Ok, I've called out the last two spa tubs I've inspected for not having the proper cold water bonding in place. Each has had a metal motor casing with an "Empty" bonding clamp and or lug clearly visible on the motor. The agent informs me today that an independent licensed electrical contractor inspected and determined that the motors were of a sealed design and did not require bonding.
I'm totally confused, I thought any and all metal within 5' of a electrically supplied pool, spa, spa tub, etc. had to be bonded. Any thoughts? |
|
#2
|
||||
|
||||
|
If the motor is double insulated, it need not be bonded.
When I see an empty bonding lug, I call it out (assuming the supply piping is metallic), and let the sparky determine if the motor is double insulated. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Please Note:
whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Jeff,
Each of these structures has had copper fresh water plumbing. Just for the sake of asking, why does the OEM equip any motor that doesn't require bonding, with a bonding lug? |
|
#4
|
||||
|
||||
|
Good question, but I don't know the answer
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Was the spa tub piping metal or plastic?
|
|
#6
|
||||
|
||||
|
Please Note:
whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Plastic, I haven't seen any metal on bathroom spa tubs for many years. The supply plumbing to the faucets was copper.
|
|
#7
|
|||
|
|||
|
Quote:
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#8
|
||||
|
||||
|
Please Note:
whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where's Paul, Greg and or Speedy when you need'em?
|
|
#9
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#10
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
To be honest I have not seen a D-I motor with bond lug.
If the lug is present, I use it. |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The answer is always supposed to be on the label. U/L has a marking guide for pool/spa motors, just like most equipment and that defines what they have to list there.
|
|
#13
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
The 2005 NEC Handbook reminds us in the commentary to 680.21(B) that attempting to bond a double insulated motor compromises the double insulated properties. Sort of a no-brainer, when you think about it. I can say with reasonable certainty that a a motor with a factory bond lug is not double insulated.
...pump[s] incorporating a system of double insulation are grounded; however, they are not required to be incorporated into the bonding system required by 680.26(B), since the act of bonding compromises the double-insulation system. |
|
#14
|
|||
|
|||
|
Always appreciate learning from you guys...
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#15
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
What would you bond it to if the plumbing is plastic and there is no other metal parts large enough to require bonding?
|
![]() |