Does square D allow 12 gauge double taps or just 14?
I wasn't sure it allowed 12 gauge or not. Thanks for the help. Andy |
|
#2
|
||||
|
||||
|
Quote:
Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#3
|
||||
|
||||
|
The 15 amp HomeLine Version I'm holding, has instructions on the side for 10#-14# AWG Cu for dual wiring.
hth, tom |
|
#4
|
|||
|
|||
|
Please Note:
cyezza is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have seen this as well. The Square D Breakers 15-30 amp are rated for 2 conductor wires 14-1O gauge. See this link:
http://www.nachi.org/forum/showthrea...=Square+double |
![]() |