Default Spliced SEC

Are the service entrance wires allowed to be spliced inside the box? Memory tells me no.
Any yes, the double taps were mentioned.
Attached Thumbnails
spliced-sec-530.jpg  
Reply With Quote
  #2  
Old 11/14/06, 9:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Spliced SEC

Quote:
Originally Posted by wsiegel
Are the service entrance wires allowed to be spliced inside the box?
Sure they are. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/15/06, 10:47 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Spliced SEC

Double tapping the main lugs
...that takes ingenuity
....er I mean insanity.
Reply With Quote
  #4  
Old 11/15/06, 11:31 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Spliced SEC

William,

The Service Conductors entering that Panel Enclosure are probably spliced because of a change to the service of some kind. It is fine to splice them if needed as long as it does not take up to much space ( I wont quote percentages for you )......now taping them ( not really TAPS but easier to understand ) can be tricky so we wont go their....but as it is shown splicing to extend them is fine.....as long as the spliced conductors are sized right and the splice connection is done correctly.

AS for the Double TAPS....yep...they are wrong.....



Paul W. Abernathy

Last edited by pabernathy; 11/15/06 at 12:11 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Spliced Rafters Richard Seay Structural Inspections 14 10/10/07 12:00 AM
Spliced roof rafters lfoster Structural Inspections 45 5/12/07 9:06 PM
Spliced SEC, FPE & Bonding dmacy Electrical Inspections 4 3/3/07 10:26 PM


All times are GMT -4. The time now is 8:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts