Default small neutral service entrance conductors

This is a 200 AMP service. The 120V hot conductors look appropriate but the neutral is smaller. Problem with this? Thanks.
Attached Thumbnails
small-neutral-service-entrance-conductors-pict0014-small-.jpg.JPG
Views:	236
Size:	77.4 KB
ID:	38164  
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/28/10, 1:07 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: small neutral service entrance conductors

Neutral(grounded conductor) can be one size smaller.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 7/28/10, 1:12 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: small neutral service entrance conductors

Size the Neutral Conductor: 220.22

310-15(B)(6) states that the neutral service and/or feeder conductor can be smaller than the ungrounded (hot) conductors, provided the requirements of 215.2, 220.22 and 230.42 are met. 250.24(B)(1) states that the neutral cannot be smaller than the required grounding electrode conductor specified in Table 250.66



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #4  
Old 7/28/10, 4:04 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: small neutral service entrance conductors

Quote:
Originally Posted by mlarson View Post
Neutral(grounded conductor) can be one size smaller.
Although it may work out to be that way, one size smaller is not part of the NEC. The neutral conductor is sized according to the calculated maximum unbalanced load. As Michael said it can't be smaller than the size permitted for the GEC.

Quote:
220.61 Feeder or Service Neutral Load.
(A) Basic Calculation. The feeder or service neutral load shall be the maximum unbalance of the load determined by this article. The maximum unbalanced load shall be the maximum net calculated load between the neutral conductor and any one ungrounded conductor.
Quote:
250.24(C) Grounded Conductor Brought to Service Equipment. Where an ac system operating at less than 1000 volts is grounded at any point, the grounded conductor(s) shall be run to each service disconnecting means and shall be connected to each disconnecting means grounded conductor(s) terminal or bus. A main bonding jumper shall connect the grounded conductor(s) to each service disconnecting means enclosure. The grounded conductor(s) shall be installed in accordance with 250.24(C)(1) through (C)(3).
Exception: Where more than one service disconnecting means are located in a single assembly listed for use as service equipment, it shall be permitted to run the grounded conductor(s) to the assembly common grounded conductor(s) terminal or bus. The assembly shall include a main bonding jumper for connecting the grounded conductor(s) to the assembly enclosure.
(1) Routing and Sizing. This conductor shall be routed with the phase conductors and shall not be smaller than the required grounding electrode conductor specified in Table 250.66 but shall not be required to be larger than the largest ungrounded service-entrance phase conductor. In addition, for service-entrance phase conductors larger than 1100 kcmil copper or 1750 kcmil aluminum, the grounded conductor shall not be smaller than 12½ percent of the area of the largest service-entrance phase conductor. The grounded conductor of a 3-phase, 3-wire delta service shall have an ampacity not less than that of the ungrounded conductors.
(2) Parallel Conductors. Where the service-entrance phase conductors are installed in parallel, the size of the grounded conductor shall be based on the total circular mil area of the parallel conductors as indicated in this section. Where installed in two or more raceways, the size of the grounded conductor in each raceway shall be based on the size of the ungrounded service-entrance conductor in the raceway but not smaller than 1/0 AWG.
FPN: See 310.4 for grounded conductors connected in parallel.
Reply With Quote
  #5  
Old 7/28/10, 4:28 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: small neutral service entrance conductors

Would you write up FI?
Reply With Quote
  #6  
Old 7/28/10, 5:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: small neutral service entrance conductors

Mark do you see an issue with this installation?
Reply With Quote
  #7  
Old 7/28/10, 6:36 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: small neutral service entrance conductors

It's fairly common but I should have said just smaller.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 6:39 PM
Service Entrance Panels gwhite1 Electrical Inspections 4 5/15/06 8:33 PM


All times are GMT -4. The time now is 8:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts