Does anyone know if Square D breakers are compatible with a Cutler Hammer panel? Thanks.
774 Manor Road Staten Island, NY 10314 718-514-3393 |
| Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
There are many electricians and inspectors who stand by Section 380-3(a) which states "Switches and circuit breakers shall be of the externally operable type mounted in an enclosure listed for their intended use....". Even though the other manufacturer may make a breaker they claim will fit into this box, the panel does not list this device for the use therein.
If the CH box prohibits the use of any breaker other than CH, it is a code violation to "mix and match" no matter what others may say of "compatability". I have an email from the President of Square D to Mike Holt explaining why his company will not honor their warranty should a box catch on fire (or otherwise not work properly) and contains anything other than a Square D breaker in it. Since CH usually prints their warning not to use another mfr breaker in their box in red, I would presume that they mean what they say, too. Write it up. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#3
|
||||
|
||||
|
Thanks for the input James. I did write it up.
774 Manor Road Staten Island, NY 10314 718-514-3393 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 77 | 5/10/12 6:13 PM |
| Square D HOM Breaker & Max Wire Size | pbennett1 | Electrical Inspections | 20 | 3/3/08 9:22 PM |
| Square D Fuse Panel | jhagarty | Electrical Inspections | 7 | 11/8/06 1:14 PM |
| GFCI breaker in service panel | cobarr | Electrical Inspections | 11 | 4/17/06 9:59 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |