I say it is not OK!
Last edited by jtedesco1; 6/12/08 at 4:39 PM.. |
|
#2
|
||||
|
||||
|
At least they didnt use duct tape.
Troy Farmer Presidential Inspections LLC Chapter President Southern Idaho PO Box 2144 Eagle, Idaho 83616 208-573-5300 http://www.presidentialinspection.com http://info@presidentialinspection.com "He who can, does. He who can’t, teaches" "Where would we be without Teachers" |
|
#3
|
|||
|
|||
|
At least a couple of radiator clamps would be nice..
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#4
|
||||
|
||||
|
What is this copper strap (original zip tie) for and called?
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 6/2/09 at 12:56 AM.. |
|
#5
|
||||
|
||||
|
I write up all twisted GECs under a single lug.
|
|
#6
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe,
I write those up all day long. What would be the proper verbage and code citation for that?? |
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
As ugly as that is, using 250.122 you are only obligated to end up on a wire sized to protect for the largest breaker in the cludge so you are left with a possible listing violation on the "bugs" (how many wires will it connect) and the nebulous "workmanship" catch all.
If each group of branches in the "tree" was made with a listed splicing device, within it's limits and it all ended up on one wire that was large enough I am not sure where the violation is. |
|
#8
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet.
Last edited by jtedesco1; 6/12/08 at 4:39 PM.. |
|
#9
|
||||
|
||||
|
Joe,
I see grounds "bundled" under a single, large terminal lug all the time. was permitted by the AHJ. I even see neutrals bundled, as in older PushMatic panels. I always flag it. I would raise concerns with what is seen in the pic, but not cite code. |
|
#10
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Joe
|
|
#11
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
This is understood, the point being is that it should be noted. You can wisper in the ear of the electrician though just to show that you are aware of the rules have good reasons to make the defect apparent to CYA. |
|
#12
|
||||
|
||||
|
code reference 408.40
|
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Niether of those references prohibit tapping an EGC
|
|
#14
|
||||
|
||||
|
Quote:
Whenever I find numerous twisted GEC's tapped under one single bolt, I've been calling them out. So you're saying they are no big deal???? |
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is sloppy and bad workmanship, probably indicating unlicensed activity but strictly speaking I am not sure it is a code violation assuming listed splicing methods are used and the terminal wire is big enough to protect the highest ampacity circuit connected.
|
![]() |
| Thread Tools | |
|
|