If two wires are first soldered together before being put into a breaker would it still be considered to be a double tap or is it now considered to be a single wire at the soldered point?
I would say double tapped, there is still 2 feeds even though they
are soldered together. carla |
Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
EDIT
I think I misunderstood the original post... I thought that the poster meant that the wires were soldered to a third wire and connected to the breaker... i thought this was more a question of the soldering... If I am to understand correctly at this point, two wires were soldered and the soldered connection was placed in the screw terminal? This would be incorrect and should be repaired. Last edited by Joey D'Adamo; 3/3/06 at 5:23 PM.. |
Paul
Its still two circuits being fed from one breaker. The breaker can't tell them apart. One wire per breaker. |
tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
So in this case instead of calling it out as a defect...
"Circuit has two wires attached. It is not known what electrical devices and/or fixtures are connected to these 2 wires. Recommend a licensed electrical contractor calculate load on these 2 wires to determine if the circuit breaker in question is overloaded. Overloading of electrical circuits can be an annoyance and a safety hazard" |
Well if that is the case, then why not put the two circuits pig tailed together in a junction box and pigtail a single line to the breaker?
By the way are you American? The Canadian Electrical Code maybe different, and the Electrical Safety Authority Inspector may not like the idea of a two wires soldered together, fwiw. |
No-No on the soldering them together part....perfectly fine to take the (2) wires off a breaker and wirenut them together and take a pigtail to the breaker...it is a solution for double taps....However as stated the entire load total of BOTH branch circuits are now added together...
The NEC does not specify how many devices can be on a circuit but it gives you guidelines for determining this in the basic general lightning calculations based on square foot of the dwelling....then you use that to determine how many 15 A or 20 A branch circuits you need....but the NEC does not specify it. Some breakers ( sq d- QO ) is listed for (2) wires but in most cases the wirenut splice option is the best for double taps...since most of the time we see this is in older panels anyway...for the most part. Just remember that pigtail has to be the same size as the wires it is junctioned to....but long story short....it all becomes one branch circuit at that point...... Paul W. Abernathy |
Joey,
Not to nitpick, but 12-112 only talks about splices of wires, it does not appear to address double taps or soldered double wires under the terminal screws. Rule 12-506 (1) states that joints may be made only in outlet boxes or junction boxes? |
Is this enough cya...whether wire nut double or solder double...either one?
Is really going to be hard for us electricians to tell the client that unless we place a amp probe on the lines but it it is safe to say the OCPD should protect both of these conductors in this case because they are now one circuit....Technically you could have 30 receptacles on a 15A or 20A circuit ( lord I hope NOT but could happen )....point is if the wires are double tapped on a breaker to begin with and it is not tripping...chances are when the "FIX" is made...probably wont trip either..... But as you DID state.....while having it looked at anyway by an Electrical Contractor they can see if the overall panel needs to be upgraded or expanded to keep the people from doing more double taps... Hope that explains it.. Paul W. Abernathy |
Thanks Paul...
My thoughts were that while the current owner may know that the addition on the rear of the home and bedroom 1 are tied together and avoid running 2 blow dryers, a cd player, and 2 heating irons at the same time...the new owners may not. After they move in and start popping that breaker...they hire an electrician...he comes in and says "why didn't the HI mention this...."....and then you know what comes next.... Just trying to avoid this sort of thing....thanks for your response. |
Hey guys,
Sorry for mucking up the thread... I made a mistake reading the original post. I thought this was a question about soldering and not "soldered double taps." Anyway, just to clarify... under the CEC soldering would be ok as long as the solder joint was properly taped and a SINGLE wire attached to the terminal... otherwise it's wrong. I had trouble invisioning someone soldering two wires and then putting the soldered joint under one screw... seems like a lot of effort to do something wrong! I deleted my posts and hopefully the thread is ok now. |
Just as a note...not sure to whom.....yes, you can have spliced within the panel....
312.8 Enclosures for Switches or Overcurrent Devices. Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space. 110.14 (B) Splices. Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose. Paul W. Abernathy |
I will say however...most electricians when they see it will know what it is..not what is controls...but what it is...and will know it was done because of no breaker space left in the panel......we have no problems figuring that part out...lol Paul W. Abernathy |
Joey...No problem fella........we got it back on track....YOU jump in anytime their fella......
Paul W. Abernathy |
| Double Tap Questions | jkogel | Electrical Inspections | 6 | 6/28/07 9:46 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 9:04 AM |
| Double Tap! | wward | Electrical Inspections | 12 | 2/22/07 5:39 PM |
| Double Taps | rwand1 | Canadian Inspectors | 39 | 3/29/06 7:16 PM |