Hi. Needed a quick answer, if anyone has one!
Can Cutler Hammer breakers usually be crossed over and installed in Square D panel? As best as I could read the CH label - Type C L 720, T060429, CU/AL SWD Thanks, |
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
This all gets down to how you regard "classified breakers". U/L and C/H say they are OK. SqD doesn't
Classified Breaker Compatibility Chart Native Document | 5651B63SH04.PDF | (340KB) | relevance:84.99 % Eaton's Cutler-Hammer Type CL Breakers list for UL approved replacements in Crouse Hinds, GE, ITE, Siemens, Square D Homeline and Murray loadcenters. " http://www.eaton.com/ecm/idcplg?IdcS...=1046632560357 |
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Square D's side
http://ecatalog.squared.com/techlib/...00892680139d70 Inspectors split on the issue, most side with U/L listing |
|
#4
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
of course square d isn't going to say its ok. That would be like coca-cola saying "you can buy our bottles but you can refill them with pepsi if you want to" Go with the UL recommendation...unbiased.
|
|
#5
|
|||
|
|||
|
Doesn't the NEC always refer to the manufacturer's instructions, i.e. panel label?
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Blaine
That is why Eaton C/H will give you a sticker to put in the panel stating the U/L classification of their replacement breaker. It is clear that SqD will not evaluate a C/H breaker in their panel so you have the U/L blessing from their evaluation. |
|
#8
|
||||
|
||||
|
Please Note:
lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for all the info.
Great message board ! Linda |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Minimum Size Breaker for Sub Panel | rmoewe | Electrical Inspections | 7 | 5/21/07 6:24 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 4:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |