Question Sq D 200 amp panel with Cutler Hammer Breaker

Hi. Needed a quick answer, if anyone has one!

Can Cutler Hammer breakers usually be crossed over and installed in Square D panel? As best as I could read the CH label - Type C L 720, T060429, CU/AL SWD

Thanks,
Reply With Quote
  #2  
Old 6/28/07, 1:07 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

This all gets down to how you regard "classified breakers". U/L and C/H say they are OK. SqD doesn't

Classified Breaker Compatibility Chart
Native Document | 5651B63SH04.PDF | (340KB) | relevance:84.99 %
Eaton's Cutler-Hammer Type CL Breakers list for UL approved replacements in Crouse Hinds, GE, ITE, Siemens, Square D Homeline and Murray loadcenters.
"

http://www.eaton.com/ecm/idcplg?IdcS...=1046632560357
Reply With Quote
  #3  
Old 6/28/07, 1:27 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

Square D's side
http://ecatalog.squared.com/techlib/...00892680139d70

Inspectors split on the issue, most side with U/L listing
Reply With Quote
  #4  
Old 6/28/07, 1:37 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

of course square d isn't going to say its ok. That would be like coca-cola saying "you can buy our bottles but you can refill them with pepsi if you want to" Go with the UL recommendation...unbiased.
Reply With Quote
  #5  
Old 6/28/07, 3:18 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

Doesn't the NEC always refer to the manufacturer's instructions, i.e. panel label?



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #6  
Old 6/28/07, 4:08 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

Quote:
Originally Posted by bwiley
Doesn't the NEC always refer to the manufacturer's instructions, i.e. panel label?
No, it says to go with listing and labeling instructions. Listing is from UL, and the UL mandates the required labeling language. "Labeling" is not manufacturer's instructions. Labeling is done in compliance with the UL Marking Guide.
Reply With Quote
  #7  
Old 6/28/07, 4:08 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

Blaine
That is why Eaton C/H will give you a sticker to put in the panel stating the U/L classification of their replacement breaker. It is clear that SqD will not evaluate a C/H breaker in their panel so you have the U/L blessing from their evaluation.
Reply With Quote
  #8  
Old 6/28/07, 10:06 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sq D 200 amp panel with Cutler Hammer Breaker

Thanks for all the info.

Great message board !
Linda
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Minimum Size Breaker for Sub Panel rmoewe Electrical Inspections 7 5/21/07 6:24 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 4:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts