Default Split nut connection

Is the type of connection wrong? 2- 200 AMP Square D panels side by side. Wire coming out the right panel and connecting to the wire above the panel of the left. I have never seen a connection like this, but I do learn something new every day.
Attached Thumbnails
split-nut-connection-101_7438.jpg   split-nut-connection-101_7439.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
Find an InterNACHI certified Maine Home Inspector (and anywhere else in North America)
  #2  
Old 8/6/09, 9:37 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Split nut connection

It is hard to tell from the pictures, but I am guessing that you are looking at the ground conductor for a system that uses 2-200 amp panels fed from two sets of lugs in the meter base to produce a 400 A service. In that case the ground conductor would connect to a single ground rod. Did you see one? Very common for larger homes around here.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #3  
Old 8/6/09, 10:34 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is online now
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Split nut connection

Ground rod in ground and ground on water pipe.

Thanks!!!!



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #4  
Old 8/11/09, 3:49 PM
Tom Horne Tom Horne is offline
New User
 
Join Date: Aug 2009
Posts: 12
Please Note: Tom Horne is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split nut connection

There is however a violation in that picture set. Each two hundred ampere panel is supplied by 4/0 Al conductors. Since neither of those could possibly be the "the main power feeder to a dwelling unit" the use of conductors sized in accordance with 310.15(B)(6) is a violation. The diversity on which 310.15(B)(6) is predicated is not assured when the load is split across two sets of service entry conductors. The Service Entry Conductors should be sized in accordance with 310.15(B) and thus taken directly from table Table 310.16. The net effect of that is when the 400 ampere load for one dwelling is split across two sets of Service Entry Conductors each set must be capable of carrying a full two hundred amperes which gives you a minimum conductor size in Al of 250 Kcmills or one size larger then is commonly available in SEC cable.
--
Tom Horne
Reply With Quote
  #5  
Old 8/11/09, 4:11 PM
Tom Horne Tom Horne is offline
New User
 
Join Date: Aug 2009
Posts: 12
Please Note: Tom Horne is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split nut connection

Buck
I'm not trying to nit pick but the term of art is a "split bolt" connector. Calling it a split nut won't help your credibility with the electrician that gets called in. That method of running the Grounding Electrode Conductor is specifically permitted by the NEC in

"250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors shall be installed as specified in 250.64(A) through (F).
(D) Grounding Electrode Conductor Taps. Where a service consists of more than a single enclosure as permitted in 230.40, Exception No. 2, it shall be permitted to connect taps to the grounding electrode conductor. Each such tap conductor shall extend to the inside of each such enclosure. The grounding electrode conductor shall be sized in accordance with 250.66, but the tap conductors shall be permitted to be sized in accordance with the grounding electrode conductors specified in 250.66 for the largest conductor serving the respective enclosures. The tap conductors shall be connected to the grounding electrode conductor in such a manner that the grounding electrode conductor remains without a splice."

If you read that with great care and patience you will see it specifically covers the situation in your second photograph providing that the conductor and the tap are sized correctly.
--
Tom Horne
Reply With Quote
  #6  
Old 8/13/09, 12:48 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Split nut connection

Quote:
Originally Posted by Tom Horne View Post
There is however a violation in that picture set. Each two hundred ampere panel is supplied by 4/0 Al conductors. Since neither of those could possibly be the "the main power feeder to a dwelling unit" the use of conductors sized in accordance with 310.15(B)(6) is a violation. The diversity on which 310.15(B)(6) is predicated is not assured when the load is split across two sets of service entry conductors. The Service Entry Conductors should be sized in accordance with 310.15(B) and thus taken directly from table Table 310.16. The net effect of that is when the 400 ampere load for one dwelling is split across two sets of Service Entry Conductors each set must be capable of carrying a full two hundred amperes which gives you a minimum conductor size in Al of 250 Kcmills or one size larger then is commonly available in SEC cable.
--
Tom Horne
Tom,

I have been squaking about this one for years......and agree with this application as you have layed out. However, what if the calculated load does not exceed 180A on each. Would you then have a problem with this application?



Paul W. Abernathy
Reply With Quote
  #7  
Old 8/13/09, 12:58 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Split nut connection

Quote:
Originally Posted by Tom Horne View Post

"250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors shall be installed as specified in 250.64(A) through (F).
(D) Grounding Electrode Conductor Taps. Where a service consists of more than a single enclosure as permitted in 230.40, Exception No. 2, it shall be permitted to connect taps to the grounding electrode conductor. Each such tap conductor shall extend to the inside of each such enclosure. The grounding electrode conductor shall be sized in accordance with 250.66, but the tap conductors shall be permitted to be sized in accordance with the grounding electrode conductors specified in 250.66 for the largest conductor serving the respective enclosures. The tap conductors shall be connected to the grounding electrode conductor in such a manner that the grounding electrode conductor remains without a splice."

If you read that with great care and patience you will see it specifically covers the situation in your second photograph providing that the conductor and the tap are sized correctly.
--
Tom Horne
In that allowance for where you have a grounding electrode conductor that is continuous from the electrode under the panels in question. The NEC allows for the grounding electrode conductor taps to extend into each panel. If the grounding electrode conductor runs all the way into one of the panels...would you consider it a grounding electrode conductor tap that extends into the panel and would this meet the intent of the allowance.

Typically we would see lets say a 4 AWG CU from lets say a UFER run to the location under the panels. Then lets say you have (2) 200A panels which the allowance of 250.64(D) allows grounding electrode conductor taps to tap onto the unspliced 4AWG CU with 6 AWG CU and extend into both panel enclosures as permitted in the NEC....in the application shown the grounding electrode conductor runs continuous into panel (1) and then panel two taps onto the (1)....do you feel this meets the intent of the allowance?



Paul W. Abernathy
Reply With Quote
  #8  
Old 8/13/09, 1:00 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Split nut connection

lol...Split Nut...now thats just plain funny.....Sorry Buck...



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Grounding rod connection from meter box fbartlo Electrical Inspections 37 7/28/07 12:30 PM
Split bolts cbuell Electrical Inspections 11 2/26/07 11:16 PM


All times are GMT -4. The time now is 8:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts