Default Spliced Ground

I found a spliced Ground in the main panel. I called it out and just wanted to make sure I was correct. I have never come across this before.
Attached Thumbnails
spliced-ground-100_3060.jpg  




Mike Hazelwood
Bakersfield, California
mike@calproinspections.com
www.calproinspections.com
Reply With Quote
  #2  
Old 12/20/07, 3:11 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spliced Ground

(C) Continuous.
Grounding electrode conductor(s) shall be
installed in one continuous length without a splice or joint
except as permitted in (1) through (4):

(1) Splicing shall be permitted only by irreversible
compression-type connectors listed as grounding and
bonding equipment or by the exothermic welding
process.

(2) Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.

(3) Bonding jumper(s) from grounding electrode(s) and
grounding electrode conductor(s) shall be permitted to
be connected to an aluminum or copper busbar not less
than 6 mm × 50 mm (
14 in. × 2 in.). The busbar shall be
securely fastened and shall be installed in an accessible
location. Connections shall be made by a listed connector
or by the exothermic welding process.

(4) Where aluminum busbars are used, the installation

shall comply with 250.64(A).
Reply With Quote
  #3  
Old 12/20/07, 6:11 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Spliced Ground

A little housekeeping wouldn't hurt either



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #4  
Old 12/20/07, 9:54 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Spliced Ground

It is defnintely not a job for a wire nut !! However, most HIs would probably not catch the distinction as to the type of connection permitted. A very good education thread for us all.

Thanks



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 12/20/07, 10:32 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Spliced Ground

Is that dirt or just a massive build-up of dust over the years?
Reply With Quote
  #6  
Old 12/20/07, 11:03 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Spliced Ground

No.....that looks like a standard wirenut.

Remember the concept is this......if lighting or transient voltages as well as potential higher voltage sources ( how ever you would like to call it) gets imposed onto the GEC and hits that wirenut it will melt open and defeat its purpose.....now and in the future.

Read Joes NEC statements.......notice all methods maintain a constant connection during the event....a wirenut does not in this situation.



Paul W. Abernathy
Reply With Quote
  #7  
Old 12/20/07, 11:52 AM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Spliced Ground

Quote:
Originally Posted by pabernathy
No.....that looks like a standard wirenut.

Remember the concept is this......if lighting or transient voltages as well as potential higher voltage sources ( how ever you would like to call it) gets imposed onto the GEC and hits that wirenut it will melt open and defeat its purpose.....now and in the future.

Read Joes NEC statements.......notice all methods maintain a constant connection during the event....a wirenut does not in this situation.
So Paul / Electrical Gurus of NACHI -

When exactly is a wirenut allowed in a service panel?

I see them quite a bit in the following circumstances:

1. A branch circuit is too short due to a replaced service panel or moving a breaker to another location. So, it's one 12awg from the circuit and one 12awg to the 20amp 120 breaker.

2. Two 15 or 20 amp branch circuits are needed but they only have one breaker of the appropriate size (usually double lugged but in rare cases), their will be 2 12awg from the circuits and one 12awg to the 20amp 120 breaker.

I don't see them often on neutral or ground wires, but I do see them double, triple, ... lugged quite often.

Thanks!

Happy Holidays All!



Brian Zimbelman
Circle Z Inspection Services
http://www.circlezinspections.com
575-535-4481 (wk)
575-313-1281 (cell)
Reply With Quote
  #8  
Old 12/20/07, 2:40 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spliced Ground

Brian,

It is not that wirenuts are not allowed in panels. The problem shown here is with its' use to extend the grounding conductor. Please read post #2 to see the Code accepted methods if a grounding conductor needs to be spliced.

Wirenuts used to extend the branch circuit wiring as in your two examples are fine. There are limits on cross-sectional fill area, like how many wires can be in a box, however, you would really need quite a few connections in the same area to exceed this rule.

Last edited by Jim Port; 12/20/07 at 2:45 PM..
Reply With Quote
  #9  
Old 12/21/07, 12:04 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Spliced Ground

This is a potentially confusing thread. The GROUNDING ELECTRODE CONDUCTOR shall not be spliced except as noted in JT's post above. An EQUIPMENT GROUND can be spliced using a wire nut, as can a grounded or ungrounded conductor.

There is no prohibition to using wire nuts in the serivce panel.
Reply With Quote
  #10  
Old 12/21/07, 12:06 AM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Spliced Ground

Thanks guys, just wanted to make sure I was understanding it...



Brian Zimbelman
Circle Z Inspection Services
http://www.circlezinspections.com
575-535-4481 (wk)
575-313-1281 (cell)
Reply With Quote
  #11  
Old 12/21/07, 5:41 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spliced Ground

Quote:
Originally Posted by pdickerson
This is a potentially confusing thread. The GROUNDING ELECTRODE CONDUCTOR shall not be spliced except as noted in JT's post above. An EQUIPMENT GROUND can be spliced using a wire nut, as can a grounded or ungrounded conductor.

There is no prohibition to using wire nuts in the serivce panel.
Thanks, this is very important, the correct terms and definitions should always be used, especially in any reports.

The issue about the splicing in any cabinet is better described by the rule:

Last edited by jtedesco1; 1/22/08 at 7:12 AM..
Reply With Quote
  #12  
Old 12/21/07, 7:36 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Spliced Ground

lol.....typical students of the Code...lo

1) nothing was ever said about wirenuts in a panel. The statement was made that the wirenut shown does not meet the requirements of the GEC being with splices....

2) The NEC prohibits splices in a panel enclosure with switches or overcurrent devices...But makes allowance for them if the space is provided and does not exceed 75 percent of the enclosures cross sectional values......most panels will allow for this space so it is not an issue.

Again its important to understand the thread.....someone i believe implied a statement that splices are not allowed in a panel...however i digress.....either way this splice (wirenut) is not allowed because this connection is not allowed.

I can also promise you that in the event of lightning imposed on that GEC......that splice will melt like butta.....thus removing the required connection to the GE.

again this thread should not have morphed into a wirenut in panels issue.........by now all HI's should know splices in a panel are allowed....hard to ever have a service change without any.



Paul W. Abernathy

Last edited by pabernathy; 12/21/07 at 7:40 PM..
Reply With Quote
  #13  
Old 12/21/07, 8:47 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spliced Ground

If you really had "lightning" on that GEC it wouldn't matter if it was CadWelded. Lightning will not make a 180 degree turn. It would just shoot out the end. That is why air terminal conductors need to be run as straight as possible with very wide radius turns. Generally you will not really get lightning in a panel and if you do it will be toast. I did take a direct hit on the air terminal above my weather station this summer with minimal damage.
Reply With Quote
  #14  
Old 12/21/07, 9:26 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spliced Ground

Quote:
Originally Posted by Greg Fretwell
If you really had "lightning" on that GEC it wouldn't matter if it was CadWelded. Lightning will not make a 180 degree turn. It would just shoot out the end. That is why air terminal conductors need to be run as straight as possible with very wide radius turns. Generally you will not really get lightning in a panel and if you do it will be toast. I did take a direct hit on the air terminal above my weather station this summer with minimal damage.
I am reminded of this rule:

"280.12 Routing of Surge Arrester Grounding Conductors.
The conductor used to connect the surge arrester to line, bus, or equipment and to a grounding conductor connection point as provided in 280.21 shall not be any longer than necessary and shall avoid unnecessary bends."

. and on another note, the original picture shows signs of dirt in the bottom, this could be because of a flood, and if so, the weep holes in the bottom of the cabinet may be plugged up.
Reply With Quote
  #15  
Old 12/21/07, 10:01 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,281
Default Re: Spliced Ground

Thanks Paul



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Two ground wires jlybolt Electrical Inspections 8 8/10/06 2:06 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 8:48 AM


All times are GMT -4. The time now is 8:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts