Talking So you say this is OK?

I say it is not OK!

Last edited by jtedesco1; 6/12/08 at 4:39 PM..
Reply With Quote
  #2  
Old 4/30/08, 10:02 AM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 619
Default Re: So you say this is OK?

At least they didnt use duct tape.



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #3  
Old 4/30/08, 10:06 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: So you say this is OK?

At least a couple of radiator clamps would be nice..



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #4  
Old 4/30/08, 10:13 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: So you say this is OK?

What is this copper strap (original zip tie) for and called?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 6/2/09 at 12:56 AM..
Reply With Quote
  #5  
Old 4/30/08, 10:17 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: So you say this is OK?

I write up all twisted GECs under a single lug.
Reply With Quote
  #6  
Old 5/1/08, 7:21 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

Joe,

I write those up all day long. What would be the proper verbage and code citation for that??
Reply With Quote
  #7  
Old 5/1/08, 10:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

As ugly as that is, using 250.122 you are only obligated to end up on a wire sized to protect for the largest breaker in the cludge so you are left with a possible listing violation on the "bugs" (how many wires will it connect) and the nebulous "workmanship" catch all.
If each group of branches in the "tree" was made with a listed splicing device, within it's limits and it all ended up on one wire that was large enough I am not sure where the violation is.
Reply With Quote
  #8  
Old 5/2/08, 1:22 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

Quote:
Originally Posted by wsiegel
Joe,

I write those up all day long. What would be the proper verbage and code citation for that??

Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet.

Last edited by jtedesco1; 6/12/08 at 4:39 PM..
Reply With Quote
  #9  
Old 5/2/08, 8:00 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: So you say this is OK?

Joe,

I see grounds "bundled" under a single, large terminal lug all the time. was permitted by the AHJ.

I even see neutrals bundled, as in older PushMatic panels. I always flag it.

I would raise concerns with what is seen in the pic, but not cite code.
Reply With Quote
  #10  
Old 5/2/08, 8:14 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

Thanks Joe
Reply With Quote
  #11  
Old 5/2/08, 8:41 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

Quote:
Originally Posted by wsiegel
Thanks Joe
My pleasure, and we are all aware that the code reference was for information only and that the HI does not include that information in their reports, as Joe mentions, by not citing code.

This is understood, the point being is that it should be noted.

You can wisper in the ear of the electrician though just to show that you are aware of the rules have good reasons to make the defect apparent to CYA.
Reply With Quote
  #12  
Old 5/2/08, 9:06 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: So you say this is OK?

code reference 408.40
Reply With Quote
  #13  
Old 5/2/08, 9:27 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

Niether of those references prohibit tapping an EGC
Reply With Quote
  #14  
Old 5/2/08, 11:21 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: So you say this is OK?

Quote:
Originally Posted by Greg Fretwell
Niether of those references prohibit tapping an EGC
Well.....this is all new to me.

Whenever I find numerous twisted GEC's tapped under one single bolt, I've been calling them out.

So you're saying they are no big deal????
Reply With Quote
  #15  
Old 5/2/08, 4:45 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: So you say this is OK?

It is sloppy and bad workmanship, probably indicating unlicensed activity but strictly speaking I am not sure it is a code violation assuming listed splicing methods are used and the terminal wire is big enough to protect the highest ampacity circuit connected.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts