Default Spot a Problem

Home subpanel, 60 amp fed from one of two 200 amp services. What's wrong, if anything?
Attached Thumbnails
spot-problem-subpanel-005-small-.jpg.jpg
Views:	129
Size:	47.2 KB
ID:	4561   spot-problem-subpanel-007-small-.jpg.jpg
Views:	110
Size:	40.4 KB
ID:	4562  
Reply With Quote
  #2  
Old 7/11/06, 5:20 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spot a Problem

Quote:
Originally Posted by cradan
Home subpanel, 60 amp fed from one of two 200 amp services. What's wrong, if anything?
Looks like feeders are under size .Is it a 60 amp main breaker?
No grounds so expect it is fed with steel conduit .
Very few neutrals so most circuits are 240 volt .
Neutral bonded to cabinet not allowed in Canada to have pony panel neutral bonded to cabinet.
Could not see a bushing on conduit Not needed on plastic but does need a ground wire if plastic.
I hate picture inspections and do not usually do them .

Roy Cooke sr
.
Reply With Quote
  #3  
Old 7/11/06, 5:32 PM
cradan cradan is offline
Active Poster
 
Join Date: Aug 2003
Location: Minooka, IL
Posts: 239
Please Note: cradan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spot a Problem

Disconnect is marked 60-amp, feeders were 6AWG, all copper including branch conductors.

Bushings all looked o.k. (crappy photo). What bothered me was the shortage of neutral branch conductors and the obvious panel bond.
Reply With Quote
  #4  
Old 7/11/06, 10:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Spot a Problem

Chris,

Firstly, if it is a sub panel they did not know they had to run (4) conductors to this panel...and isolate the grounded conductors on it's own termial bar. See my BTW statement below...lol

Second, if this is # 6 AWG to the " grounded" conductor it is a violation of Art 200.6 Means of Identidying Grounded Conductors. Because of it's size the grounded conductor should be continuous white or gray outer finish or by three continuous white striples on other than green insulation along its ENTIRE length.

Third, Obvioulsy the additional picture shows it is bonded to the CASE...to the neutral terminal bar......THIS is a sub-panel or Remote Distributrion Panel so that is wrong.


Hope this helps

Oh..BTW......I figured some "conduit" lover would come in and say the 4th wire is the conduit.....it serves as the grounding conductor...well......if someone brings that into play...they better remove that bonding jumper......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 7/11/06 at 10:23 PM..
Reply With Quote
  #5  
Old 7/12/06, 12:57 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,526
Default Re: Spot a Problem

"Oh..BTW......I figured some "conduit" lover would come in and say the 4th wire is the conduit.....it serves as the grounding conductor...well......if someone brings that into play...they better remove that bonding jumper......"

Paul;

You are such a spoil sport.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 7/12/06, 7:14 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spot a Problem

If those are 240v circuits then the breakers should be double poles and they appear to be all singles. Also, there is no breaker lockdown device on the double pole 60 that is being used as the main. That's in addition to all the other problems noted above.
Reply With Quote
  #7  
Old 7/12/06, 9:07 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spot a Problem

2nd picture, right side of panel, 2nd wire up -

my eyes are bad, it looks like the insulation on the wire was not trimmed below connection screw?
Reply With Quote
  #8  
Old 7/12/06, 12:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Spot a Problem

Quote:
Originally Posted by wdecker
"Oh..BTW......I figured some "conduit" lover would come in and say the 4th wire is the conduit.....it serves as the grounding conductor...well......if someone brings that into play...they better remove that bonding jumper......"

Paul;

You are such a spoil sport.
LOLOLO......You are so cool Will....I knew you would reply to that BAIT..thehehe



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 7/14/06, 2:02 PM
cradan cradan is offline
Active Poster
 
Join Date: Aug 2003
Location: Minooka, IL
Posts: 239
Please Note: cradan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spot a Problem

Quote:
Originally Posted by smcarthur
If those are 240v circuits then the breakers should be double poles and they appear to be all singles. Also, there is no breaker lockdown device on the double pole 60 that is being used as the main. That's in addition to all the other problems noted above.
None of the installed circuits are configured as 240v; only the feeder disconnect is a two-pole breaker. I'm not sure where you got the idea... Also, why is a breaker lockdown device required at the main disconnect for this sub-panel?
Reply With Quote
  #10  
Old 7/14/06, 5:11 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 834
Send a message via Skype™ to pbolliger
Default Re: Spot a Problem

Quote:
Originally Posted by cradan
None of the installed circuits are configured as 240v; only the feeder disconnect is a two-pole breaker. I'm not sure where you got the idea... Also, why is a breaker lockdown device required at the main disconnect for this sub-panel?

From the ratio of "hot" to "neutral" wires.. Hardly any neutrals..

I don't see handle ties on the OCPD's either so there's something else going on..

Perhaps the conduit is being used as a neutral....
The panel case is bonded so ...maybe... Three wire... and no isolation between neutral and grounding...
Reply With Quote
  #11  
Old 7/14/06, 11:14 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Spot a Problem

If the circuits are not 240v, then they could be sharing neutrals. It's hard to tell from the photo, but there should be a total of 8 neutrals. Only 2 hots (in this case,three if it were three phase), one from each phase, may share a neutral. The GFCI needs a dedicated neutral.
I assume they are using the conduit as a ground, since I see none in the panel and since it's a sub panel the neutral bar should not be bonded to the can.

Also, if you are backfeeding a panel, such as they are here, then the breaker being used as the main must have a lock down device to prevent it from being removed from the panel. Go to www.squareD.com and do a search for PK4MB2LA to see what I'm refering to and why they are used.

How about it Paul, see anything else?

Last edited by smcarthur; 7/14/06 at 11:40 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fetchreport.com Email Problem jmckenna1 Misc. Discussion 13 11/1/07 11:50 AM
Is MAC a problem bemelander General Inspection Discussion 2 9/6/07 12:34 PM
Camera Problem nwagner Misc. Discussion 19 7/30/07 11:10 PM
Plumbing problem at home. mnahrgang Plumbing 25 7/10/07 6:32 PM
Can you spot the problem?? mmorgan Plumbing 12 2/25/07 5:34 AM


All times are GMT -4. The time now is 10:37 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts