Thumbs down Some problems here to identify, what are they?

If you know what's wrong cite "them thar" problems here! ...
Reply With Quote
  #2  
Old 1/5/07, 7:50 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

Recommend immediate repair or replacement by qualified person.

Roy Cooke
Reply With Quote
  #3  
Old 1/5/07, 7:59 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

(submitted by Joe Tedesco)
quote: (picture 1) shows a 208/120V panelboard, typical of panelboards throughout the building. In addition to other violations, notice that the panel is not grounded, that neutrals and grounding conductors are freely mixed on the neutral bus, multiple-colored insulations on neutral bus, white used as a phase conductor in feeder, etc.
quote: (picture 2) shows a Fernco plumbing coupling used on the service conductor raceways between a pad-mounted transformer and the service entrance switchgear. This is a 1200A 480V service.

Enjoy

Robert E. Brown
Reply With Quote
  #4  
Old 1/5/07, 8:07 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

OK, let's make believe we are training a new home inspector, you are the experienced inspector and can see the many problems, so, why should they be referred to a professional?

Surely, we have many here who can do this.
Reply With Quote
  #5  
Old 1/5/07, 1:40 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

Besides the obvious overheated lug and double taps I also see missing connectors in the upper right, uncovered KO and EIGHT disconnects. Those small breakers probably do not have sufficient interrupt ratings/service rated
Reply With Quote
  #6  
Old 1/5/07, 6:03 PM
lfranklin lfranklin is offline
New User
 
Join Date: Jan 2003
Location: Kodak, TN
Posts: 31
Please Note: lfranklin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

If they are are all twin breakers or piggy back breakers.
Does this make the panel have more circuits than it was intended for. Now making the panel undersized
Reply With Quote
  #7  
Old 1/5/07, 7:04 PM
Robert Francis's Avatar
Robert Francis Robert Francis is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Toronto, ON
Posts: 406
Default Re: Some problems here to identify, what are they?

Quote:
Originally Posted by jtedesco1
OK, let's make believe we are training a new home inspector, you are the experienced inspector and can see the many problems, so, why should they be referred to a professional?

Surely, we have many here who can do this.
Burnt/meted wirining, Alunimum wiring, double taps, main double tapped, can;t make it out but looks like wrong breakers to wire size (might be wrong on that as cn't make it out) GET A LICENSED ELECTRIAN IN HERE ASAP and thats just to start;

SO what did I win besides being almost electricfied removing tha cover????
Reply With Quote
  #8  
Old 1/5/07, 10:45 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Arrow Re: Some problems here to identify, what are they?

What will be the prize? Your observing the need for the correction, and telling me what you want for the prize, and I will ask Nick for something, on the other hand if you look over on the Electric West show site www.ecmweb.com for the February convention in Long Beach, they have a contest on: "What's Wrong here?" and the winner can win some big bucks, just a way of celebrating the issues discovered by that same subject in their publications for over 10 years, look for the picture and commentary already used in the past:



1
2

3

4

5

6

7

8

9

10

Next
Reply With Quote
  #9  
Old 1/5/07, 10:54 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

Quote:
Originally Posted by lfranklin
If they are are all twin breakers or piggy back breakers.
Does this make the panel have more circuits than it was intended for. Now making the panel undersized
See the UL Directory under PANELBOARDS QEUY for specific information related to use of the "twins" which will advise that the label on the cabinet will provide the listing and use of them.
Reply With Quote
  #10  
Old 1/6/07, 10:23 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Some problems here to identify, what are they?

Joe,

Back to your picture. Is that box the service panel. If not, its improperly bonded, a wrongly identified wire into one of the breakers, improper bundling of wires, the obvious burned wires and double taps, Zinsco or Sylvania box, looks like there are some non compatable breakers in that box, possible damged insulation on the upper wires.
Reply With Quote
  #11  
Old 1/6/07, 10:37 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

If you look real close on the right side there is no neutral installed because the lug is empty.

This is a 1200A 480V service, meaning this it was the 3-wire supply to this panelboard from the main disconnect elsewhere.

The use of colors is sometimes confusng to some, and while it is true that phases A and C have colors other than white, gray, or 3 stripes along the entire wire, the B phase is white here, and that is not the proper way to identify that "ungrounded conductor",

I must get ready for the road now and hope that someone else who sees other items here can comment. The original images were sent to me and I think there may be some comments in the archives.
Reply With Quote
  #12  
Old 1/6/07, 11:31 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Some problems here to identify, what are they?

Hey Joe,

Always nice pictures fella and I will comment on the FIRST one as it is easier to do it that way versus a bunch of pictures...gets confusing but here we go.

Obvious Issues :
1.) No OCPD on the main SE Conductors
2.) No OCPD on the illegal double tap on the main lug connection points
3.) Wrongful Double Tap on the Main Termination Point
4.) No grounded conductor re-identification ( Field Done- White Wrap )
5.) Missing KO's not plugged
6.) Wrongful termination of a WHITE wire onto a breaker without re-identify
7.) Bundling and or overcrowding of conductors into the enclosure, Unless it is only sleeved for protection....can't really tell on that one...I cant see above it.
8.) Can't tell where that stranded aluminum conductor terminates on the buss bar....my eyes just SUCK today.
9.) Conductors comeing through the open KO's without connectors
10.) Another "Grounded" conductor on the wires above not identified as it should.
11.) Obvious Melting due to overloaded circuit on the double tap.

Ok....thats enough...I do question the grounding of this panel with the solid coming throught he same connector...and where it possibly goes.if into the meter can on the other side...parrallel paths and a problem...and I dont see a supplimental which could be suggested and added.

Also with the rust on that connector in the upper right and signs of it on the lower right of the panel, I would also say moisture is getting in through those KO's and connector at the upper right...needs to be looked at besides being a Zinsco and probably not sized properly for their NEW addition of the overheated double tap......HI's recomment evaluation is proper.

I would certainly recommend it be evaluated, some items not seen in a picture could possibly be identified as well....just cant see it that clear....actually early for me I got rather TIPSEY last night...(head spins )

Nice picture Joe........



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 1/6/07 at 12:07 PM..
Reply With Quote
  #13  
Old 1/6/07, 4:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

Quote:
Originally Posted by jtedesco1
(submitted by Joe Tedesco)quote: (picture 1) shows a 208/120V panelboard, typical of panelboards throughout the building. In addition to other violations, notice that the panel is not grounded, that neutrals and grounding conductors are freely mixed on the neutral bus, multiple-colored insulations on neutral bus, white used as a phase conductor in feeder, etc.
Here's my shot at that pic:


-The panel appears to be affixed to the plywood with #8 bugle head type wood screws (probably drywall screws). This does not meet the 110.13(A) requirements in the eyes of many.
-General appearance of installation does not meet 110.12, as clarified by the NECA standards.
-Panelboard enclosure may not be rated to contain the RR7 style lighting relay in the upper right corner. 110.3(B)
-The #4 grounded conductor terminating on the neutral bar has a green outer covering, in violation of 200.6(B)
-The grounded conductor feeding this panel is sorely undersized. 250
-The equipment grounding conductor appears to be by way of the EMT that feeds this panel. There is no equipment ground bar installed in this panel, and the MC cables appear to have their equipment grounding conductors landed on the neutral bar.
-B phase conductor has a white outer covering, in violation of 310.12(C)
-There is a red wire on the neutral bar, in violation of 200.6(A)
-Several branch circuit breakers are double tapped, but this is okay with a QO breaker under many circumstances.
-One grounded conductor of the one MC cable appears to share a hole with an equipment grounding conductor, in violation of 408.41
-There appears to be a single red #12 conductor in the feeder pipe, without the rest of that circuit's conductors, in violation of 300.5(I)
-The yellow conductor on the left, above the zip tie, appears to have arcing type damage, in violation of 110.7
-The grounded conductor of the lighting transformer is not remarked white, in violation of 200.6(A)
-Piece of cardboard in panel, and some of the MC or AC cables appear to still have the interleaving paper on them, in violation of 240.24(D)

Last edited by Marc D. Shunk; 1/6/07 at 5:19 PM..
Reply With Quote
  #14  
Old 1/6/07, 6:16 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Some problems here to identify, what are they?

ahhh...thats the problem...which panel are we supposed to be observing and citing.....the first one shown on the one MARC is commenting on.

Keep it one panel at a time fella...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/24/08, 5:41 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Some problems here to identify, what are they?

Bump
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hire IAQ Professional dplummer Ancillary Services & Additional Topics 0 11/15/07 10:01 AM
Tidbits from the ASHI Message Board jbushart Misc. Discussion 124 4/27/07 12:05 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical 9 4/18/07 8:22 PM
Common Defects List by Age of House trausch Education 10 6/12/06 5:52 AM
CBC - Province called on to force home-sellers to disclose property's problems rwand1 Canadian Inspectors 2 4/5/06 9:40 PM


All times are GMT -4. The time now is 6:39 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts