Default Square D ARC Fault Recall

Hey Guys,

I am not sure if anyone posted this before as I did not find anything on the search feature so it might be on the old boards but I wanted to post some of it here just in case.

Product Recall Information -

Square D Arc Fault Breakers Manufactured between March1, 2004 and September 23, 2004 are the Arc Faults being recalled.

Ok....Why did I post this again.......... it was posted last year so the reason I am posting it is to show some model numbers and things to look for.

Here are the products affected :

QO115AFI,QO120AFI,QOB115AFI,QOB120AFI,HOM115AFI and HOM120AFI

Just a note...the TEST button on those models are BLUE...

Ok.......the Identidying Date Codes.....when you see one of these you think is one from the recall...remember to check the date code.....

" To identify if a product was produced during this timeframe, you must find the product date code, STAMPED IN RED ON THE BREAKER LABEL located just above the wiring terminal."

"If the date code on the arc fault circuit breaker matches one of the date codes listed below, please follow the procedure I will also post below:

Affected Date Codes : CN, DN, EN, FN, GN, HN and JN

Note: Arc Faults produced before 3/2004 ( AN, BN ) or after 10/2004 ( KN) are not affected. Also breakers that carry the date code BEFORE CN are in compliance ( AN,BN and any date code ending in "L" or "M" )

OK........if you find one....refer it to an electrician ASAP.....They will replace it and test it and return the recalled one to the Square D retailer.

Important note: While the AFC FAULT function of the recalled items is the problem...they still aoffer the same protection of Short Circuit and Overload Protection as a standard breaker.....However they are ARC FAULT for a reason and should be replaced ASAP.....

Just in case you run into one guys....figured I would post some numbers for you....



Paul W. Abernathy
Reply With Quote
  #2  
Old 3/21/06, 9:56 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D ARC Fault Recall

Thanks! Very nice!
Reply With Quote
  #3  
Old 3/21/06, 9:58 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Square D ARC Fault Recall

Thanks Paul,

I read this last year, but forgot all about it, I bet there are 1,000's out there that never got replaced.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 3/21/06, 10:03 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Square D ARC Fault Recall

Gerry,

Heck yeah.......If you think the electrician's who wired homes from March to September of 2004 are going back to replace them.....think again...Sad Fact is probably 90% or more of the breakers during that time frame as still in use....



Paul W. Abernathy
Reply With Quote
  #5  
Old 3/21/06, 10:09 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,268
Default Re: Square D ARC Fault Recall

Quote:
Just a note...the TEST button on those models are BLUE...


Quote:
Affected Date Codes : CN, DN, EN, FN, GN, HN and JN

Good information Paul.....thanks.
Reply With Quote
  #6  
Old 3/21/06, 10:18 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Square D ARC Fault Recall

Actually....I should clarify.....other models in that era may be BLUE also.....I used BLUE just to be a instant notice of a Square D model.....then going that extra step to check the ID codes and so on is important....

I don't know if they changed any colors after that...but use the BLUE to give you FIRST notice....then investigate more beyond the color....

But YES.....all of the affected models I can guarantee have a BLUE button......



Paul W. Abernathy
Reply With Quote
  #7  
Old 3/21/06, 12:48 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D ARC Fault Recall

http://www.squared.com/us/squared/corporate_info.nsf/unid/9CB09A222974952E85256F19005EAE4F/$file/productSafetyNotice.pdf

http://www.squared.com/us/squared/corporate_info.nsf/unid/9CB09A222974952E85256F19005EAE4F/$file/ElectronicInspectorLetter1014.pdf
Reply With Quote
  #8  
Old 3/21/06, 10:31 PM
rglenn rglenn is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Largo, FL
Posts: 107
Default Re: Square D ARC Fault Recall

I was called responsible today !

Customer is an investor located in California. Bought a home built last year here in Florida. I had completed the New Home Warranty Inspection last week and had sent the report to him. I went back and looked at the photos I had taken of the Electric Panel. Sure enough, after blowing them up, there they were ! AFCI's that are on the recall list. I knew those blue test buttons sounded familiar. I sent a follow up letter stating the recall on the AFCI's. The Builder will be replacing the AFCI's at all of the homes in the development.
The investor was so happy he sent me an e-mail stating that I was responsible. Next week someone will bring me back to earth, I can feel it coming......
Reply With Quote
  #9  
Old 3/22/06, 10:20 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Square D ARC Fault Recall

See.........You just never know....Thats why we post these things...



Paul W. Abernathy
Reply With Quote
  #10  
Old 3/28/06, 3:29 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Exclamation Re: Square D ARC Fault Recall

Some interesting news about AFCI testers.. You cannot rely on any brands of testers at this point to properly test AFCI's .. I will find the UL article and post it "shortly"..

Some of these testing devices are not UL tested or approved either...Scary.. Use the test button on the AFCI instead of your Testing device.
Reply With Quote
  #11  
Old 3/28/06, 3:35 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Exclamation Re: Square D ARC Fault Recall

Here is a Square D blurb about testers...
Attached Files
File Type: pdf AFCI TRUTH.pdf (77.4 KB, 167 views)
Reply With Quote
  #12  
Old 3/28/06, 9:12 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: Square D ARC Fault Recall

Quote:
Originally Posted by rglenn
I was called responsible today !

Customer is an investor located in California. Bought a home built last year here in Florida. I had completed the New Home Warranty Inspection last week and had sent the report to him. I went back and looked at the photos I had taken of the Electric Panel. Sure enough, after blowing them up, there they were ! AFCI's that are on the recall list. I knew those blue test buttons sounded familiar. I sent a follow up letter stating the recall on the AFCI's. The Builder will be replacing the AFCI's at all of the homes in the development.
The investor was so happy he sent me an e-mail stating that I was responsible. Next week someone will bring me back to earth, I can feel it coming......
Be careful not to jump the gun on these recalls as the recalls in question were made in 2004. Make sure that the the following codes are visible above the connection:Affected Date Codes : CN, DN, EN, FN, GN, HN and JN

I called one out that I though said HN, but actually said HH as the label was slightly torn. Good luck!
Attached Thumbnails
square-d-arc-fault-recall-picture-154-small-.jpg.jpg
Views:	152
Size:	97.3 KB
ID:	2434  

Last edited by srowe; 3/28/06 at 9:19 PM..
Reply With Quote
  #13  
Old 3/29/06, 5:03 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,630
Default Re: Square D ARC Fault Recall

Quote:
Originally Posted by pbolliger
Use the test button on the AFCI instead of your Testing device.
Since I've only found AFCIs in the electric panel, I disclaim them and do not test them. I want nothing to do with having to reprogram all the equipment in all the bedrooms; my inspection protocols do not include testing outlets that have stuff plugged into them, including GFCI outlets.

I do educate my Clients about regularly testing such outlets and circuit breakers.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 3/29/06, 11:00 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Square D ARC Fault Recall

Quote:
Originally Posted by pbolliger
... Use the test button on the AFCI instead of your Testing device.
I agree (same for GFCI receptacles)... good advice ...

Quote:
Originally Posted by rray
I do educate my Clients about regularly testing such outlets and circuit breakers.
Even better advice ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 3/29/06, 11:38 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Talking Re: Square D ARC Fault Recall

I agree with you RR on that.. Just passing along the information from the MFG on proper testing methods since the AFCI testers with the exception of:
http://www.arcfaulttester.com/index.html
are NOT reliable ways of triggering the AFCI via remote means.

Not endorsing anything here or getting any royalties for this link. Been hearing a lot about bogus UL tags and false claims on AFCI testers. This unit above proves it has a valid UL label since you can trace it back to the UL site.

The push for 2008 to have all new homes "completely " AFCI protected is the next battle in the mix.. Get your margarita and pizza ready....."LETS GET READY TO RUMBLE"...

When you get the chance , check out Joe Tedesco's link on a house fire caused by an electrical recepticle.....in the living room!.. Everyone is pushing for complete AFCI house protection in that video..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Counterfeit Square D Recall ldapkus Electrical Inspections 3 10/30/07 10:23 PM
Square D recall bwiley Electrical Inspections 2 12/18/06 10:41 AM
Square D Electrocution Hazard Safety Switch Recall jtedesco1 Miscellaneous Discussion for Inspectors 5 12/16/06 12:09 AM
Square D Files Lawsuit to Prevent Counterfeiting jtedesco1 Electrical Inspections 2 5/26/06 6:36 PM


All times are GMT -4. The time now is 5:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts