I found a spliced Ground in the main panel. I called it out and just wanted to make sure I was correct. I have never come across this before.
|
|
#2
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
(C) Continuous. Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted in (1) through (4): (1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process. (2) Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor. (3) Bonding jumper(s) from grounding electrode(s) and grounding electrode conductor(s) shall be permitted to be connected to an aluminum or copper busbar not less than 6 mm × 50 mm (1⁄4 in. × 2 in.). The busbar shall be securely fastened and shall be installed in an accessible location. Connections shall be made by a listed connector or by the exothermic welding process. (4) Where aluminum busbars are used, the installation shall comply with 250.64(A). |
|
#3
|
||||
|
||||
|
A little housekeeping wouldn't hurt either
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#4
|
|||
|
|||
|
It is defnintely not a job for a wire nut !! However, most HIs would probably not catch the distinction as to the type of connection permitted. A very good education thread for us all.
Thanks Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#5
|
||||
|
||||
|
Is that dirt or just a massive build-up of dust over the years?
|
|
#6
|
|||
|
|||
|
No.....that looks like a standard wirenut.
Remember the concept is this......if lighting or transient voltages as well as potential higher voltage sources ( how ever you would like to call it) gets imposed onto the GEC and hits that wirenut it will melt open and defeat its purpose.....now and in the future. Read Joes NEC statements.......notice all methods maintain a constant connection during the event....a wirenut does not in this situation. Paul W. Abernathy |
|
#7
|
|||
|
|||
|
Quote:
When exactly is a wirenut allowed in a service panel? I see them quite a bit in the following circumstances: 1. A branch circuit is too short due to a replaced service panel or moving a breaker to another location. So, it's one 12awg from the circuit and one 12awg to the 20amp 120 breaker. 2. Two 15 or 20 amp branch circuits are needed but they only have one breaker of the appropriate size (usually double lugged but in rare cases), their will be 2 12awg from the circuits and one 12awg to the 20amp 120 breaker. I don't see them often on neutral or ground wires, but I do see them double, triple, ... lugged quite often. Thanks! Happy Holidays All! Brian Zimbelman Circle Z Inspection Services http://www.circlezinspections.com 575-535-4481 (wk) 575-313-1281 (cell) |
|
#8
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Brian,
It is not that wirenuts are not allowed in panels. The problem shown here is with its' use to extend the grounding conductor. Please read post #2 to see the Code accepted methods if a grounding conductor needs to be spliced. Wirenuts used to extend the branch circuit wiring as in your two examples are fine. There are limits on cross-sectional fill area, like how many wires can be in a box, however, you would really need quite a few connections in the same area to exceed this rule. Last edited by Jim Port; 12/20/07 at 2:45 PM.. |
|
#9
|
|||
|
|||
|
This is a potentially confusing thread. The GROUNDING ELECTRODE CONDUCTOR shall not be spliced except as noted in JT's post above. An EQUIPMENT GROUND can be spliced using a wire nut, as can a grounded or ungrounded conductor.
There is no prohibition to using wire nuts in the serivce panel. |
|
#10
|
|||
|
|||
|
Thanks guys, just wanted to make sure I was understanding it...
Brian Zimbelman Circle Z Inspection Services http://www.circlezinspections.com 575-535-4481 (wk) 575-313-1281 (cell) |
|
#11
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The issue about the splicing in any cabinet is better described by the rule: Last edited by jtedesco1; 1/22/08 at 7:12 AM.. |
|
#12
|
|||
|
|||
|
lol.....typical students of the Code...lo
1) nothing was ever said about wirenuts in a panel. The statement was made that the wirenut shown does not meet the requirements of the GEC being with splices.... 2) The NEC prohibits splices in a panel enclosure with switches or overcurrent devices...But makes allowance for them if the space is provided and does not exceed 75 percent of the enclosures cross sectional values......most panels will allow for this space so it is not an issue. Again its important to understand the thread.....someone i believe implied a statement that splices are not allowed in a panel...however i digress.....either way this splice (wirenut) is not allowed because this connection is not allowed. I can also promise you that in the event of lightning imposed on that GEC......that splice will melt like butta.....thus removing the required connection to the GE. again this thread should not have morphed into a wirenut in panels issue.........by now all HI's should know splices in a panel are allowed....hard to ever have a service change without any. Paul W. Abernathy Last edited by pabernathy; 12/21/07 at 7:40 PM.. |
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If you really had "lightning" on that GEC it wouldn't matter if it was CadWelded. Lightning will not make a 180 degree turn. It would just shoot out the end. That is why air terminal conductors need to be run as straight as possible with very wide radius turns. Generally you will not really get lightning in a panel and if you do it will be toast. I did take a direct hit on the air terminal above my weather station this summer with minimal damage.
|
|
#14
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
"280.12 Routing of Surge Arrester Grounding Conductors. The conductor used to connect the surge arrester to line, bus, or equipment and to a grounding conductor connection point as provided in 280.21 shall not be any longer than necessary and shall avoid unnecessary bends."
. and on another note, the original picture shows signs of dirt in the bottom, this could be because of a flood, and if so, the weep holes in the bottom of the cabinet may be plugged up. |
|
#15
|
||||
|
||||
|
Thanks Paul
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Ground Wires Inside a Panel | mveitenhans | Electrical Inspections | 13 | 10/29/06 11:39 AM |
| Two ground wires | jlybolt | Electrical Inspections | 8 | 8/10/06 2:06 PM |
| Harmonized Ground Fault Circuit Interrupters | jtedesco1 | Electrical Inspections | 5 | 3/21/06 8:48 AM |