Default Smoke Alarm Insanity

I am going crazy here. Last night about 12:00AM our smoke alarm went off on the 2nd floor. Took a tour of the house (stubbed my toe twice in the dark) No fire, no smoke, nothing anywhere. Took a magazine and waved air across the detector and it stopped. Went back to bed. An hour later same thing happened. I decided to unplug the detector from the wire harness. All our smoke alarms are hard wired, and are about 16 years old. I figured maybe this particular detector was done for and just needed replacement.

So today I bought a new smoke alarm from Home Depot. Killed the power at the breaker panel, made all the new wiring connections, and returned power to the circuit. Instantly the new smoke alarm goes off. I took a battery powered detector from the basement and brought it upstairs with a fresh battery to see if perhaps there was something going on that my nose did not detect. Nothing. Not even a chirp.

Anybody have any suggestions or ideas? I have unplugged the new smoke alarm, and returned power to the other detectors in the house, and am keeping the battery operated one upstairs for the time being.....

I am stumped here....
Reply With Quote
  #2  
Old 1/30/09, 10:42 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Smoke Alarm Insanity

The only thing that rings a bell with me is some info I got from a client once...

They had some semi hidden plumbing leaks in a new home and said a smoke alarm started going off. Fire dept came out and could find nothing except some water leaking.


I suggest checking the attic area over that detector for moisture problems.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 1/30/09, 10:43 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Smoke Alarm Insanity

Take all the smokes that are hardwired and take 'em down. Take a shopvac and blow them all out. While they are down, replace the batteries in them. That tends to fix the problem. I've had to do this to a few houses.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #4  
Old 1/30/09, 10:50 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Smoke Alarm Insanity

Hey John...

Shouldn't you be over at Austin's Saloon watching the 80's cover band Sixteen Candles?

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #5  
Old 1/30/09, 11:03 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: Smoke Alarm Insanity

I believe a smoke that is 16 years old may have out lived its life i believe they have an expiration date i will try to find it.
Reply With Quote
  #6  
Old 1/30/09, 11:05 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: Smoke Alarm Insanity

I found this will look for more.
Funny how we end up on bets over the weirdest things. Well with your bet with your friend, you loose. The guiding advice about smoke detector replacement seems to come from the National Fire Protection Agency (NFPA), they recommend replacing smoke detectors every 10 years (max). It seems that there is concern about electronics operating 24/7 for more than 10 years. So officially you loose, but from this knowledge, you gain the possibility of fixing a problem that might exist. Are your home's smoke detectors over 10 years in age? Be a hero, change them.
Reply With Quote
  #7  
Old 1/30/09, 11:12 PM
John A. Reim John A. Reim is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Grayslake, IL
Posts: 55
Default Re: Smoke Alarm Insanity

I am aware of the 10 year replacement guideline. Thanks. Doesn't explain why the brand new one is going off. I will try cleaning them all, and look for moisture in attic above. Thanks guys!

Anyone else have any ideas?
Reply With Quote
  #8  
Old 1/30/09, 11:23 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Smoke Alarm Insanity

John, I'm thinking your house is on fire. Dial 911; Get off the computer and the Nachi site and go outside.



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #9  
Old 1/30/09, 11:31 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Alarm Insanity

Just curious, are they ionization or photoelectric?
Reply With Quote
  #10  
Old 1/30/09, 11:46 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Alarm Insanity

All the alarms need to be compatible. Mixing brands doe not work. Even within the same brand some will not work with others.

Change all of them. The failure rate past 10 yrs. is great.
Reply With Quote
  #11  
Old 1/31/09, 11:14 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Smoke Alarm Insanity

Bumped into a similar situation once, but in a HIGH Humidity situation.

http://www.nachi.org/forum/f13/smoke...umidity-29589/

Hope this helps. I learned allot.
Reply With Quote
  #12  
Old 1/31/09, 12:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Alarm Insanity

When I get a service call for interconnected smoke detectors intermittently going off for no clear reason, I have one course of action. They all get replaced. Just saves callbacks on a system that probably has some age on it anyhow. It can be hard to find a matching smoke detector for a system that's already installed anyhow, and they must match for proper operation. You can monkey around with a shot in the dark for weeks or you can just replace them all. I choose the latter.
Reply With Quote
  #13  
Old 1/31/09, 2:26 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Smoke Alarm Insanity

I have to agree with Marc. Typically when I ran into intermittent smoke detector problems, the detectors were out of warranty, and exceeded/close the NFPA age recommendations. The only time I didn't recommend total replacement, it would be when I found a smoke detector in an 'unconditioned' space. Then I would talk about getting a 'heat' detector instead.

This is a reflection, not advice. My advice is to get a qualified electrician involved. Smoke detectors save lives, and locally we had a few lost because of things like batteries pulled out, being disconnected, etc.

Tom
Reply With Quote
  #14  
Old 1/31/09, 3:38 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Smoke Alarm Insanity

I just added on 1800 SF with 5 interconnected smoke alarms. All brand new. Not connected to any other alarm in the old part of the house. Mine went off about 3 times in the middle of the night for no apparent reason (always at night it seems). Scared the poop out of me. They finally quit the false alarms. Haven't had a problem in months. I say give it some time. Perhaps call the manufacturer...I was planning to do that but never got around to it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 2/3/09, 12:04 PM
John A. Reim John A. Reim is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Grayslake, IL
Posts: 55
Default Re: Smoke Alarm Insanity

Thank you gentlemen for the info and suggestions. I went out and dropped $100 on new detectors and installed them all. No problems now (knock on wood). I will sleep better at night now with no alarms going off, and some peace of mind!

John

I think it must have been a compatability issue as the new detector was not the same brand. Now they all match, and I am in compliance with the new CO detector rule!

Last edited by jreim; 2/3/09 at 12:06 PM.. Reason: cause of issue?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 questions staylor5 Electrical Inspections 14 12/18/09 2:32 AM
Smoke Detector placement jwicklander Electrical Inspections 0 9/17/08 6:43 PM
Escape, Fire & Smoke Alarms badair Interior Inspections 14 1/28/08 7:21 AM
Illinois: Carbon Monoxide Alarm Detector Act rcramer Legislation, Licensing & Legal Issues for Inspectors 2 2/9/07 7:52 AM


All times are GMT -4. The time now is 2:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts