Default Smoke Detectors on AFCI breaker...finally:-)

Finally found the smoke detectors on their own 20 amp AFCI breaker in the panel board...

People are learnin' here in the South...
Attached Thumbnails
smoke-detectors-afci-breaker-finally-22-jan-08-113.jpg   smoke-detectors-afci-breaker-finally-22-jan-08-114.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 1/22/08, 8:36 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 137
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

I hope they do included the battery back up in case the AFCI tripped for somereason.

Merci, Marc
Reply With Quote
  #3  
Old 1/23/08, 9:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Glad they are catching on.......even in the area I am inspecting now in Richmond they are finding out I am enforcing this requirement......heck they are just learning that it means receptacles AND lights as well as smokes.....( All 15 & 20A -120V circuits within the bedroom)....

Ironically enough....if the circuits are wired properly you wont see near the tripping issues...now as of Jan 1 of this year in regards to the combination requirement...we may see more but not enough false trip issues to out weigh the advantages...

Glad they are coming up to speed fella....hopefully it will make your job easier when they comply.

Also forgive my typos..i am limited to a motorola Q and all thumbs the past 2 days.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 1/23/08, 9:45 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Paul have you seen the LED diagnostic model yet?
http://news.thomasnet.com/fullstory/809016
Reply With Quote
  #5  
Old 1/23/08, 10:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Way cool Robert....no i had not seen them. I did recall Eaton talking about doing it and showed me some ideas but did not get to see them physically.

I have always maintained that AFCI's are every bit a diagnostic tool as well as a potential life saver....now they are really breaking huge ground with this technology....its good for the consumer and even with the increased requirements of 2008 .....they will prove they are worthy....

Thanks for the link.......i am excited about the AFCI's advancement.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 1/23/08, 10:42 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Yes the smokes should be on an AFCI, but I don't agree it is a good idea to put them on their own circuit all by themselves. Too easy to shut them off and forget about them. If you put them on the bedroom circuit people will notice when the circuit is off.

And a 20 amp circuit at that? Someone has money to burn.
Reply With Quote
  #7  
Old 1/23/08, 10:44 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Certainly smokes should be AFCI protected, but putting them on their own circuit serves no useful purpose and is a waste of a circuit.
Reply With Quote
  #8  
Old 1/23/08, 10:54 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Quote:
Originally Posted by Marc D. Shunk
Certainly smokes should be AFCI protected, but putting them on their own circuit serves no useful purpose and is a waste of a circuit.
ESPECIALLY a 20A circuit.
What a waste of copper!
Reply With Quote
  #9  
Old 1/23/08, 11:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

It's a matter of personal style, I suppose. It's certainly legal to dedicate an AFCI circuit to the smokes, but it is quite wasteful of an expensive breaker for maybe a total of a 1 amp load, plus the waste of a home run wire.
Reply With Quote
  #10  
Old 1/23/08, 11:11 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Hopefully this stuf will get settled with time.
Everything I read indicates most of the problems are related to poor installation.
Keeps us working ,from an HI standpoint.
Reply With Quote
  #11  
Old 1/24/08, 1:59 AM
Paul Sabados Paul Sabados is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Olathe, KS
Posts: 1,826
Default Re: Smoke Detectors on AFCI breaker...finally:-)

20 amps certainly seems like an overkill, especially with the low draw. Most of the fire marshalls that I have talked with are mixed on the dedicated breaker though, both sides offer good arguements, we'll see what the fire marshall orgs finally settle on.

Paul



Nachi #03091108
Olathe, Ks

Nachi Member of the Year 2005

Foundation for Safer Housing, President



Reply With Quote
  #12  
Old 1/24/08, 2:01 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Quote:
Originally Posted by psabados
20 amps certainly seems like an overkill, especially with the low draw. Most of the fire marshalls that I have talked with are mixed on the dedicated breaker though, both sides offer good arguements, we'll see what the fire marshall orgs finally settle on.
Actually, the NASFM has a position paper on that. Their official position is that it does not matter as long as the units have battery backups.
Reply With Quote
  #13  
Old 1/24/08, 2:26 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

Makes sense
Reply With Quote
  #14  
Old 1/24/08, 3:02 AM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Smoke Detectors on AFCI breaker...finally:-)

I had one [future] home owner want the smoke detectors on their own circuit so she could shut them off when cooking.

Gene pool filtering?

tom
Reply With Quote
  #15  
Old 1/24/08, 3:05 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detectors on AFCI breaker...finally:-)

actualy that can be a problem.
Some people smoke it up with no vents and seem to like it that way.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Escape, Fire & Smoke Alarms badair Interior 14 1/28/08 8:21 AM
Stand-alone Smoke detectors (posted by Pamela Bloom) AskNACHI.org AskNACHI.org Forum 1 7/10/07 3:11 AM
2 questions staylor5 Electrical 9 3/23/07 11:40 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
Can an AFCI offer GFCI protection gbeaumont Electrical 19 7/7/06 12:45 AM


All times are GMT -4. The time now is 4:22 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts