I have seen tons of "stranded" #6 aluminum for ranges etc, but I have never seen solid conductor #6 before----in this case to the range. How would you report on this----2003 house.
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why do you feel the need to report a legal installation?
|
|
#3
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc, at what date between 1975 and now would you consider solid conductor aluminum wiring ok?
|
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I'd be very curious to see what it says on the sheath of a 2003 vintage cable with a "solid" #6AL inside.
I wouldn't think such a thing existed. |
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I'm with Petey, never seen any cable with solid (anything) above #10, only bare solid 8, 6 and 4 for grounding and that was copper.
|
|
#7
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Strange stuff---here is a picture of the ground and neutral
|
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Wow! That looks like solid conductor SER cable.
Strange to say the least. |
|
#9
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Charles
Would you be able to get back to take more pictures and get a number off of the cable these conductors are installed in? |
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The funny thing is I don't see anything prohibiting #8 solid and larger in a cable. You can't pull that in a raceway tho. The only raceway exception is the GEC
|
|
#11
|
||||
|
||||
|
Quote:
I did a inspected a home with I think it was #2 solid pyro service a few years ago . I will try and find the pictures . I put in a lot back about 1960 and we had many sizes 2/0 was very common. Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#12
|
||||
|
||||
|
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
MI cable in a house? Amazing.
|
|
#14
|
||||
|
||||
|
Quote:
Added Below The house was knob and tube and had vermulite for insulation so I expect it was from the 1950 +or- Found the pictures send me email and I will send them back. Do not know how to post here Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. Last edited by rcooke; 4/28/07 at 10:14 PM.. |
|
#15
|
||||
|
||||
|
Quote:
I don't see anything to write up considering the facts you provided. It has anti oxidant at the connections (at least appears to). If it appeared to be a part of the original install as approved by L&I, then I would not personally have a concern. Does the panel have an L&I "cover" and/ or "final" tag? |
![]() |