapped? One of the panels was a recent installation, approved by the city.
No it should not be double tapped .
Easy fix pig tail it to one wire to breaker .
I do not know what the box is but suspect it could be some sort of a filter to take spikes out of the lines to offer some computer protection .
Have seen some smooth sales people who can sell these things some work better then others .
Roy Cooke
Reply With Quote
  #3  
Old 8/26/06, 7:00 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Small gray box with double-tapped wires: what is it?

Looks like surge supressor.
Reply With Quote
  #4  
Old 8/26/06, 7:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by smcarthur
Looks like surge supressor.
Yep, and the double taps should be corrected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 8/26/06, 7:28 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Small gray box with double-tapped wires: what is it?

Thanks. I figured the double-taps were improper. Surge protectors make sense.

BTW, what are the best relatively inexpensive surge protectors? My computer and audio equipment are hooked up to Dataguard "surge-protecting" power strips. Is such a thing really very effective? At least it's not been proven ineffective during my use ...
Reply With Quote
  #6  
Old 8/26/06, 7:35 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by fbartlo
Thanks. I figured the double-taps were improper. Surge protectors make sense.

BTW, what are the best relatively inexpensive surge protectors? My computer and audio equipment are hooked up to Dataguard "surge-protecting" power strips. Is such a thing really very effective? At least it's not been proven ineffective during my use ...
Expensive computer much information you need .
Cheap Protection is like a cheap inspection not much good .
My openion ,others may agree.
Roy Cooke
Reply With Quote
  #7  
Old 8/26/06, 9:20 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Small gray box with double-tapped wires: what is it?

All surge suppressors should be replaced after a few years. They use MOVs (Metal Oxide Varistors) and some of the MOVs burn up with every surge that they control, therefore, after a period of time the surges render them relatively useless. So, if you plug your new computer into that 10 year old surge strip, you are probably not protected.

Last edited by smcarthur; 8/26/06 at 9:28 PM..
Reply With Quote
  #8  
Old 8/27/06, 7:08 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Small gray box with double-tapped wires: what is it?

I notice that "double taps" are a large part of discussion on this site.

There are circuit breakers installed today and in the past that do permit the installation of more than one conductor. So one cannot randomly say the double tapping is not permitted. The NEC permits double tapping if the manufacturer does, so before you write this up, you should investigate fully first.
Reply With Quote
  #9  
Old 8/27/06, 7:15 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by Pierre Belarge
I notice that "double taps" are a large part of discussion on this site.

There are circuit breakers installed today and in the past that do permit the installation of more than one conductor. So one cannot randomly say the double tapping is not permitted. The NEC permits double tapping if the manufacturer does, so before you write this up, you should investigate fully first.
Welcome aboard . It is obvious you have not been reading for avile . Yes you are correct there are some Breakers Sqare D is the manufacture .
But to use two wires they must be same size and type and also on oppisite side of the screw.
Glad you are able to visit and learn . Come again
Roy Cooke
Reply With Quote
  #10  
Old 8/27/06, 8:22 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Small gray box with double-tapped wires: what is it?

For example:
Attached Thumbnails
small-gray-box-double-tapped-wires-twowirebreaker.jpg  
Reply With Quote
  #11  
Old 8/27/06, 8:26 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by lkage
For example:
Great picture of a sq.D. luge where the wires go thanks Larry .

Roy Cooke
Reply With Quote
  #12  
Old 8/27/06, 8:57 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by rcooke
Yes you are correct there are some Breakers Sqare D is the manufacture ....
Glad you are able to visit and learn .
Roy, first off, Sq D is not the only one who permits this. Many of C-H's CH series breakers allow it, as well as others I'm sure.

Also, I truly don't mean to speak for him, and I know we can all learn something, but I seriously doubt there is much you are going to teach Pierre with regard to the electrical field/trade.
Reply With Quote
  #13  
Old 8/27/06, 8:59 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by Pierre Belarge
I notice that "double taps" are a large part of discussion on this site.

There are circuit breakers installed today and in the past that do permit the installation of more than one conductor. So one cannot randomly say the double tapping is not permitted. The NEC permits double tapping if the manufacturer does, so before you write this up, you should investigate fully first.
I agree with your post concerning double lugging, but how is a home inspector to know which of the many breakers allow 2 wires per terminal? Would it be correct to not note double lugging in your report? Should breakers be labeled as to the number of wire they will accept? It has been established here that some Square D breakers will accept 2 wire of the same size, but are there others? Who has the time and resources to research all the different manufacturers to determine the number of wire their breakers will accept?
I'm still in the learning stage of Home Inspection and it's important to me to give customers all the information they need.
So, what is the concensus here? How do you report double lugged breakers?
Reply With Quote
  #14  
Old 8/27/06, 9:06 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by smcarthur
I agree with your post concerning double lugging, but how is a home inspector to know which of the many breakers allow 2 wires per terminal? Would it be correct to not note double lugging in your report? Should breakers be labeled as to the number of wire they will accept? It has been established here that some Square D breakers will accept 2 wire of the same size, but are there others? Who has the time and resources to research all the different manufacturers to determine the number of wire their breakers will accept?
I'm still in the learning stage of Home Inspection and it's important to me to give customers all the information they need.
So, what is the concensus here? How do you report double lugged breakers?
Too simple read here and read previous posts .
There has been much great information posted .
I only know of Sq D being approved for double taps .
Roy Cooke
Reply With Quote
  #15  
Old 8/27/06, 9:23 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Small gray box with double-tapped wires: what is it?

Quote:
Originally Posted by rcooke
Too simple read here and read previous posts .
There has been much great information posted .
I only know of Sq D being approved for double taps .
Roy Cooke
So are you saying this is the only place to get this information? Because Sq D is the only one you know of that means there are no others?

From a H-I standpoint I'd say report it as a "possible" violation or problem. Although it has been established that it is a very minor issue.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM
Double tapped grounds. gheller Electrical Inspections 10 4/17/07 8:14 PM
Double tapped GFCI breaker sspradling Electrical Inspections 6 12/9/06 10:51 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM


All times are GMT -4. The time now is 8:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts