Default Solid conductor aluminum

I have seen tons of "stranded" #6 aluminum for ranges etc, but I have never seen solid conductor #6 before----in this case to the range. How would you report on this----2003 house.
Reply With Quote
  #2  
Old 4/24/07, 7:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

Why do you feel the need to report a legal installation?
Reply With Quote
  #3  
Old 4/24/07, 7:56 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

Marc, at what date between 1975 and now would you consider solid conductor aluminum wiring ok?
Reply With Quote
  #4  
Old 4/24/07, 8:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

Quote:
Originally Posted by cbuell
Marc, at what date between 1975 and now would you consider solid conductor aluminum wiring ok?
Depends on the alloy number. That could be any date. In this particular gauge, I'd never worry about it, no matter what alloy number or what year vintage.
Reply With Quote
  #5  
Old 4/24/07, 8:57 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

I'd be very curious to see what it says on the sheath of a 2003 vintage cable with a "solid" #6AL inside.
I wouldn't think such a thing existed.
Reply With Quote
  #6  
Old 4/24/07, 11:38 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

I'm with Petey, never seen any cable with solid (anything) above #10, only bare solid 8, 6 and 4 for grounding and that was copper.
Reply With Quote
  #7  
Old 4/25/07, 12:43 AM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

Strange stuff---here is a picture of the ground and neutral
Attached Thumbnails
solid-conductor-aluminum-sierra-240.jpg  
Reply With Quote
  #8  
Old 4/25/07, 7:03 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

Wow! That looks like solid conductor SER cable.
Strange to say the least.
Reply With Quote
  #9  
Old 4/28/07, 11:40 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

Charles
Would you be able to get back to take more pictures and get a number off of the cable these conductors are installed in?
Reply With Quote
  #10  
Old 4/28/07, 12:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

The funny thing is I don't see anything prohibiting #8 solid and larger in a cable. You can't pull that in a raceway tho. The only raceway exception is the GEC
Reply With Quote
  #11  
Old 4/28/07, 5:02 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Solid conductor aluminum

Quote:
Originally Posted by Greg Fretwell
I'm with Petey, never seen any cable with solid (anything) above #10, only bare solid 8, 6 and 4 for grounding and that was copper.
I believe you can get solid single conductor Pyrotenax up too 500 mcm
I did a inspected a home with I think it was #2 solid pyro service a few years ago .
I will try and find the pictures .
I put in a lot back about 1960 and we had many sizes 2/0 was very common.

Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #12  
Old 4/28/07, 9:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Solid conductor aluminum

Does this help?

http://www.harger.com/catalog2004/1_1_2.pdf
Reply With Quote
  #13  
Old 4/28/07, 9:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Solid conductor aluminum

MI cable in a house? Amazing.
Reply With Quote
  #14  
Old 4/28/07, 10:08 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Solid conductor aluminum

Quote:
Originally Posted by Greg Fretwell
MI cable in a house? Amazing.
The main distributor for Canada is in Trenton and I figured the home owner could have worked there many years ago .

Added Below
The house was knob and tube and had vermulite for insulation so I expect it was from the 1950 +or-
Found the pictures send me email and I will send them back.
Do not know how to post here
Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 4/28/07 at 10:14 PM..
Reply With Quote
  #15  
Old 4/29/07, 11:56 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Solid conductor aluminum

Quote:
Originally Posted by cbuell
I have seen tons of "stranded" #6 aluminum for ranges etc, but I have never seen solid conductor #6 before----in this case to the range. How would you report on this----2003 house.
Charles,
I don't see anything to write up considering the facts you provided. It has anti oxidant at the connections (at least appears to). If it appeared to be a part of the original install as approved by L&I, then I would not personally have a concern.
Does the panel have an L&I "cover" and/ or "final" tag?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solid Aluminum Wiring carolinainspector Electrical Inspections 7 6/19/06 5:06 PM


All times are GMT -4. The time now is 8:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts